<br><br><div class="gmail_quote">On Thu, Jul 28, 2011 at 5:40 AM, Omar Katanani <span dir="ltr"><<a href="mailto:omar@ecoconsulting.net">omar@ecoconsulting.net</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<div link="blue" vlink="blue" lang="EN-GB">
<div>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy">Dear all,</span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy"> </span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy">Thank you for your responses.</span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy"> </span></font></p>
<ol style="margin-top:0cm" start="1" type="1">
<li class="MsoNormal" style="color:navy"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial">Are the NFRC testing and the
values in table A8.2 used for the Baseline, Proposed, or both scenarios?</span></font></li></ol></div></div></blockquote><div style="background-color: rgb(255, 255, 255);">For the baseline windows, Appendix G gives the following instructions:<br>
Fenestration<br>U-factors shall match the appropriate requirements in Tables 5.5-1 through<br>5.5-8. Fenestration SHGC shall match the appropriate requirements in Tables<br>5.5-1 through 5.5-8. <br>They are silent about frames but I would use one, match the frame width of your proposed window. Use an Aluminum frame with no thermal break.<br>
</div><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;"><div link="blue" vlink="blue" lang="EN-GB"><div><ol style="margin-top: 0cm; background-color: rgb(255, 255, 255);" start="1" type="1">
</ol>
<p class="MsoNormal" style="margin-left:18.0pt"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy"> <span style="background-color: rgb(0, 0, 0);"></span></span></font></p>
<ol style="margin-top:0cm" start="2" type="1">
<li class="MsoNormal" style="color:navy"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial">Let’s say I do not have
NFRC test results and decide to use the values in table A8.2. For a clear
double glazed and metal frame type, I get an assembly U-factor of 5.1. How
can I input this into eQUEST? As far as I know, I can enter the glass
properties and the frame properties. Do I have to play with the glass
properties and check the LV-D report for the calculated Assembly u-value?</span></font></li></ol></div></div></blockquote><div>A U of 5.1 does not make sense. Are you sure this isn't R?<br> </div><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div link="blue" vlink="blue" lang="EN-GB"><div><ol style="margin-top: 0cm;" start="2" type="1">
</ol>
<p class="MsoNormal" style="text-indent:36.0pt"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy">Similarly,
for the baseline, Tables 5.5-1 to 5.5-8 of ASHRAE 90.1 provide the assembly
u-values for vertical glazing. How can I enter these values into eQUEST?</span></font></p>
<p class="MsoNormal" style="margin-left:18.0pt"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy"> </span></font></p>
<ol style="margin-top:0cm" start="3" type="1">
<li class="MsoNormal" style="color:navy"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial">I am attaching the specs of the
proposed glazing. These numbers are for the glass only (note that the
u-values reported are NFRC ones). Additionally, I know that the frame will
be aluminium. Do I still need NFRC U-values for the whole assembly, or is
the NFRC usually for the glass only? If yes, how can I calculate the whole
assembly U-value (given that eQUEST doesn’t have the ability to
calculate this)</span></font></li></ol></div></div></blockquote><div><br><span style="background-color: rgb(255, 255, 255);">For your proposed building I highly recommend you use LBNL's Window program. In it you can select your window type, e.g. casement, picture, etc,, select your glass from their glass library, which is huge and definitely includes Solarban, and then model your frame using whatever information the architect gives you related to thermal breaks and spacers. After you run your window in the program you can select to save it to a DOE 2 report which will automatically go into your DOE 2 Window folder. Then you just have to select it from the pull down menu.</span><br style="background-color: rgb(255, 255, 255);">
<br style="background-color: rgb(255, 255, 255);"><span style="background-color: rgb(255, 255, 255);">Otherwise, input your glass values, as you are already, </span><u style="background-color: rgb(255, 255, 255);">and</u><span style="background-color: rgb(255, 255, 255);"> input your frame data, the same data you got from your architect, and model it that way. When you look at your LV-D report you will likely see a variety of U values. That's because they will vary based on window size.due to the frame effect. You need to have a frame.</span><br style="background-color: rgb(255, 255, 255);">
