Ben,<div><br></div><div>You will have to create a separate "shell" for each floor. First, create the first floor shell and populate all its fields. Next, create a new shell via the DD Wizard and chose to copy the first shell and inherit all its components. Specify that the new shell be directly above the first. Now you should have the same footprint pre-loaded from the first shell, and you can now do a separate zoning for the second floor.</div>
<div><br></div><div>Aaron<br clear="all"><br><span class="Apple-style-span" style="font-family: arial, sans-serif; font-size: 13px; background-color: rgb(255, 255, 255); "><p class="MsoNormal">Is it possible to make a multi-story shell where each floor has the same footprint but completely different zoning? For example, I have an 8-story building with underground parking, retail on the first floor, and residential on 2-8. I don’t see any way to draw separate zones for each floor in the wizard, and I don’t want to go through and delete zones manually in detailed mode, if I can avoid it.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Any suggestions?<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Thank you,<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Ben Pressman, EIT, BESA<u></u><u></u></p><p class="MsoNormal"><i><span style="font-size: 9pt; ">Project Engineer<u></u><u></u></span></i></p><p class="MsoNormal"><i><span style="font-size: 9pt; "><u></u> <u></u></span></i></p>
<p class="MsoNormal">Practical Energy Solutions<u></u><u></u></p><p class="MsoNormal">101 E. Evans Street, Suite 2<u></u><u></u></p><p class="MsoNormal">West Chester, PA 19380<u></u><u></u></p><p class="MsoNormal">ph: <a href="tel:610.430.1382%C2%A0%20x304" value="+16104301382" target="_blank" style="color: rgb(42, 93, 176); ">610.430.1382 x304</a><u></u><u></u></p>
<p class="MsoNormal">fax: <a href="tel:610.430.1375" value="+16104301375" target="_blank" style="color: rgb(42, 93, 176); ">610.430.1375</a><u></u><u></u></p><p class="MsoNormal">cell: <a href="tel:610.733.9518" value="+16107339518" target="_blank" style="color: rgb(42, 93, 176); ">610.733.9518</a><u></u><u></u></p>
<p class="MsoNormal">web: <u><a href="http://www.practicalenergy.net/" target="_blank" style="color: rgb(42, 93, 176); "><span style="color: blue; ">http://www.practicalenergy.net</span></a></u><u></u><u></u></p><p class="MsoNormal">
<u></u> </p></span>
</div>