<p class="MsoNormal">Anthony,</p><p class="MsoNormal"><br></p><p class="MsoNormal">When modeling HRC's in eQUEST, I've found that by default, the chiller does not operate without a load on the chilled water side.</p>
<p class="MsoNormal"><br></p><p class="MsoNormal">I would suggest a few things to troubleshoot:</p><p class="MsoNormal">- Create an hourly report containing chilled water loop load, hot water loop load, and assigned load to the HRC. Check to see if indeed there are hours during which the chiller is operating with no call for cooling.</p>
<p class="MsoNormal">- Do you have other chillers besides the HRC? If so, you may be seeing more HRC operation in the winter because eQUEST is selecting one of the other chillers to run as the lead chiller during the higher load hours of the summer. For example, say that the HRC is 200 tons and your other chiller is 400 tons. In the summer with a load of 350 tons, eQUEST may be choosing to run the 400 ton chiller because it is a better match for the load, while in the winter with a load of 200 tons, eQUEST may choose to run the 200 ton HRC.<br>
</p><p class="MsoNormal"><br></p><p class="MsoNormal">If you want the HRC to always be the lead, then you'll have to specify this with equipment controls. I have not been able to successfully implement anything other than a load-based control scheme for HRCs in eQUEST (which may be all that you're after). Attempting to stage the chillers based on outside air temperature or load in the HW loop, for example, causes eQUEST to crash during run time for me (with no BDL errors). If you figure out how to do this, I would love to know the secret. I prefer to stage HRCs based on a combination of loop loads and outside air temperature, but I've never been able to capture these savings in eQUEST.</p>
<p class="MsoNormal"><br></p><p class="MsoNormal">Aaron<br></p><p class="MsoNormal"><br></p><p class="MsoNormal"><br></p><p class="MsoNormal"><br></p><p class="MsoNormal">Couldn’t find an answer in the archives so I thought I’d solicit the experts. </p>
<p class="MsoNormal"> </p><p class="MsoNormal">Objective: I only want my HRC to recover waste heat when there’s a call for cooling.</p><p class="MsoNormal"> </p><p class="MsoNormal">Problem:
I have more chiller operation in the winter than the summer. It seems
my HRC’s are activating whenever there is a demand on the hot water
loop it’s attached to. </p><p class="MsoNormal"> </p><p class="MsoNormal">Question:
Does one have to specify equipment controls to get the HRC to operate
in the desired mode? If not, what else am I doing wrong here? </p><p class="MsoNormal"> </p><p class="MsoNormal"><b><span style="color: rgb(15, 36, 62);">Anthony Hardman, PE</span></b></p><p class="MsoNormal"><b><span style="font-size: 9pt; color: rgb(15, 36, 62);">LEED AP BD&C</span></b><b><span style="color: rgb(15, 36, 62);"></span></b></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(15, 36, 62);">Building Performance Analyst</span></p><p class="MsoNormal"><b><span style="color: rgb(0, 176, 80);">The Green Engineer, LLP</span></b></p><p class="MsoNormal">
<span style="font-size: 10pt; color: rgb(0, 176, 80);">Sustainable Design Consulting</span></p><p class="MsoNormal"><span style="font-size: 10pt; color: rgb(15, 36, 62);">50 Beharrell St</span></p><p class="MsoNormal"><span style="font-size: 10pt; color: rgb(15, 36, 62);">Concord, MA 01742</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(15, 36, 62);">O: <a href="tel:978%2F610-2801" value="+19786102801" target="_blank">978/610-2801</a></span></p><span style="font-size: 10pt; color: rgb(15, 36, 62);">C: <a href="tel:720%2F840-7862" value="+17208407862" target="_blank">720/840-7862</a></span>