<div>Hi Omar,</div>
<div> </div>
<div>I apologize it took so long for me to look at this too for you. My own project deadlines have me running...</div>
<div> </div>
<div>Here is what I know and interpret from your situation and the thread that has been created from this discussion.</div>
<div> </div>
<div>1) for LEED you will have to submit constructions specifications for both the selected/installed glazing (glass only) AND the frame systems. In most cases you can get tables from the frame mfg that will show how the Assembly U-value is derated with the frame performance on top of the glass performance values. You should try and get these tables from the fram mfg if you can (i.e. Kawneer, or other).</div>
<div> </div>
<div>2) These window systems in the US are typically NFRC rated, but by my experience window systems outside the US are not NFRC rated....yours are most likely not NFRC rated; this forces you to the Appendix A tables to get your proposed <u>assembly</u> U-value that you have to use. Yes this will be worse performing than your baseline value and thus shall reduce your proposed model energy savings--in accordance with LEED modeling requirements (and Appendix G.)</div>
<div> </div>
<div>3) From the perspective of eQuest. When you are in the wizard you can specify your glass/window performance in the wizard mode. When you do this you can choose "NFRC U-value" or "U-value". When you use the NFRC U-value method, then eQuest will take this value to account for the frame effects and thus you do not have to specify frame data in your model inputs. If you choose the U-value method, then this represents the glass (center of glass) U-value only, and doesn't account for frame properties or performance. This info comes from the help files for eQuest/DOE-2.2. The only difference in eQuest is that using the U-value method assisgns a frame width to the input properties NFRC U-value method sets frame width input value at 0.00.</div>
<div> </div>
<div>Recommendation: Based what I can pick up on your dilemma, I suggest the following-- Use the U-value from Appendix A and model this in your proposed case model. For your eQuest input, select NFRC method (frame width = 0.0) because the appendix A data is for <u>assembly</u> factors including the frame effects with the glass.</div>
<div> </div>
<div>4) Resubmit to LEED that your proposed U-value was incorrectly applied initially and then reference the Appendix A table data that you used in your updated model since your projecd doesn't have NFRC rated fenestration assemblies.</div>
<div> </div>
<div>Hope that helps, Cheers,</div>
<div> </div>
<div>Pasha<br><br></div>
<div class="gmail_quote">On Wed, Aug 3, 2011 at 9:22 AM, Omar Katanani <span dir="ltr"><<a href="mailto:omar@ecoconsulting.net">omar@ecoconsulting.net</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-GB" vlink="blue" link="blue">
<div>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">Indeed there are many ways to model windows! I am kind of lost on how to proceed.</span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">I think I’m going to directly response to the Review comment by arguing that eQUEST captures frame effects.</span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt"> </span></font></p>
<p style="MARGIN-LEFT: 36pt" class="MsoNormal"><i><font color="navy" size="2" face="Arial"><span style="FONT-STYLE: italic; FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">“It is It is unclear whether the window U-value of 0.26 and SHGC of 0.28 used for the Proposed case accounts for the impact of the window frames on the whole assembly as required by ASHRAE modeling protocol. Please provide additional information to confirm that the framed assembly U-value was used for the Proposed case windows (e.g. showing that the whole window assembly has been tested by NFRC, or verifying that LBNL Window5 calculations have been provided for the whole assembly, or <u>verifying that the frame effects are captured within the energy modeling software</u>), or revise the model referencing ASHRAE 90.1-2007 Table A8.2 if needed.”</span></font></i></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">I mean, I got 1 or 2 responses in this thread arguing that eQUEST does indeed capture frame effects. The issue is that no single manufacturer has heard of NFRC in Lebanon (and there are no documented standards on frames in Lebanon), and U-values of Table A8.2 are much, much higher than what’s proposed, so using these A8.2 values in my proposed case will increase my energy consumption considerably!</span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">Best regards,</span></font></p>
<div>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">Omar</span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">___________________________</span></font><font color="navy"><span style="COLOR: navy"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">Omar Katanani</span></font><font color="navy"><span style="COLOR: navy"><br></span></font><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">Sustainable Design Engineer</span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">Email: <a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a></span></font></p>
<p class="MsoNormal"><font color="navy" size="3" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 12pt"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">EcoConsulting (Lebanon)</span></font></p>
<p class="MsoNormal"><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">Nahas</span></font><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US"> Building</span></font><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">, 4<sup>th</sup> floor</span></font></p>
<p class="MsoNormal"><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">4 St-Maron Street</span></font><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US"> / Georges Haddad Avenue</span></font></p>
<p class="MsoNormal"><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">Postal Code: 2028 5806 SAIFI</span></font></p>
<p class="MsoNormal"><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">Beirut</span></font><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">, Lebanon</span></font></p>
<p class="MsoNormal"><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">Tel: </span></font><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt"><a href="tel:%2B961%20%280%29%201%20971%20266" target="_blank" value="+9611971266">+961 (0) 1 971 266</a><br>
Mobile: <a href="tel:%2B961%20%280%29%203%20045%20045" target="_blank" value="+9613045045">+961 (0) 3 045 045</a></span></font></p>
<p class="MsoNormal"><font color="navy" size="3" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 12pt"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt">EcoConsulting (UK) Ltd<br>28 Marshalsea Road<br>London, SE1 1HF<br>Tel: <a href="tel:%2B44%20%280%29%20207%20939%200989" target="_blank" value="+442079390989">+44 (0) 207 939 0989</a><br>
Fax: <a href="tel:%2B44%20%280%29%20207%20939%200981" target="_blank" value="+442079390981">+44 (0) 207 939 0981</a></span></font></p>
<p class="MsoNormal"><font color="navy" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 7.5pt">Website: <a href="http://www.ecoconsulting.net/" target="_blank">www.ecoconsulting.net</a></span></font></p>
<p class="MsoNormal"><font color="navy" size="3" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 12pt"> </span></font></p>
<p style="MARGIN: 0cm 0cm 0pt"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt"> <img border="0" src="cid:image001.jpg@01CC520A.5A4A9690" width="870" height="102"></span></font></p>
</div>
<div>
<div style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt" lang="EN-US">
<hr align="center" size="2" width="100%">
</span></font></div>
<p class="MsoNormal"><b><font size="2" face="Tahoma"><span style="FONT-FAMILY: Tahoma; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US">From:</span></font></b><font size="2" face="Tahoma"><span style="FONT-FAMILY: Tahoma; FONT-SIZE: 10pt" lang="EN-US"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b><span style="FONT-WEIGHT: bold">On Behalf Of </span></b>Brad Robinson<br>