<br style="background-color: rgb(255, 255, 255);"><span style="background-color: rgb(255, 255, 255);">As far as NFRC, your Solarban glass data is NFRC rated which should be good enough, I think. It's rare in commercial buildings to have a rating for the entire window.</span><br style="background-color: rgb(255, 255, 255);">
<br style="background-color: rgb(255, 255, 255);"><span style="background-color: rgb(255, 255, 255);">Carol</span><br style="background-color: rgb(255, 255, 255);"></div><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div link="blue" vlink="blue" lang="EN-GB"><div><ol style="margin-top: 0cm; background-color: rgb(255, 255, 255);" start="3" type="1">
</ol>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy"> </span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy">Thanks for clarifying this, as my project
is outside the US and we are not too familiar with standards such as NFRC.</span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy"> </span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy">Best regards,</span></font></p>
<div><div class="im">
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy">Omar</span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy">___________________________</span></font><font color="navy"><span style="color:navy"> </span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy">Omar Katanani</span></font><font color="navy"><span style="color:navy"><br>
</span></font><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy">Sustainable Design Engineer</span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy">Email: <a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a></span></font></p>
<p class="MsoNormal"><font color="navy" face="Times New Roman" size="3"><span style="font-size:12.0pt;color:navy"> </span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy" lang="EN-US">EcoConsulting (Lebanon)</span></font></p>
</div><p class="MsoNormal"><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy" lang="EN-US">Nahas</span></font><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy" lang="EN-US"> Building</span></font><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy" lang="EN-US">, 4<sup>th</sup> floor</span></font></p>
<div class="im">
<p class="MsoNormal"><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy" lang="EN-US">4 St-Maron Street</span></font><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy" lang="EN-US"> / Georges Haddad Avenue</span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy" lang="EN-US">Postal Code: 2028 5806
SAIFI</span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy" lang="EN-US">Beirut</span></font><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy" lang="EN-US">, Lebanon</span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy" lang="EN-US">Tel: </span></font><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy"><a href="tel:%2B961%20%280%29%201%20971%20266" value="+9611971266" target="_blank">+961 (0) 1 971 266</a><br>
Mobile: <a href="tel:%2B961%20%280%29%203%20045%20045" value="+9613045045" target="_blank">+961 (0) 3 045 045</a></span></font></p>
<p class="MsoNormal"><font color="navy" face="Times New Roman" size="3"><span style="font-size:12.0pt;color:navy"> </span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy">EcoConsulting (UK) Ltd<br>
28 Marshalsea Road<br>
London, SE1 1HF<br>
Tel: <a href="tel:%2B44%20%280%29%20207%20939%200989" value="+442079390989" target="_blank">+44 (0) 207 939 0989</a><br>
Fax: <a href="tel:%2B44%20%280%29%20207%20939%200981" value="+442079390981" target="_blank">+44 (0) 207 939 0981</a></span></font></p>
<p class="MsoNormal"><font color="navy" face="Arial" size="1"><span style="font-size:7.5pt;font-family:Arial;color:navy">Website: <a href="http://www.ecoconsulting.net/" target="_blank">www.ecoconsulting.net</a></span></font></p>
<p class="MsoNormal"><font color="navy" face="Times New Roman" size="3"><span style="font-size:12.0pt;color:navy"> </span></font></p>
<p style="margin:0cm;margin-bottom:.0001pt"><font color="navy" face="Arial" size="2"><span style="font-size:10.0pt;font-family:Arial;color:navy"> <img src="cid:image001.jpg@01CC4D3C.3C1494A0" border="0" height="102" width="870"></span></font></p>
</div></div>
<div>
<div class="MsoNormal" style="text-align:center" align="center"><font face="Times New Roman" size="3"><span style="font-size:12.0pt" lang="EN-US">
<hr align="center" size="2" width="100%">
