<font face="tahoma,sans-serif">Thanks Bruce. </font><span class="Apple-style-span" style="font-family: tahoma, sans-serif; ">Great reply. </span><div><font class="Apple-style-span" face="tahoma, sans-serif">I completely agree that modelers need to have a good technical knowledge.</font></div>
<div><font class="Apple-style-span" face="tahoma, sans-serif">Oversizing AHU is justified now. I appreciate your help.</font></div><div><font class="Apple-style-span" face="tahoma, sans-serif"><br></font></div><div><font class="Apple-style-span" face="tahoma, sans-serif"><br>
</font></div><div><font class="Apple-style-span" face="tahoma, sans-serif">Much thanks,</font></div><div><font class="Apple-style-span" face="tahoma, sans-serif">Aru</font></div><div><font class="Apple-style-span" face="tahoma, sans-serif"><br>
</font></div><div><font class="Apple-style-span" face="tahoma, sans-serif"><br></font><div class="gmail_quote">On Tue, Jul 26, 2011 at 7:28 AM, Bruce Easterbrook <span dir="ltr"><<a href="mailto:bruce5@bellnet.ca">bruce5@bellnet.ca</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    <font size="+1">    The intent of 90.1 and using a modelling program
      like eQuest is to size the equipment closer to the actual demand. 
      The 15% and 25% variance factors were used in the past before the
      computerized modelling we are using today.  Doing load
      calculations buy hand or using a spreadsheet made for much more
      deviation between the calculations and the building.  Less things
      were accounted for as well.  By providing more certainty using a
      modelling program we should be reducing these safety factors. 
      These factors are still a best guess and the designer must keep
      all this in mind.  The next step in the process is specifying the
      equipment for the building.  So if the modeller has a 15% SF on
      the equipment and because most equipment is built with discrete
      sizes, the specifier adds another 20% by picking the next size up
      you can see how things start to chain together and get out of
      control.  Next step is bidding, the specifier uses Trane as base
      bid but Carrier wins the process and submits shop drawings.  They
      are normally required to provide a superior bid, there is another
      8%.  Remember as well the second and third increases are now
      compounding, we are not 43% over sized but probably more like
      50%+.  My point is the original design and SF should be used from
      start to finish.<br>
          Next question is where to apply these factors.  They should be
      on the air handlers.  If your fan is too small and your coils are
      too small what you get supplied from the plant is irrelevant.  You
      physically do not have the equipment to handle the diversity.  So
      the method is to account for the diversity in the end units, and
      have the plant at 1.0 or less.  Your SF on the units flows through
      to the plant.  Note I mentioned "or less".  Consider a building
      with a north south split.  An AHU on the north side will only see
      diversity due to weather.  A south side AHU will see diversity due
      to weather and sun.  You may consider different diversity factors
      for each.  Throw in 10 buildings of different sizes and
      orientations you can see the effect in the deviation on the plant
      using old methods.  eQuest due to the through nature of the model
      can account for all this.  Can is a critical word, it all depends
      on the model.  There is still diversity in the model.  The amount
      depends on what the money people want to spend modelling.  LEED is
      the attempt to control these factors, to set a minimum quality
      level for the model.  It is now realized this is not enough. 
      Original LEED buildings on the majority do not perform as the
      model suggested they would.  Now commissioning is the new buzz
      word.  As if that is the only reason.  If your units are too small
      commissioning won't fix the problem either.  If your units are too
      big the system will work but not efficiently.  Part of the problem
      is the process, hence the proposal that modellers be PE's.  That
      may help but it wouldn't solve many of the problems.  The model is
      important but is only effective if used as a reference start to
      finish.  The safety factors come from using eQuest and doing
      project reviews.  Comparing the actual building performance to the
      model and taking a look at the allowances for variance.  There is
      only one group responsible for this whole process, it is the
      mechanical engineer who has assumed responsibility for the
      building project.<br>
          The short answer is there is no rule of thumb for the safety
      factors.  More experience allows you to guess better but it is
      still a guess because every project is different.  Model feedback
      is spotty.  The safety factors should be applied at the terminal
      equipment not at the plant.  Mostly, 15% for cooling and 25% for
      heating are too big.  In most cases .5 cfm/SF is too small.  But
      that is where I start.  Get the model built and running, let it
      run on defaults, let it determine the initial sizing, thoroughly
      review the sim output, then start tuning it.<br>
      Bruce Easterbrook P.Eng.<br>
      Abode Engineering<br>
    </font><div><div></div><div class="h5"><br>
    On 25/07/2011 07:47 PM, Arunabha Sau wrote:
    </div></div><blockquote type="cite"><div><div></div><div class="h5"><font face="tahoma, sans-serif">Howdy!</font>
      <div><font face="tahoma, sans-serif"><br>
        </font></div>
      <div><font face="tahoma, sans-serif"><br>
        </font></div>
      <div><font face="tahoma, sans-serif">So,
          I just saw a project which<span style="border-collapse:collapse"> has applied its oversizing factors (1.15 for
            cooling and 1.25 for heating) to the plant rather than the
            air handlers.  ASHRAE 90.1 Appendix G </span><span style="border-collapse:collapse">page
            180, G3.1.2.2 Equipment capacities</span><span style="border-collapse:collapse"> 
            does not specify where the oversizing should occur.  Have
            you seen this method used before?  Is it an acceptable and
            accurate way of meeting the baseline modeling requirements?</span></font></div>
      <span style="border-collapse:collapse"><font face="tahoma, sans-serif">
          <div class="gmail_quote"><br>
          </div>
          <div class="gmail_quote">I appreciate your help.</div>
          <div class="gmail_quote"><br>
          </div>
          <div class="gmail_quote"><br>
          </div>
          <div class="gmail_quote"><br>
          </div>
          <div class="gmail_quote"><br>
          </div>
          <div class="gmail_quote">Much thanks,</div>
          <div class="gmail_quote">Aru</div>
        </font></span>
      <br>
      <fieldset></fieldset>
      <br>
      </div></div><pre>_______________________________________________
Equest-users mailing list
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </div>

</blockquote></div><br></div>