<b><span style="FONT-WEIGHT: bold">Sent:</span></b> 02 August 2011 21:24<br><b><span style="FONT-WEIGHT: bold">To:</span></b> R B; eQUEST Users List<br><b><span style="FONT-WEIGHT: bold">Subject:</span></b> Re: [Equest-users] URGENT: Window U-values: Total window assemblyv/s Glass only</span></font></p>
</div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt">There are, it seems, a multitude of ways people on this forum go about modeling windows. It would be interesting to know, in terms of a LEED review, what others have been required to provide in terms of modeling the windows. Does anyone have experience on the Canadian side of the border what is required? Thanks.</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt">Brad Robinson</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt"> </span></font></p></div>
<div>
<div>
<div style="TEXT-ALIGN: center; BACKGROUND: white" class="MsoNormal" align="center"><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt">
<hr align="center" size="1" width="100%">
</span></font></div>
<p style="MARGIN-BOTTOM: 12pt; BACKGROUND: white" class="MsoNormal"><b><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt; FONT-WEIGHT: bold">From:</span></font></b><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt"> R B <<a href="mailto:slv3sat@gmail.com" target="_blank">slv3sat@gmail.com</a>><br>
<b><span style="FONT-WEIGHT: bold">To:</span></b> eQUEST Users List <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>><br><b><span style="FONT-WEIGHT: bold">Sent:</span></b> Saturday, July 30, 2011 11:29:31 PM<br>
<b><span style="FONT-WEIGHT: bold">Subject:</span></b> Re: [Equest-users] URGENT: Window U-values: Total window assembly v/s Glass only</span></font></p>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">Came across this in eQuest help - basically suggests to use zero frame width.</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">-Rohini</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">Volume 2: Dictionary<span> > </span>Envelope Components<span> > </span>WINDOW<span> > </span>Window Frames and Skylight Curbs</span></font></p>
</div>
<h5 style="BACKGROUND: white"><b><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt">FRAME-WIDTH</span></font></b></h5>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">Projected width of the frame in the plane of the glazing (Figure 27). We recommend that frames be entered only if the frame area is more than 10 percent or so of the glazed area, which is generally only the case in residential applications. The program assumes that the frame width is the same on all sides of the window. If this is not the case, use the average frame width.</span></font></p>
</div>
<p style="MARGIN-BOTTOM: 12pt; BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">On Fri, Jul 29, 2011 at 4:15 PM, Alex Krickx <<a href="mailto:akrickx@seriousenergy.com" target="_blank">akrickx@seriousenergy.com</a>> wrote:</span></font></p>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">Great thread-</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">To answer Vikram’s question - When using WINDOW, you are slightly limited in the output file (for example, if I create an NFRC-type model to figure out U-value for a curtainwall system, I will need to simply the window to export it into a DOE-2 report format). When you do import a WINDOW Report for DOE-2 into eQUEST it does not load any frame information with it – it presents the COG glass performance. My process is to adjust the spacer type and frame width+conductance to make an object that matches what WINDOW tells me my window performance is.</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">I don’t model for LEED, so am less familiar with what is required for that – since I work for a window manufacturer I usually have access to all the data I need to determine frame-inclusive u-value and SHGCs, i.e. no need to rely on 90.1 defaults. </span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">Since the conversation was about using NFRC data – let me ask this question: NFRC data for windows (curtainwall assemblies included) is for a “default” size. I believe for curtainwall a mulled unit is modeled at 2m x 2m (or 78.54” x 78.54”) – as shown below:</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"><img border="0" width="533" height="491"></span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">This is an example, but let’s say that the NFRC value is U-0.34. If your building has a smaller or larger window (which will change the glass-to-frame ratio) the U-value will be different. </span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">Is it still appropriate to use the NFRC value in that case, where it is entered as a frame-inclusive U-factor and SHGC? I’m curious as to how others approach this issue when dealing with models for compliance.</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">Kind regards,</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">Alex Krickx</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#262f13" size="3" face="Times New Roman"><span style="COLOR: #262f13; FONT-SIZE: 12pt" lang="EN-US">Alex Krickx, LEED AP</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="gray" size="2" face="Times New Roman"><span style="COLOR: gray; FONT-SIZE: 11pt" lang="EN-US">Building Energy Specialist</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt" lang="EN-US">Serious Energy, Inc.</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt" lang="EN-US">1250 Elko Dr</span></font><font color="black" size="2"><span style="COLOR: black; FONT-SIZE: 10pt" lang="EN-US">, Sunnyvale, CA 94089</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt" lang="EN-US">(t) <a href="tel:408.541.8124" target="_blank" value="+14085418124">408.541.8124</a></span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt" lang="EN-US"><a href="mailto:akrickx@seriousenergy.com" target="_blank">akrickx@seriousenergy.com</a></span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="1" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 9pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><i><font color="black" size="1" face="Times New Roman"><span style="FONT-STYLE: italic; COLOR: black; FONT-SIZE: 8pt" lang="EN-US">The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments.</span></font></i></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<div style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 0cm; PADDING-RIGHT: 0cm; BORDER-TOP: windowtext 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<div>
<p style="BACKGROUND: white" class="MsoNormal"><b><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US">From:</span></font></b><font color="black" size="2"><span style="COLOR: black; FONT-SIZE: 10pt" lang="EN-US"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b><span style="FONT-WEIGHT: bold">On Behalf Of </span></b>Sami, Vikram<br>
<b><span style="FONT-WEIGHT: bold">Sent:</span></b> Friday, July 29, 2011 1:39 PM<br><b><span style="FONT-WEIGHT: bold">To:</span></b> Robby Oylear; Bill Talbert; Carol Gardner</span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"><br><b><span style="FONT-WEIGHT: bold">Cc:</span></b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b><span style="FONT-WEIGHT: bold">Subject:</span></b> Re: [Equest-users] URGENT: Window U-values: Total window assembly v/s Glass only</span></font></p></div></div></div></div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">Firstly – congratulations to all contributors – I think this is probably the first time (that I recall) that all of the posts on this list have been on a single thread. I couldn’t resist being a part of this so I’m going to add my 2 cents:</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">90.1 baseline values & SHGC are assembly u-values so your frame needs to be calculated into this. To get the derated value – you could either use the handy little XL spreadsheet that comes with the install of eQUEST (under the data\window folder) called eQUEST-DOE2 Glass Library.xls. This gives you COG values <b><u><span style="FONT-WEIGHT: bold">AND</span></u></b> glass+frame NFRC values. They have separate table where it is sorted by U-value and SHGC – I use it all the time (screenshot below). </span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"><img border="0" width="1197" height="134"></span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">So you can select your values in conjunction with the values below from the DOE2 help file to get what you need. </span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div align="center">