</span></font></div>
<p class="MsoNormal"><b><font face="Tahoma" size="2"><span style="font-size:10.0pt;font-family:Tahoma;font-weight:bold" lang="EN-US">From:</span></font></b><font face="Tahoma" size="2"><span style="font-size:10.0pt;font-family:Tahoma" lang="EN-US">
Robby Oylear [mailto:<a href="mailto:robbyoylear@gmail.com" target="_blank">robbyoylear@gmail.com</a>] <br>
<b><span style="font-weight:bold">Sent:</span></b> 28 July 2011 00:53<br>
<b><span style="font-weight:bold">To:</span></b> Omar Katanani<br>
<b><span style="font-weight:bold">Cc:</span></b> Brad Robinson;
<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a></span></font></p><div><div><font face="Tahoma" size="2"></font></div><div class="h5"><font face="Tahoma" size="2"><br>
<b><span style="font-weight:bold">Subject:</span></b> Re: [Equest-users]
URGENT: Window U-values: Total window assembly v/s Glass only</font></div></div><p></p>
</div><div><div></div><div class="h5">
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> </span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">Omar,</span></font></p>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> </span></font></p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">To directly answer your question:</span></font></p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> </span></font></p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">"</span></font><span><font color="navy" face="Arial" size="1"><span style="font-size:9.0pt;font-family:Arial;color:navy">I’m assuming that, given that I entered the u-values for the
glass only, and then I entered information about the frame, then I need not
worry about any conversions in U-values, <u>since eQUEST has all the
necessary information to calculate the equivalent u-value of the whole pane +
frame assembly,</u>right?</span></font></span>"</p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> </span></font></p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">No. Your method will result in an assembly U-value based on your
input glass conductance and whatever default frame properties that the eQUEST
wizard will use. I have never tried to let eQUEST determine an assembly
value, as NFRC values are required for LEED and code compliance studies.
I would not be surprised if the values eQUEST is calculating (shown in
LV-D and LV-E reports like previously mentioned) are much different than what
you'll actually see in the test results.</span></font></p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> </span></font></p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">Again, NFRC values are a LEED requirement, so unless you're just doing
preliminary analysis for a client, you need to receive NFRC simulation reports
or certified product directory numbers in accordance with NFRC 100.</span></font></p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> </span></font></p>
</div>
<div>
<p class="MsoNormal" style="margin-top:1.0pt"><b><span><font color="#632423" face="Verdana" size="2"><span style="font-size:10.0pt;font-family:Verdana;color:#632423;font-weight:bold">Robby Oylear, LEED</span><sup>®</sup><span> AP BD+C</span></font></span></b></p>
<p class="MsoNormal"><i><span><font color="black" face="Verdana" size="1"><span style="font-size:8.0pt;font-family:Verdana;color:black;font-style:italic">Mechanical Project Engineer</span></font></span></i></p>
<p class="MsoNormal"><i><span><font color="black" face="Verdana" size="1"><span style="font-size:8.0pt;font-family:Verdana;color:black;font-style:italic">Energy Analyst</span></font></span></i></p>
<p class="MsoNormal"><i><span><font color="black" face="Verdana" size="1"><span style="font-size:8.0pt;font-family:Verdana;color:black;font-style:italic"> </span></font></span></i></p>
<p class="MsoNormal" style="line-height:115%"><b><span><font color="#632423" face="Verdana" size="1"><span style="font-size:8.0pt;line-height:115%;font-family:Verdana;color:#632423;font-weight:bold">D</span></font></span></b><font color="#1f497d" face="Verdana" size="1"><span style="font-size:8.0pt;line-height:115%;font-family:Verdana;color:#1F497D"><span>
</span></span></font><font color="black" face="Verdana" size="1"><span style="font-size:8.0pt;line-height:115%;font-family:Verdana;color:black"></span><span><a href="tel:206-788-4571" value="+12067884571" target="_blank">206-788-4571</a> |</span></font><font color="#bfab7f" face="Verdana" size="1"><span style="font-size:8.0pt;line-height:115%;font-family:Verdana;color:#BFAB7F"><span>
