<div>Thank you, Jenny, your advise is really helpful.</div>
<div> </div>
<div>But I still can't solve the question 3.</div>
<div> </div>
<div>ASHRAE 90.7 2007, G3.1.3.12: The air temperature for cooling shall be reset highter by 5 under the minimum cooling load conditions.</div>
<div> </div>
<div>My question is: I can reset the temperature depend on outside temperature or inside temperature, but I don't know how to reset temperature depend on "load".<br><br>Thank you for your help!</div>
<div> </div>
<div class="gmail_quote">Jenny Zhang <span dir="ltr"><<a href="mailto:jenny.zhang@arup.com" target="_blank">jenny.zhang@arup.com</a>></span> 於 2011年8月26日上午10:36 寫道:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-US" vlink="purple" link="blue">
<div>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt"><u></u> <u></u></span></p>
<div style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 0cm; PADDING-RIGHT: 0cm; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">From:</span></b><span style="FONT-SIZE: 10pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b></span><span style="FONT-SIZE: 10pt" lang="JA">何宗翰</span><span style="FONT-SIZE: 10pt"><br>
<b>Sent:</b> 2011</span><span style="FONT-SIZE: 10pt" lang="JA">年</span><span style="FONT-SIZE: 10pt">8</span><span style="FONT-SIZE: 10pt" lang="JA">月</span><span style="FONT-SIZE: 10pt">26</span><span style="FONT-SIZE: 10pt" lang="JA">日</span><span style="FONT-SIZE: 10pt"> 9:07<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] LEED EAp1 baseline problem<u></u><u></u></span></p></div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal">Hello All,<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">I am trying to establish the baseline model for LEED NC 3.0, and have some problem as following:<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">1. From ASHRAE 90.1 2007 G3.1.2.8, does it mean that I can simulation the supply airflow rate by <u></u><u></u></p></div>
<div>
<p class="MsoNormal"> setting MIN-SUPPLY-T & DESIGN-COOL-T have 20 degree difference and let eQUEST to calculate the <u></u><u></u></p></div></div>
<div>
<p class="MsoNormal"> supply airflow automatically?<span style="COLOR: #1f497d"> </span><span style="COLOR: red">YES</span><u></u><u></u></p></div>
<div>
<p class="MsoNormal">2. My baseline HVAC is system No.8, VAV with PFP boxes, so from G3.1.3.12, the supply air temperature reset must depend on the load, but I can't find this setting option in eQUEST, could anybody tell me how to set that?<span style="COLOR: #1f497d"> </span><span style="COLOR: red">you could find reset setting options on the ‘air side system’>system>cooling>control and reset.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal">3.Because I am not in a LEED project, could anyone send me the LEED NC3.0 "EAp2 Section 1.4 table.xls" to check if there is anything I loss?<span style="COLOR: #1f497d"> </span><span style="COLOR: red">please see the attached file, also you could down it on LEED online Credit Resource.<u></u><u></u></span></p>
</div>
<div>
<div>
<p class="MsoNormal"><span style="COLOR: red"> <u></u><u></u></span></p></div>
<div>
<p class="MsoNormal"><u></u> <u></u></p></div>
<div>
<p class="MsoNormal">Thanks in advance, <u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">Stan Ho<u></u><u></u></p></div></div></div><font face="monospace">____________________________________________________________<br>Electronic mail messages entering and leaving Arup business<br>systems are scanned for acceptability of content and viruses</font></div>