<table style="BORDER-COLLAPSE: collapse" border="0" cellspacing="0" cellpadding="0">
<tbody>
<tr>
<td style="BORDER-BOTTOM: windowtext 1pt solid; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 147.6pt; PADDING-RIGHT: 5.4pt; BACKGROUND: aqua; BORDER-TOP: windowtext 1pt solid; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" bgcolor="aqua" valign="top" width="197">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><b><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt; FONT-WEIGHT: bold"><br>Frame Type</span></font></b></p></td>
<td style="BORDER-BOTTOM: windowtext 1pt solid; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 109.8pt; PADDING-RIGHT: 5.4pt; BACKGROUND: aqua; BORDER-TOP: windowtext 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 0cm" bgcolor="aqua" valign="top" width="146">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><b><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt; FONT-WEIGHT: bold">FRAME-CONDUCT (excludes OA film)</span></font></b></p></td>
<td style="BORDER-BOTTOM: windowtext 1pt solid; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 108pt; PADDING-RIGHT: 5.4pt; BACKGROUND: aqua; BORDER-TOP: windowtext 1pt solid; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" bgcolor="aqua" valign="top" width="144">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><b><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt; FONT-WEIGHT: bold"><br>U-value<sup>a</sup></span></font></b></p></td></tr>
<tr>
<td style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 147.6pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="197">
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Thermally unbroken aluminum</span></font></p></div></td>
<td style="PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 109.8pt; PADDING-RIGHT: 5.4pt; PADDING-TOP: 0cm" valign="top" width="146">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">3.037 (17.24)</span></font></p></td>
<td style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 108pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="144">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">1.90 (10.79)</span></font></p></td></tr>
<tr>
<td style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 147.6pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="197">
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Thermally broken aluminum</span></font></p></div></td>
<td style="PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 109.8pt; PADDING-RIGHT: 5.4pt; PADDING-TOP: 0cm" valign="top" width="146">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">1.245 (7.07)</span></font></p></td>
<td style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 108pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="144">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">1.00 (5.68)</span></font></p></td></tr>
<tr>
<td style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 147.6pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="197">
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">External flush glazed aluminum</span></font></p></div></td>
<td style="PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 109.8pt; PADDING-RIGHT: 5.4pt; PADDING-TOP: 0cm" valign="top" width="146">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">0.812 (4.61)</span></font></p></td>
<td style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 108pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="144">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">0.70 (3.97)</span></font></p></td></tr>
<tr>
<td style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 147.6pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="197">
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Wood with or without cladding</span></font></p></div></td>
<td style="PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 109.8pt; PADDING-RIGHT: 5.4pt; PADDING-TOP: 0cm" valign="top" width="146">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">0.434 (2.46)</span></font></p></td>
<td style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 108pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="144">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">0.40 (2.27)</span></font></p></td></tr>
<tr>
<td style="BORDER-BOTTOM: windowtext 1pt solid; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 147.6pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="197">
<div>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">Vinyl</span></font></p></div></td>
<td style="BORDER-BOTTOM: windowtext 1pt solid; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 109.8pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: medium none; PADDING-TOP: 0cm" valign="top" width="146">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">0.319 (1.81)</span></font></p></td>
<td style="BORDER-BOTTOM: windowtext 1pt solid; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 108pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="144">
<p style="TEXT-ALIGN: center" class="MsoNormal" align="center"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">0.30 (1.70)</span></font></p></td></tr>
<tr>
<td style="BORDER-BOTTOM: windowtext 1pt solid; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; PADDING-LEFT: 5.4pt; WIDTH: 365.4pt; PADDING-RIGHT: 5.4pt; BORDER-TOP: medium none; BORDER-RIGHT: windowtext 1pt solid; PADDING-TOP: 0cm" valign="top" width="487" colspan="3">
<div>
<p class="MsoNormal"><sup><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt">a</span></font></sup> U-value includes OA film at 15 mph [6.7 m/s] windspeed<br> FRAME-CONDUCT = [(U-value)<sup>-1</sup> - 0.197]<sup>-1</sup> Btu/ft2-F-h<br>
FRAME-CONDUCT = [(U-value)<sup>-1</sup> - 0.035]<sup>-1</sup> W/m2-K</p></div></td></tr></tbody></table></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><b><font color="#dcaa2c" size="2" face="Times New Roman"><span style="COLOR: #dcaa2c; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US"> </span></font></b></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">Alternately, you can select a COG value to match what you want, set your frame to zero and your spacer to UE-EQ-UC (this will give you a uniform COG conductance across the assembly).</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US">I am curious about LBNL window imports. When you set up your assembly in window – it includes frames, but you import it in as a glass type – should you zero out the frame (as in the second case) if you import from window? </span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><b><font color="#dcaa2c" size="2" face="Times New Roman"><span style="COLOR: #dcaa2c; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US"> </span></font></b></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><b><font color="gray" size="1" face="Times New Roman"><span style="COLOR: gray; FONT-SIZE: 9pt; FONT-WEIGHT: bold" lang="EN-US">Vikram Sami</span></font></b><font color="gray" size="1"><span style="COLOR: gray; FONT-SIZE: 9pt" lang="EN-US">, LEED AP BD+C</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="gray" size="1" face="Times New Roman"><span style="COLOR: gray; FONT-SIZE: 9pt" lang="EN-US">Sustainable Design Analyst</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="gray" size="1" face="Times New Roman"><span style="COLOR: gray; FONT-SIZE: 9pt" lang="EN-US">1315 Peachtree St. NE</span></font><font color="gray" size="1"><span style="COLOR: gray; FONT-SIZE: 9pt" lang="EN-US">, Atlanta, GA 30309</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="gray" size="1" face="Times New Roman"><span style="COLOR: gray; FONT-SIZE: 9pt" lang="EN-US">t: <a href="tel:404-443-7462" target="_blank" value="+14044437462">404-443-7462</a> f: </span></font><font color="gray" size="1"><span style="COLOR: gray; FONT-SIZE: 9pt" lang="ES"><a href="tel:404.892.5823" target="_blank" value="+14048925823">404.892.5823</a> </span></font><font color="gray" size="1"><span style="COLOR: gray; FONT-SIZE: 9pt" lang="EN-US"> e: <a href="mailto:vikram.sami@perkinswill.com" target="_blank">vikram.sami@perkinswill.com</a> </span></font><font color="#1f497d" size="2"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"><a href="http://www.perkinswill.com/" target="_blank"><font color="gray" size="1"><span style="COLOR: gray; FONT-SIZE: 9pt; TEXT-DECORATION: none">www.perkinswill.com</span></font></a></span></font></p>