</span></span></font><b><font color="#632423" face="Verdana" size="1"><span style="font-size:8.0pt;line-height:115%;font-family:Verdana;color:#632423;font-weight:bold">C</span></font></b><font color="#a50021" face="Verdana" size="1"><span style="font-size:8.0pt;line-height:115%;font-family:Verdana;color:#A50021"><span> </span></span></font><font color="black" face="Verdana" size="1"><span style="font-size:8.0pt;line-height:115%;font-family:Verdana;color:black"></span><span><a href="tel:206-354-2721" value="+12063542721" target="_blank">206-354-2721</a></span></font></p>
<p class="MsoNormal" style="line-height:115%"><font face="Times New Roman" size="3"><span style="font-size:12.0pt;line-height:115%"><a href="http://www.rushingco.com/" target="_blank"><b><i><span><font color="#632423" face="Verdana" size="1"><span style="font-size:8.0pt;line-height:115%;font-family:Verdana;color:#632423;font-weight:bold;font-style:italic">www.rushingco.com</span></font></span></i></b></a></span></font></p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> </span></font></p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> </span></font></p>
</div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> </span></font></p>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">On Wed, Jul 27, 2011 at 2:44 PM, <<a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a>> wrote:</span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">Dear Robby,<br>
<br>
Yes, I am modeling for LEED purposes.<br>
I'll look into A8.2. But at least, is my method correct for the proposed
scenario?<br>
<br>
Brad: I think you need to enter the center of glass u-value in the "Glass
Type", and then enter the frame properties in the "Window"
properties...<br>
<br>
Best,<br>
Omar</span></font></p>
<div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"><br>
<br>
Quoting Brad Robinson <<a href="mailto:brad.robinson@yahoo.com" target="_blank">brad.robinson@yahoo.com</a>>:</span></font></p>
</div>
<blockquote style="border:none;border-left:solid #CCCCCC 1.0pt;padding:0cm 0cm 0cm 6.0pt;margin-left:4.8pt;margin-right:0cm">
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"><br>
<br>
Is the u-value listed for a manufacturer and specific model on the NRCAN
website centre of glass or overall assembly? Many windows are custom made
to suit so I am unclear if each individual custom window would need to be
tested.<br>
<br>
<br>
<br>
In eQuest, when entering the window, if the u-value represents the whole
window, including frame, do you need to enter a frame width, conductance etc as
well under the Window Frame section under Window Properties? Thanks.<br>
<br>
<br>
Brad Robinson<br>
<br>
<br>
<br>
________________________________<br>
From: Robby Oylear <<a href="mailto:robbyoylear@gmail.com" target="_blank">robbyoylear@gmail.com</a>><br>
To: Omar Katanani <<a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a>><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
Sent: Wednesday, July 27, 2011 12:32:08 PM<br>
Subject: Re: [Equest-users] URGENT: Window U-values: Total window assembly v/s
Glass only<br>
<br>
<br>
Omar,<br>
<br>
The answer depends on the purpose of your study. If you're trying to get
results for a client on the impact of the glazing on their energy performance,
this may be adequate. Make sure you've entered in the framing information
properly (metal vs. non-metal).<br>
<br>
I'd recommend opening up your simulation output results file (xxxx.SIM) and
going to the either the last page of the LV-D report or sort through your LV-E
report to see what value eQUEST has calculated. Compare these values to the
ASHRAE Fundamentals results for overall assembly values including frame to see
how close you've come. I would not blindly trust that eQUEST will give
you an appropriate overall assembly value based on entering only the center of
glass number.<br>
<br>
However, if this is for a LEED study, this is not adequate. This an
excerpt from an e-mail I sent out recently regarding LEED and NFRC
requirements.<br>
<br>
In order to meet LEED EAp2 Minimum Energy Performance, the project must comply
with all mandatory provisions of ASHRAE 90.1-2007. Section 5.4.2
Fenestration and Doors requires that fenestration performance be determined per
section 5.8.2. Section 5.8.2.4 U-factor requires that the U-factor for
the overall fenestration area (including framing) be determined in accordance
with NFRC 100. If you do not have NFRC data available, values from section A8.2
are the only acceptable alternative.<br>
<br>
Robby Oylear, LEED®AP BD+C<br>
Mechanical Project Engineer<br>
Energy Analyst<br>
</span></font></p>
</div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">D206-788-4571 |C206-354-2721</span></font></p>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"><br>
