Hello eQuesters,<br>                               <br>                           Currently i am working on a project which has 2 VSD enabled centrifugal chillers. When i ran the simulation with one chiller and checked the PS-D report, the Peak Load is 480 TR. Same is the case with two chillers. But there is difference in Annual Energy consumption. For instance Annual energy consumption with one chiller is 1050k kWh whereas with two chillers it is 680k kWh. PS-H report shows cooling Capacity is 4.2 MBTU with two chillers and 8.314 MBTU with single chiller. My doubt is why there is discrepancy in Annual Energy Consumption even if i am equally sizing both the chiller with with 4.2 MBTU.<br>
<br>Thanks in advance,<br>                    <br clear="all"><br>-- <br><br><br><i><font style="font-family:arial,helvetica,sans-serif;color:rgb(102, 102, 102)" size="2">Javed Iqbal, LEED AP, CEA<br>Project Manager   <br>