</div>
<div style="MARGIN-BOTTOM: 3pt">
<p style="BACKGROUND: white" class="MsoNormal"><b><font color="gray" size="1" face="Times New Roman"><span style="COLOR: gray; FONT-SIZE: 9pt; FONT-WEIGHT: bold" lang="EN-US">Perkins+Will.</span></font></b><font color="gray" size="1"><span style="COLOR: gray; FONT-SIZE: 9pt" lang="EN-US"> </span></font><font color="#add425" size="1"><span style="COLOR: #add425; FONT-SIZE: 9pt" lang="EN-US">Ideas + buildings that honor the broader goals of society</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 0cm; PADDING-RIGHT: 0cm; BORDER-TOP: windowtext 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<div>
<p style="BACKGROUND: white" class="MsoNormal"><b><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US">From:</span></font></b><font color="black" size="2"><span style="COLOR: black; FONT-SIZE: 10pt" lang="EN-US"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b><span style="FONT-WEIGHT: bold">On Behalf Of </span></b>Robby Oylear<br>
<b><span style="FONT-WEIGHT: bold">Sent:</span></b> Friday, July 29, 2011 4:18 PM<br><b><span style="FONT-WEIGHT: bold">To:</span></b> Bill Talbert; Carol Gardner<br><b><span style="FONT-WEIGHT: bold">Cc:</span></b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b><span style="FONT-WEIGHT: bold">Subject:</span></b> Re: [Equest-users] URGENT: Window U-values: Total window assembly v/s Glass only</span></font></p></div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">From the 90.1 User's Manual pg 5-12:</span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">"With Addendum 90.1ag (published </span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">with Standard 90.1-2001) glazed wall </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">systems, including glass curtain walls used </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">on large buildings, storefront glazing </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">systems, and other similar products that </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">are assembled at the construction site, as </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">opposed to at the factory, must either be </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">rated using NFRC procedures or the </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">default U-factor, SHGC and VLT from </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">Table A8.2. Since the performance values </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">in Table A8.1A are based on uncoated </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">clear glass in poorly performing metal </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">frame, they do not offer any credit for </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">low-e coatings, thermal break frames or </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">any other advanced feature. In general, </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">values from Table A8.1A will not achieve </span></font></p></div>
</div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">compliance with the fenestration </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">requirements. </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">The NFRC procedure for site-built </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">fenestration is described in NFRC 100. </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">The NFRC ratings are based on computer </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">simulations of various product options at </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">standard sizes. (For curtain walls, the </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">standard size specified is 2000 mm by </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">2000 mm, or approximately 79 in. by 79 </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">in.) Multiple glass options can be included </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">in one simulation matrix. The entire </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">simulation matrix is then validated by a </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">single physical test at the standard size. If </span></font></p>
</div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">the matrix for a product has previously </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">been validated, then a new glass option </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">can be added to the matrix by simulation </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">alone. Simulations and tests must be done </span></font></p></div>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">by an NFRC-accredited simulation and </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">test laboratories." </span></font></p></div></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">Also, the LEED Reference Guide for Green Building Design and Construction, pg 275 specifically references Tables A8.1 and A8.2 or requires that the products be certified and labeled in accordance with NFRC. </span></font></p>
</div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">Not seeing any statements that would allow the modeler to perform their own fenestration assembly performance calculations.</span></font></p>
</div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">-Robby</span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">On Fri, Jul 29, 2011 at 12:02 PM, Bill Talbert <<a href="mailto:btalbert@aeieng.com" target="_blank">btalbert@aeieng.com</a>> wrote:</span></font></p>
</div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 11pt" lang="EN-US">Regarding Omar’s first question, I would also clarify that adding a frame to the baseline is probably not the correct approach unless you are adjusting the U-value to a center of glass value and accounting for the frame and edge effects such that the total fenestration performance is equal to the 90.1 prescribed value.</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="TEXT-INDENT: 36pt; BACKGROUND: white" class="MsoNormal"><font color="#548dd4" size="2" face="Times New Roman"><span style="COLOR: #548dd4; FONT-SIZE: 11pt" lang="EN-US">‘They are silent about frames but I would use one, match the frame width of your proposed window. Use an Aluminum frame with no thermal break.’</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 11pt" lang="EN-US">Baseline Table 5.5-1 through 5.5-8 specify ‘fenestration assembly’ values which include the effect of the frames and edge of glass. Modeling a frame in the Baseline will further degrade the overall fenestration U-value (unless your frame outperforms the glazing) and result in overestimating the savings relative to the fenestration performance. If you use the Table values for your window performance, frames shouldn’t be included. If you include a frame, you should create a 90.1 compliant product using WINDOW and use the appropriate frame and glazing performance values as eQuest inputs such that your overall frame and glazing performance matches the A90.1 Table value.</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 11pt" lang="EN-US">Regards,</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 11pt" lang="EN-US">Bill</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<table style="WIDTH: 355.5pt" border="0" cellpadding="0" width="474">
<tbody>
<tr>
<td style="PADDING-BOTTOM: 0.75pt; PADDING-LEFT: 0.75pt; WIDTH: 125.25pt; PADDING-RIGHT: 0.75pt; PADDING-TOP: 0.75pt" valign="top" width="167">
<div>
<p class="MsoNormal"><b><font color="#660000" size="2" face="Times New Roman"><span style="TEXT-TRANSFORM: uppercase; COLOR: #660000; FONT-SIZE: 10pt; FONT-WEIGHT: bold">Bill Talbert</span></font></b><b><font color="#333333" size="1"><span style="COLOR: #333333; FONT-SIZE: 9pt; FONT-WEIGHT: bold"> </span></font></b><font color="#333333" size="1"><span style="COLOR: #333333; FONT-SIZE: 9pt">PE, LEED® AP<br>