<a href="http://www.rushingco.com" target="_blank">www.rushingco.com</a><br>
<br>
<br>
<br>
<br>
<br>
On Wed, Jul 27, 2011 at 8:14 AM, Omar Katanani <<a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a>>
wrote:<br>
<br>
Dear all,</span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> <br>
I have a small question regarding entering</span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">window properties to eQUEST:</span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> <br>
I have read a lot of emails in the forum</span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">discussing NFRC testing, LBNL Window 5 import, and other topics that I
haven?t<br>
paid attention to before.</span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> <br>
The way I modelled my windows is the</span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">following:</span></font></p>
</div>
<blockquote style="border:none;border-left:solid #CCCCCC 1.0pt;padding:0cm 0cm 0cm 6.0pt;margin-left:4.8pt;margin-right:0cm">
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> <br>
1. I have manufacturer?s specifications listing the
glass U-values, not the total assembly.<br>
2. In the ?Glass Types? (eQUEST Detailed Mode), I
created glass types, and entered the glass conductance, visible transmittance,
SC, and emissivity from the manufacturer?s details I have.<br>
3. When creating windows, I specify which glass type
(from the ones I created in step 2), in addition to the frame width and
conductance.</span></font></p>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"><br>
<br>
I?m assuming that, given that I</span></font></p>
</div>
</blockquote>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">entered the u-values for the glass only, and then I entered information
about<br>
the frame, then I need not worry about any conversions in U-values, since<br>
eQUEST has all the necessary information to calculate the equivalent u-value of<br>
the whole pane + frame assembly, right?</span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> <br>
I appreciate your feedback / comments</span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">today if possible, as this has become really urgent!</span></font></p>
</div>
<blockquote style="border:none;border-left:solid #CCCCCC 1.0pt;padding:0cm 0cm 0cm 6.0pt;margin-left:4.8pt;margin-right:0cm">
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> <br>
Many thanks,<br>
Omar<br>
___________________________<br>
Omar Katanani<br>
Sustainable Design Engineer<br>
Email: <a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a><br>
<br>
EcoConsulting (Lebanon)</span></font></p>
</div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">NahasBuilding, 4th floor</span></font></p>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"><br>
4 St-Maron Street/ Georges Haddad Avenue<br>
Postal Code: 2028 5806</span></font></p>
</div>
</blockquote>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">SAIFI</span></font></p>
<p class="MsoNormal" style="margin-bottom:12.0pt"><font face="Times New Roman" size="3"><span style="font-size:12.0pt">Beirut</span></font>, Lebanon<br>
Tel: <a href="tel:%2B961%20%280%29%201%20971%20266" value="+9611971266" target="_blank">+961
(0) 1 971 266</a><br>
Mobile: <a href="tel:%2B961%20%280%29%203%20045%20045" value="+9613045045" target="_blank">+961 (0) 3 045 045</a><br>
<br>
EcoConsulting (UK) Ltd<br>
28 Marshalsea Road<br>
London, SE1 1HF<br>
Tel: <a href="tel:%2B44%20%280%29%20207%20939%200989" value="+442079390989" target="_blank">+44 (0) 207 939 0989</a><br>
Fax: <a href="tel:%2B44%20%280%29%20207%20939%200981" value="+442079390981" target="_blank">+44 (0) 207 939 0981</a><br>
Website: <a href="http://www.ecoconsulting.net" target="_blank">www.ecoconsulting.net</a><br>
<br>
<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br>
</p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span></font></p>
</div>
</blockquote>
<div>
<div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"><br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span></font></p>
</div>
</div>
</div>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span style="font-size:12.0pt"> </span></font></p>
</div>
</div></div></div>
</div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; left: -5000px;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup{position: absolute;z-index: 9999;padding: 0px 0px;margin-left: 0px;margin-top: 0px;overflow: hidden;word-wrap: break-word;color: black;font-size: 10px;text-align: left;line-height: 130%;}</style>