<div>I have not found it possible to create this type if system in eQuest. Use of a DOA system with an energy recovery ventilator is problematic even without the WTWHP. What I have done is create an energy recovery ventilator for each zone, and adjust the COP and capacities of the zone heat pumps to account for the additional capacity and different efficiency of the WTWHP unit.<br>
</div><div><br></div><div>I have had no real luck with WTWHP's in eQuest, and I don't know of anyone who has used them successfully.</div><div><br></div><div>The system you describe can be created in EnergyPlus (though not easily).</div>
<div><br></div><div>--</div><div>Karen</div><br><div class="gmail_quote">On Wed, Aug 3, 2011 at 11:38 AM, Kathryn Kerns <span dir="ltr"><<a href="mailto:kathryn.kerns@bceengineers.com">kathryn.kerns@bceengineers.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<div lang="EN-US" vlink="purple" link="blue">
<div dir="ltr">
<div dir="ltr"><font face="Arial" color="#000000" size="2">Crina, what I have done in the past that is similar is:</font></div>
<div dir="ltr"><font face="Arial" color="#000000" size="2">1. in the Wizard, model your DOAs as hydronic chilled water and hot water units and the rest of your units as WSHPs</font></div>
<div dir="ltr"><font face="Arial" size="2">2. in Detailed Edit, add a 2-pipe loop, a heat pump chiller, a ground source heat exchanger loop, and a lake/well ground source heat exchanger.</font></div>
<div dir="ltr"><font face="Arial" size="2">3. In Detailed Edit, convert the DOA coils to the 2 pipe loop and remove the chilled water</font> and hot water system.</div>
<div dir="ltr"> </div>
<div dir="ltr">That should leave you with a WSHP system and a ground loop WTWHP system. If you want to attach the WTWHPs to the WSHP loop, look up the eQuest literature on the Heat Pump Chiller option and see if there is a way to do this.</div>
</div>
<div dir="ltr"><br>
<hr>
<font face="Tahoma" size="2"><b>From:</b> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> on behalf of Bosch, Crina<br><b>Sent:</b> Tue 8/2/2011 4:04 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] WTWHP with ERU 100% OA and WSHP<br></font><br></div><div><div class="h5">
<div>
<div>
<p class="MsoNormal">Dear eQuest users, </p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">I am working on a project that has WSHP conditioning all my spaces but I also have energy recovery units with 100% OA and the OA is conditioned by WTWHP’s . </p>
<p class="MsoNormal">Did anybody tried this kind of system before because each idea I have and tried to apply into eQuest does not work for me today. </p>
<p class="MsoNormal">Any help is appreciated. </p>
<p class="MsoNormal">Thank you. </p>
<p class="MsoNormal"> </p>
<div>
<p class="MsoNormal"><span style="font-size:10pt">Crina Bosch<br>Engineer, Mechanical</span></p></div>