</span></font><font color="#333333" size="2"><span style="TEXT-TRANSFORM: uppercase; COLOR: #333333; FONT-SIZE: 10pt">Sustainable</span></font></p></div></td>
<td style="PADDING-BOTTOM: 0.75pt; PADDING-LEFT: 0.75pt; WIDTH: 7.5pt; PADDING-RIGHT: 0.75pt; PADDING-TOP: 0.75pt" valign="top" width="10">
<div>
<p class="MsoNormal"><font color="#333333" size="1" face="Times New Roman"><span style="COLOR: #333333; FONT-SIZE: 9pt"> </span></font></p></div></td>
<td style="PADDING-BOTTOM: 0.75pt; PADDING-LEFT: 0.75pt; WIDTH: 212.25pt; PADDING-RIGHT: 0.75pt; PADDING-TOP: 0.75pt" valign="top" width="283">
<div>
<p class="MsoNormal"><b><font color="#660000" size="1" face="Times New Roman"><span style="COLOR: #660000; FONT-SIZE: 9pt; FONT-WEIGHT: bold">AEI</span></font></b><font color="#333333" size="1"><span style="COLOR: #333333; FONT-SIZE: 9pt"> | AFFILIATED ENGINEERS, INC. <br>
5802 Research Park Boulevard | Madison, WI 53719<br><br></span></font><font color="#660000" size="1"><span style="COLOR: #660000; FONT-SIZE: 9pt">P: <a href="tel:608.441.6677" target="_blank" value="+16084416677">608.441.6677</a> | C: <a href="tel:608.234.3803" target="_blank" value="+16082343803">608.234.3803</a> | F: <a href="tel:608.238.2614" target="_blank" value="+16082382614">608.238.2614</a></span></font><font color="#333333" size="1"><span style="COLOR: #333333; FONT-SIZE: 9pt"> <br>
</span></font><font color="#660000" size="1"><span style="COLOR: #660000; FONT-SIZE: 9pt"><a href="mailto:btalbert@aeieng.com" target="_blank"><font color="#660000"><span style="COLOR: #660000; TEXT-DECORATION: none">btalbert@aeieng.com</span></font></a> | <b><span style="FONT-WEIGHT: bold"><a href="http://www.aeieng.com/" target="_blank"><font color="#660000"><span style="COLOR: #660000; TEXT-DECORATION: none">www.aeieng.com</span></font></a></span></b></span></font><font color="#333333" size="1"><span style="COLOR: #333333; FONT-SIZE: 9pt"> </span></font></p>
</div></td></tr></tbody></table>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#1f497d" size="2" face="Times New Roman"><span style="COLOR: #1f497d; FONT-SIZE: 11pt" lang="EN-US"> </span></font></p></div>
<div style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0cm; PADDING-LEFT: 0cm; PADDING-RIGHT: 0cm; BORDER-TOP: windowtext 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<div>
<p style="BACKGROUND: white" class="MsoNormal"><b><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US">From:</span></font></b><font color="black" size="2"><span style="COLOR: black; FONT-SIZE: 10pt" lang="EN-US"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b><span style="FONT-WEIGHT: bold">On Behalf Of </span></b>Carol Gardner<br>
<b><span style="FONT-WEIGHT: bold">Sent:</span></b> Friday, July 29, 2011 1:35 PM<br><b><span style="FONT-WEIGHT: bold">To:</span></b> Robby Oylear</span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"><br><b><span style="FONT-WEIGHT: bold">Cc:</span></b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a></span></font></p>
</div></div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><b><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt; FONT-WEIGHT: bold" lang="EN-US">Subject:</span></font></b><font color="black"><span style="COLOR: black" lang="EN-US"> Re: [Equest-users] URGENT: Window U-values: Total window assembly v/s Glass only</span></font></p>
</div></div></div></div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">This came off of the Window website:</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">WINDOW 6.3 is a publicly available computer program for calculating total window thermal performance indices (i.e. U-values, solar heat gain coefficients, shading coefficients, and visible transmittances). WINDOW 6.3 provides a versatile heat transfer analysis method consistent with the updated rating procedure developed by the National Fenestration Rating Council (NFRC) that is consistent with the ISO 15099 standard. The program can be used to design and develop new products, to assist educators in teaching heat transfer through windows, and to help public officials in developing building energy codes. </span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div>
<div style="MARGIN-BOTTOM: 12pt">
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">On Fri, Jul 29, 2011 at 11:26 AM, Robby Oylear <<a href="mailto:robbyoylear@gmail.com" target="_blank">robbyoylear@gmail.com</a>> wrote:</span></font></p>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">Carol,</span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">I have to take exception to this:</span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">"As far as NFRC, your Solarban glass data is NFRC rated which should be good enough, I think. It's rare in commercial buildings to have a rating for the entire window."</span></font></p>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">From my first response: </span></font></p></div></div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt" lang="EN-US">In order to meet LEED EAp2 Minimum Energy Performance, the project must comply with all mandatory provisions of ASHRAE 90.1-2007. Section 5.4.2 Fenestration and Doors requires that fenestration performance be determined per section 5.8.2. Section 5.8.2.4 U-factor requires that the U-factor for the overall fenestration area (including framing) be determined in accordance with NFRC 100. If you do not have NFRC data available, values from section A8.2 are the only acceptable alternative.</span></font></p>
</div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">NFRC values for the glazing alone not "good enough". This is exactly what the reviewer is trying to get at.</span></font></p>
</div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">I'd hardly call NFRC certification rare. In the State of Washington NFRC certification has been required for all glazing assemblies for over 10 years. </span></font></p>
</div></div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">How do you justify certifying that your projects have met the mandatory provisions of ASHRAE 90.1 without NFRC data?</span></font></p>
</div></div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div>
<div>
<div style="MARGIN-TOP: 1pt">
<p style="BACKGROUND: white" class="MsoNormal"><a name="131903e5b78ead2b_13177c071350ddb0_1317746f9272af25_131772"><b><font color="#632423" size="2" face="Times New Roman"><span style="COLOR: #632423; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US">Robby Oylear, LEED</span></font></b></a><b><sup><font color="#632423" size="2"><span style="COLOR: #632423; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US">®</span></font></sup></b><b><font color="#632423" size="2"><span style="COLOR: #632423; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US"> AP BD+C</span></font></b></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><i><font color="black" size="1" face="Times New Roman"><span style="FONT-STYLE: italic; COLOR: black; FONT-SIZE: 8pt" lang="EN-US">Mechanical Project Engineer</span></font></i></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><i><font color="black" size="1" face="Times New Roman"><span style="FONT-STYLE: italic; COLOR: black; FONT-SIZE: 8pt" lang="EN-US">Energy Analyst</span></font></i></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><i><font color="black" size="1" face="Times New Roman"><span style="FONT-STYLE: italic; COLOR: black; FONT-SIZE: 8pt" lang="EN-US"> </span></font></i></p></div>
<div>
<p style="LINE-HEIGHT: 115%; BACKGROUND: white" class="MsoNormal"><b><font color="#632423" size="1" face="Times New Roman"><span style="LINE-HEIGHT: 115%; COLOR: #632423; FONT-SIZE: 8pt; FONT-WEIGHT: bold" lang="EN-US">D</span></font></b><font color="#1f497d" size="1"><span style="LINE-HEIGHT: 115%; COLOR: #1f497d; FONT-SIZE: 8pt" lang="EN-US"> </span></font><font color="black" size="1"><span style="LINE-HEIGHT: 115%; COLOR: black; FONT-SIZE: 8pt" lang="EN-US"><a href="tel:206-788-4571" target="_blank" value="+12067884571">206-788-4571</a> |</span></font><font color="#bfab7f" size="1"><span style="LINE-HEIGHT: 115%; COLOR: #bfab7f; FONT-SIZE: 8pt" lang="EN-US"> </span></font><b><font color="#632423" size="1"><span style="LINE-HEIGHT: 115%; COLOR: #632423; FONT-SIZE: 8pt; FONT-WEIGHT: bold" lang="EN-US">C</span></font></b><font color="#a50021" size="1"><span style="LINE-HEIGHT: 115%; COLOR: #a50021; FONT-SIZE: 8pt" lang="EN-US"> </span></font><font color="black" size="1"><span style="LINE-HEIGHT: 115%; COLOR: black; FONT-SIZE: 8pt" lang="EN-US"><a href="tel:206-354-2721" target="_blank" value="+12063542721">206-354-2721</a></span></font></p>
