<div>Hi Kirti,</div>
<div> </div>
<div>essentially, the rooms that are asking for cooling energy are not getting it for some reason...this is the reason (or input) that you need to find to be the culprit of not providing enough energy or not letting the cooling energy get to the spaces that are asking for cooling.</div>
<div> </div>
<div>Start by going to the SS-R reports after you see the unmet hours in your BEPS/BEPU reports. Find which zones/systems are the culprit of the issue. Next go to the SS-F reports for each zone that is being undercooled and this will help you determine what also might be happening.</div>
<div> </div>
<div>Hope this is a start to getting you the info you are looking for.</div>
<div> </div>
<div>Cheers,</div>
<div>Pasha<br><br></div>
<div class="gmail_quote">On Thu, Aug 25, 2011 at 10:25 PM, kirti pabrekar <span dir="ltr"><<a href="mailto:arkirtipabrekar@gmail.com">arkirtipabrekar@gmail.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote"><br clear="all">
<div>dear all, </div>
<div><br></div>
<div>while checking through my simulation reports, i have realized that the the number of cooling unmet hours for one of my projects is 579 hours. this far exceeds the tab of allowable 300 hours. can anybody please explain me the idea behind cooling unmet hours.</div>
<div><br></div>
<div>any help is greatly appreciated.</div>
<div><br></div>
<div>thank you</div>-- <br><font color="#888888">
<div>Regards,<br>Ar. Kirti Pramod Pabrekar.</div>
<div>IGBC AP, LEED India, <br>M. Arch,<br>Environmental Planning and Design.<br></div>
<div> </div>
<div><em>...Green is a commitment...not a competition...</em></div><br></font><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>