<html><body><div style="color:#000; background-color:#fff; font-family:arial, helvetica, sans-serif;font-size:10pt"><div><span>Hmmm..</span></div><div><br><span></span></div><div><span>Does that mean you need to sum the unmet hours of ALL separate systems as well?</span></div><div><span><br></span></div><div><span>In regards to the unmet cooling, LEED NC-2009 (Canada) notes that it is acceptable to have unmet cooling hours. I interpreted this to mean that the unmet hours of concern are only on the heating side, not the cooling.<br></span></div><div><br></div><div style="font-family: arial, helvetica, sans-serif; font-size: 10pt;"><div style="font-family: times new roman, new york, times, serif; font-size: 12pt;"><font face="Arial" size="2"><hr size="1"><b><span style="font-weight:bold;">From:</span></b> "Patrick J. O'Leary, Jr." <poleary1969@gmail.com><br><b><span style="font-weight: bold;">To:</span></b> Brad Robinson
<brad.robinson@yahoo.com><br><b><span style="font-weight: bold;">Cc:</span></b> "equest-users@lists.onebuilding.org" <equest-users@lists.onebuilding.org><br><b><span style="font-weight: bold;">Sent:</span></b> Thursday, July 7, 2011 10:56:08 AM<br><b><span style="font-weight: bold;">Subject:</span></b> Re: [Equest-users] Unmet Hours<br></font><br><div id="yiv543004948">
<title></title>
that would be 500 unmet hours.<br>
<br>
the bigger leed review problem i've had is when i have more unmet hours
in one category in the proposed (like 200 unmet in cooling) and fewer
unmet hours in the other (like 0 in heating) but the baseline is
opposite. certain leed reviewers think this is a problem. the 90.1
requirement addresses the unmet hours per the entire building design
(both heating and cooling) not heating and cooling individually.<br>
<br>
On 7/7/11 7:49 AM, Brad Robinson wrote:
<blockquote type="cite">
<div style="color:rgb(0, 0, 0);background-color:rgb(255, 255, 255);font-family:arial, helvetica, sans-serif;font-size:10pt;">
<div>For LEED compliance under ASHRAE 90.1, are the 300 unmet hours
the sum of all the unmet hours in each zone, or the peak per zone? In
other words if I have 250 unmet hours in one zone and 250 unmet hours
in another zone, does this comply, or is it considered 500 unmet hours
total? By zones, I mean thermal zones served by the same air handling
unit. Thanks.<br>
</div>
<div><br>
</div>
<div>Brad Robinson</div>
<div><br>
</div>
</div>
<pre><fieldset class="yiv543004948mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a rel="nofollow" class="yiv543004948moz-txt-link-freetext" target="_blank" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a rel="nofollow" class="yiv543004948moz-txt-link-abbreviated" ymailto="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
</div><br><br></div></div></div></body></html>