</div>
<div>
<p style="LINE-HEIGHT: 115%; BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="LINE-HEIGHT: 115%; COLOR: black; FONT-SIZE: 12pt" lang="EN-US"><a href="http://www.rushingco.com/" target="_blank"><b><i><font color="#632423" size="1"><span style="LINE-HEIGHT: 115%; FONT-STYLE: italic; COLOR: #632423; FONT-SIZE: 8pt; FONT-WEIGHT: bold">www.rushingco.com</span></font></i></b></a></span></font></p>
</div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div></div>
<div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">On Fri, Jul 29, 2011 at 11:12 AM, Carol Gardner <<a href="mailto:cmg750@gmail.com" target="_blank">cmg750@gmail.com</a>> wrote:</span></font></p>
</div>
<div style="MARGIN-BOTTOM: 12pt">
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">On Thu, Jul 28, 2011 at 5:40 AM, Omar Katanani <<a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a>> wrote:</span></font></p>
</div></div>
<blockquote style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; MARGIN: 5pt 0cm 5pt 4.8pt; PADDING-LEFT: 6pt; PADDING-RIGHT: 0cm; BORDER-TOP: medium none; BORDER-RIGHT: medium none; PADDING-TOP: 0cm">
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt">Dear all,</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt">Thank you for your responses.</span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt"> </span></font></p></div>
<ol type="1">
<li style="BACKGROUND: white; COLOR: navy" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="FONT-SIZE: 10pt">Are the NFRC testing and the values in table A8.2 used for the Baseline, Proposed, or both scenarios?</span></font> </li>
</ol></div></div></div></blockquote>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">For the baseline windows, Appendix G gives the following instructions:<br>
Fenestration<br>U-factors shall match the appropriate requirements in Tables 5.5-1 through<br>5.5-8. Fenestration SHGC shall match the appropriate requirements in Tables<br>5.5-1 through 5.5-8. <br>They are silent about frames but I would use one, match the frame width of your proposed window. Use an Aluminum frame with no thermal break.</span></font></p>
</div></div>
<div>
<blockquote style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; MARGIN: 5pt 0cm 5pt 4.8pt; PADDING-LEFT: 6pt; PADDING-RIGHT: 0cm; BORDER-TOP: medium none; BORDER-RIGHT: medium none; PADDING-TOP: 0cm">
<div>
<div>
<div style="MARGIN-LEFT: 18pt">
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt"> </span></font></p></div>
<ol type="1" start="2">
<li style="BACKGROUND: white; COLOR: navy" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="FONT-SIZE: 10pt">Let’s say I do not have NFRC test results and decide to use the values in table A8.2. For a clear double glazed and metal frame type, I get an assembly U-factor of 5.1. How can I input this into eQUEST? As far as I know, I can enter the glass properties and the frame properties. Do I have to play with the glass properties and check the LV-D report for the calculated Assembly u-value?</span></font> </li>
</ol></div></div></blockquote></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">A U of 5.1 does not make sense. Are you sure this isn't R?<br>
</span></font></p></div></div>
<div>
<blockquote style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; MARGIN: 5pt 0cm 5pt 4.8pt; PADDING-LEFT: 6pt; PADDING-RIGHT: 0cm; BORDER-TOP: medium none; BORDER-RIGHT: medium none; PADDING-TOP: 0cm">
<div>
<div>
<div>
<p style="TEXT-INDENT: 36pt; BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt">Similarly, for the baseline, Tables 5.5-1 to 5.5-8 of ASHRAE 90.1 provide the assembly u-values for vertical glazing. How can I enter these values into eQUEST?</span></font></p>
</div>
<div style="MARGIN-LEFT: 18pt">
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt"> </span></font></p></div>
<ol type="1" start="3">
<li style="BACKGROUND: white; COLOR: navy" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="FONT-SIZE: 10pt">I am attaching the specs of the proposed glazing. These numbers are for the glass only (note that the u-values reported are NFRC ones). Additionally, I know that the frame will be aluminium. Do I still need NFRC U-values for the whole assembly, or is the NFRC usually for the glass only? If yes, how can I calculate the whole assembly U-value (given that eQUEST doesn’t have the ability to calculate this)</span></font> </li>
</ol></div></div></blockquote></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"><br><span style="BACKGROUND: white">For your proposed building I highly recommend you use LBNL's Window program. In it you can select your window type, e.g. casement, picture, etc,, select your glass from their glass library, which is huge and definitely includes Solarban, and then model your frame using whatever information the architect gives you related to thermal breaks and spacers. After you run your window in the program you can select to save it to a DOE 2 report which will automatically go into your DOE 2 Window folder. Then you just have to select it from the pull down menu.</span><br>
<br><span style="BACKGROUND: white">Otherwise, input your glass values, as you are already, <u>and</u> input your frame data, the same data you got from your architect, and model it that way. When you look at your LV-D report you will likely see a variety of U values. That's because they will vary based on window size.due to the frame effect. You need to have a frame.</span><br>
<br><span style="BACKGROUND: white">As far as NFRC, your Solarban glass data is NFRC rated which should be good enough, I think. It's rare in commercial buildings to have a rating for the entire window.</span><br><br>
<span style="BACKGROUND: white">Carol</span></span></font></p></div></div>
<div>
<div>
<blockquote style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; MARGIN: 5pt 0cm 5pt 4.8pt; PADDING-LEFT: 6pt; PADDING-RIGHT: 0cm; BORDER-TOP: medium none; BORDER-RIGHT: medium none; PADDING-TOP: 0cm">
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt">Thanks for clarifying this, as my project is outside the US and we are not too familiar with standards such as NFRC.</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt">Best regards,</span></font></p></div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt">Omar</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt">___________________________</span></font><font color="navy"><span style="COLOR: navy"> </span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt">Omar Katanani</span></font><font color="navy"><span style="COLOR: navy"><br></span></font><font color="navy" size="2"><span style="COLOR: navy; FONT-SIZE: 10pt">Sustainable Design Engineer</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt">Email: <a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a></span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="3" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="1" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">EcoConsulting (Lebanon)</span></font></p></div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="1" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">Nahas</span></font><font color="navy" size="1"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US"> Building</span></font><font color="navy" size="1"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">, 4<sup>th</sup> floor</span></font></p>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="1" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">4 St-Maron Street</span></font><font color="navy" size="1"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US"> / Georges Haddad Avenue</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="1" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">Postal Code: 2028 5806 SAIFI</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="1" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">Beirut</span></font><font color="navy" size="1"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">, Lebanon</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="1" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-US">Tel: </span></font><font color="navy" size="1"><span style="COLOR: navy; FONT-SIZE: 7.5pt">+961 (0) 1 971 266<br>
