<font size="+1">This is not the spot to be considering your control
method. There will be very little difference in efficiency at
this point. The critical point to consider is when the first
chiller is at 100% and you are bringing the second one on line.
The program default is probably the correct method. You have to
look at the part load curves of the chillers and decide what your
split is going to be based on the efficiencies and at what point
the second chiller can to run at at the bottom end. You may find
the lead chiller has to drop to say, 75% so your second chiller
can operate at 25%. Efficiency may dictate a different split on
start up and a varying split as your load ramps up.</font> <font
size="+1">You might need to get your lead chiller back to say 83%,
and then ramp the second chiller to 83%. It all depends on the
equipment and it's part load performance.<br>
Bruce Easterbrook P.Eng.<br>
Abode Engineering<br>
</font><br>
On 26/07/2011 04:17 AM, tiejun hu wrote:
<blockquote
cite="mid:268664ce.ec46.1316584c255.Coremail.hutiejun1223@126.com"
type="cite">
<div
style="line-height:1.7;color:#000000;font-size:14px;font-family:arial">
<div>HI everyone</div>
<div> Does anyone know the default control strategy of
multiple chillers? for example. if there two identical
chillers in the project. when it is in part load 90%. then it
exist two control methods: one case is that main chiller bear
100%.and the other bear 80%. another case is that two chiller
is 90%. which way is default of the software. or the default
is other control way, is not i said. hope some can give me a
hand. thanks!</div>
</div>
<br>
<br>
<span title="neteasefooter"><span id="netease_mail_footer"></span></span>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>