Mobile: <a href="tel:%2B961%20%280%29%203%20045%20045" target="_blank" value="+9613045045">+961 (0) 3 045 045</a></span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="3" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="1" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 7.5pt">EcoConsulting (UK) Ltd<br>28 Marshalsea Road<br>London, SE1 1HF<br>Tel: <a href="tel:%2B44%20%280%29%20207%20939%200989" target="_blank" value="+442079390989">+44 (0) 207 939 0989</a><br>
Fax: <a href="tel:%2B44%20%280%29%20207%20939%200981" target="_blank" value="+442079390981">+44 (0) 207 939 0981</a></span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="1" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 7.5pt">Website: <a href="http://www.ecoconsulting.net/" target="_blank">www.ecoconsulting.net</a></span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="3" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="navy" size="2" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 10pt"> <img border="0" width="870" height="102"></span></font></p></div></div></div>
<div>
<div style="TEXT-ALIGN: center; BACKGROUND: white" class="MsoNormal" align="center"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US">
<hr align="center" size="2" width="100%">
</span></font></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><b><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-US">From:</span></font></b><font color="black" size="2"><span style="COLOR: black; FONT-SIZE: 10pt" lang="EN-US"> Robby Oylear [mailto:<a href="mailto:robbyoylear@gmail.com" target="_blank">robbyoylear@gmail.com</a>] <br>
<b><span style="FONT-WEIGHT: bold">Sent:</span></b> 28 July 2011 00:53<br><b><span style="FONT-WEIGHT: bold">To:</span></b> Omar Katanani<br><b><span style="FONT-WEIGHT: bold">Cc:</span></b> Brad Robinson; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a></span></font></p>
</div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="2" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 10pt"><br><b><span style="FONT-WEIGHT: bold">Subject:</span></b> Re: [Equest-users] URGENT: Window U-values: Total window assembly v/s Glass only</span></font></p>
</div></div></div></div>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">Omar,</span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">To directly answer your question:</span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">"</span></font><font color="navy" size="1"><span style="COLOR: navy; FONT-SIZE: 9pt">I’m assuming that, given that I entered the u-values for the glass only, and then I entered information about the frame, then I need not worry about any conversions in U-values, <u>since eQUEST has all the necessary information to calculate the equivalent u-value of the whole pane + frame assembly,</u>right?</span></font><font color="black"><span style="COLOR: black">"</span></font></p>
</div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">No. Your method will result in an assembly U-value based on your input glass conductance and whatever default frame properties that the eQUEST wizard will use. I have never tried to let eQUEST determine an assembly value, as NFRC values are required for LEED and code compliance studies. I would not be surprised if the values eQUEST is calculating (shown in LV-D and LV-E reports like previously mentioned) are much different than what you'll actually see in the test results.</span></font></p>
</div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">Again, NFRC values are a LEED requirement, so unless you're just doing preliminary analysis for a client, you need to receive NFRC simulation reports or certified product directory numbers in accordance with NFRC 100.</span></font></p>
</div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div></div>
<div>
<div style="MARGIN-TOP: 1pt">
<p style="BACKGROUND: white" class="MsoNormal"><b><font color="#632423" size="2" face="Times New Roman"><span style="COLOR: #632423; FONT-SIZE: 10pt; FONT-WEIGHT: bold">Robby Oylear, LEED<sup>®</sup> AP BD+C</span></font></b></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><i><font color="black" size="1" face="Times New Roman"><span style="FONT-STYLE: italic; COLOR: black; FONT-SIZE: 8pt">Mechanical Project Engineer</span></font></i></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><i><font color="black" size="1" face="Times New Roman"><span style="FONT-STYLE: italic; COLOR: black; FONT-SIZE: 8pt">Energy Analyst</span></font></i></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><i><font color="black" size="1" face="Times New Roman"><span style="FONT-STYLE: italic; COLOR: black; FONT-SIZE: 8pt"> </span></font></i></p></div>
<div>
<p style="LINE-HEIGHT: 115%; BACKGROUND: white" class="MsoNormal"><b><font color="#632423" size="1" face="Times New Roman"><span style="LINE-HEIGHT: 115%; COLOR: #632423; FONT-SIZE: 8pt; FONT-WEIGHT: bold">D</span></font></b><font color="#1f497d" size="1"><span style="LINE-HEIGHT: 115%; COLOR: #1f497d; FONT-SIZE: 8pt"> </span></font><font color="black" size="1"><span style="LINE-HEIGHT: 115%; COLOR: black; FONT-SIZE: 7.5pt"><a href="tel:206-788-4571" target="_blank" value="+12067884571">206-788-4571</a> |</span></font><font color="#bfab7f" size="1"><span style="LINE-HEIGHT: 115%; COLOR: #bfab7f; FONT-SIZE: 8pt"> </span></font><b><font color="#632423" size="1"><span style="LINE-HEIGHT: 115%; COLOR: #632423; FONT-SIZE: 8pt; FONT-WEIGHT: bold">C</span></font></b><font color="#a50021" size="1"><span style="LINE-HEIGHT: 115%; COLOR: #a50021; FONT-SIZE: 8pt"> </span></font><font color="black" size="1"><span style="LINE-HEIGHT: 115%; COLOR: black; FONT-SIZE: 7.5pt"><a href="tel:206-354-2721" target="_blank" value="+12063542721">206-354-2721</a></span></font></p>
</div>
<div>
<p style="LINE-HEIGHT: 115%; BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="LINE-HEIGHT: 115%; COLOR: black; FONT-SIZE: 12pt"><a href="http://www.rushingco.com/" target="_blank"><b><i><font color="#632423" size="1"><span style="LINE-HEIGHT: 115%; FONT-STYLE: italic; COLOR: #632423; FONT-SIZE: 8pt; FONT-WEIGHT: bold">www.rushingco.com</span></font></i></b></a></span></font></p>
</div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">On Wed, Jul 27, 2011 at 2:44 PM, <<a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a>> wrote:</span></font></p>
</div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">Dear Robby,<br><br>Yes, I am modeling for LEED purposes.<br>I'll look into A8.2. But at least, is my method correct for the proposed scenario?<br>
<br>Brad: I think you need to enter the center of glass u-value in the "Glass Type", and then enter the frame properties in the "Window" properties...<br><br>Best,<br>Omar</span></font></p></div>
<div>
<div style="MARGIN-BOTTOM: 12pt">
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"><br><br>Quoting Brad Robinson <<a href="mailto:brad.robinson@yahoo.com" target="_blank">brad.robinson@yahoo.com</a>>:</span></font></p>
</div></div>
<blockquote style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; MARGIN: 5pt 0cm 5pt 4.8pt; PADDING-LEFT: 6pt; PADDING-RIGHT: 0cm; BORDER-TOP: medium none; BORDER-RIGHT: medium none; PADDING-TOP: 0cm">
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"><br><br>Is the u-value listed for a manufacturer and specific model on the NRCAN website centre of glass or overall assembly? Many windows are custom made to suit so I am unclear if each individual custom window would need to be tested.<br>
<br><br><br>In eQuest, when entering the window, if the u-value represents the whole window, including frame, do you need to enter a frame width, conductance etc as well under the Window Frame section under Window Properties? Thanks.<br>
<br><br>Brad Robinson<br><br><br><br>________________________________<br>From: Robby Oylear <<a href="mailto:robbyoylear@gmail.com" target="_blank">robbyoylear@gmail.com</a>><br>To: Omar Katanani <<a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a>><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>Sent: Wednesday, July 27, 2011 12:32:08 PM<br>Subject: Re: [Equest-users] URGENT: Window U-values: Total window assembly v/s Glass only<br>
<br><br>Omar,<br><br>The answer depends on the purpose of your study. If you're trying to get results for a client on the impact of the glazing on their energy performance, this may be adequate. Make sure you've entered in the framing information properly (metal vs. non-metal).<br>
<br>I'd recommend opening up your simulation output results file (xxxx.SIM) and going to the either the last page of the LV-D report or sort through your LV-E report to see what value eQUEST has calculated. Compare these values to the ASHRAE Fundamentals results for overall assembly values including frame to see how close you've come. I would not blindly trust that eQUEST will give you an appropriate overall assembly value based on entering only the center of glass number.<br>
<br>However, if this is for a LEED study, this is not adequate. This an excerpt from an e-mail I sent out recently regarding LEED and NFRC requirements.<br><br>In order to meet LEED EAp2 Minimum Energy Performance, the project must comply with all mandatory provisions of ASHRAE 90.1-2007. Section 5.4.2 Fenestration and Doors requires that fenestration performance be determined per section 5.8.2. Section 5.8.2.4 U-factor requires that the U-factor for the overall fenestration area (including framing) be determined in accordance with NFRC 100. If you do not have NFRC data available, values from section A8.2 are the only acceptable alternative.<br>
<br>Robby Oylear, LEED®AP BD+C<br>Mechanical Project Engineer<br>Energy Analyst<br> </span></font></p></div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">D206-788-4571 |C206-354-2721</span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"><br><a href="http://www.rushingco.com/" target="_blank">www.rushingco.com</a><br>
<br><br><br><br><br>On Wed, Jul 27, 2011 at 8:14 AM, Omar Katanani <<a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a>> wrote:<br><br>Dear all,</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> <br>I have a small question regarding entering</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">window properties to eQUEST:</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> <br>I have read a lot of emails in the forum</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">discussing NFRC testing, LBNL Window 5 import, and other topics that I haven?t<br>
paid attention to before.</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> <br>The way I modelled my windows is the</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">following:</span></font></p></div></div>
<blockquote style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; MARGIN: 5pt 0cm 5pt 4.8pt; PADDING-LEFT: 6pt; PADDING-RIGHT: 0cm; BORDER-TOP: medium none; BORDER-RIGHT: medium none; PADDING-TOP: 0cm">
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> <br> 1. I have manufacturer?s specifications listing the glass U-values, not the total assembly.<br>
2. In the ?Glass Types? (eQUEST Detailed Mode), I created glass types, and entered the glass conductance, visible transmittance, SC, and emissivity from the manufacturer?s details I have.<br> 3. When creating windows, I specify which glass type (from the ones I created in step 2), in addition to the frame width and conductance.</span></font></p>
</div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"><br> <br>I?m assuming that, given that I</span></font></p></div></div></blockquote>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">entered the u-values for the glass only, and then I entered information about<br>
the frame, then I need not worry about any conversions in U-values, since<br>eQUEST has all the necessary information to calculate the equivalent u-value of<br>the whole pane + frame assembly, right?</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> <br>I appreciate your feedback / comments</span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">today if possible, as this has become really urgent!</span></font></p></div></div>
<blockquote style="BORDER-BOTTOM: medium none; BORDER-LEFT: windowtext 1pt solid; PADDING-BOTTOM: 0cm; MARGIN: 5pt 0cm 5pt 4.8pt; PADDING-LEFT: 6pt; PADDING-RIGHT: 0cm; BORDER-TOP: medium none; BORDER-RIGHT: medium none; PADDING-TOP: 0cm">
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> <br>Many thanks,<br>Omar<br>___________________________<br>Omar Katanani<br>
Sustainable Design Engineer<br>Email: <a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a><br> <br>EcoConsulting (Lebanon)</span></font></p></div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">NahasBuilding, 4th floor</span></font></p></div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"><br>4 St-Maron Street/ Georges Haddad Avenue<br>Postal Code: 2028 5806</span></font></p>
</div></div></blockquote>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">SAIFI</span></font></p></div>
<div style="MARGIN-BOTTOM: 12pt">
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt">Beirut</span></font><font color="black"><span style="COLOR: black">, Lebanon</span></font><br>
<font color="black"><span style="COLOR: black">Tel: <a href="tel:%2B961%20%280%29%201%20971%20266" target="_blank" value="+9611971266">+961 (0) 1 971 266</a><br>Mobile: <a href="tel:%2B961%20%280%29%203%20045%20045" target="_blank" value="+9613045045">+961 (0) 3 045 045</a><br>
<br>EcoConsulting (UK) Ltd<br>28 Marshalsea Road<br>London, SE1 1HF<br>Tel: <a href="tel:%2B44%20%280%29%20207%20939%200989" target="_blank" value="+442079390989">+44 (0) 207 939 0989</a><br>Fax: <a href="tel:%2B44%20%280%29%20207%20939%200981" target="_blank" value="+442079390981">+44 (0) 207 939 0981</a><br>
Website: <a href="http://www.ecoconsulting.net/" target="_blank">www.ecoconsulting.net</a><br> <br> <br> <br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span></font></p></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"><br>_______________________________________________<br>Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span></font></p>
</div></div></blockquote>
<div>
<div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"><br><br>_______________________________________________<br>Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span></font></p>
</div></div></div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div></div></div></div></div></div>
<div style="MARGIN-BOTTOM: 12pt">
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"><br>_______________________________________________<br>Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span></font></p>
</div></blockquote></div></div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="#888888" size="3" face="Times New Roman"><span style="COLOR: #888888; FONT-SIZE: 12pt" lang="EN-US"><br><br clear="all"><br>-- <br>Carol Gardner PE</span></font></p>
</div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div></div></div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"><br><br clear="all"><br>-- <br>Carol Gardner PE</span></font></p>
</div></div></div></div></div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"> </span></font></p></div></div>
<div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt" lang="EN-US"><br></span></font><font color="gray" size="1"><span style="COLOR: gray; FONT-SIZE: 7.5pt" lang="EN-US">This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.</span></font></p>
</div></div></div></div></div>
<p style="MARGIN-BOTTOM: 12pt; BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"><br>_______________________________________________<br>Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span></font></p>
</div>
<p style="BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"> </span></font></p></div>
<p style="MARGIN-BOTTOM: 12pt; BACKGROUND: white" class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="COLOR: black; FONT-SIZE: 12pt"><br>_______________________________________________<br>Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></span></font></p></div></div></div></div></div><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>