<div>Let me re-direct my question regarding reheating:</div>
<div> </div>
<div>How do I make my reheating (electric) work only(mainly) for cooling mode? <br></div>
<div>~DE<br></div>
<div class="gmail_quote">2011/6/27 John Aulbach <span dir="ltr"><<a href="mailto:jra_sac@yahoo.com">jra_sac@yahoo.com</a>></span><br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div>
<div style="FONT-FAMILY: times new roman,new york,times,serif; FONT-SIZE: 12pt">DongEun:<br><br>There is no difference, except to make the secondary heating coil ELECTRIC. No problem in eQuest.<br><br>John Aulbach<br>
<div><br></div>
<div style="FONT-FAMILY: times new roman,new york,times,serif; FONT-SIZE: 12pt"><br>
<div style="FONT-FAMILY: times new roman,new york,times,serif; FONT-SIZE: 12pt"><font size="2" face="Tahoma">
<hr size="1">
<b><span style="FONT-WEIGHT: bold">From:</span></b> DongEun Kim <<a href="mailto:equested@gmail.com" target="_blank">equested@gmail.com</a>><br><b><span style="FONT-WEIGHT: bold">To:</span></b> Will Mak <<a href="mailto:wmak@epsteinglobal.com" target="_blank">wmak@epsteinglobal.com</a>><br>
<b><span style="FONT-WEIGHT: bold">Cc:</span></b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b><span style="FONT-WEIGHT: bold">Sent:</span></b> Sun, June 26, 2011 9:19:02 PM<br>
<b><span style="FONT-WEIGHT: bold">Subject:</span></b> Re: [Equest-users] VAV with Electric Reheat<br></font>
<div>
<div></div>
<div class="h5"><br>
<div>Will,</div>
<div> </div>
<div>If I understand correctly, reheat Delta T, which was to specify  max reheat coil capacity.</div>
<div> </div>
<div>What I want is to switch reheat source from 'how water' to 'ectricity', while the heating source for </div>
<div> </div>
<div>the main heating coil is 'how water.'</div>
<div> </div>
<div>Thank you.</div>
<div> </div>
<div>~DE<br><br></div>
<div class="gmail_quote">2011/6/24 Will Mak <span dir="ltr"><<a href="mailto:wmak@epsteinglobal.com" rel="nofollow" target="_blank">wmak@epsteinglobal.com</a>></span><br>
<blockquote style="BORDER-LEFT: rgb(204,204,204) 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-US">
<div>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125); FONT-SIZE: 10pt">You have to put a value for the reheat delta T or the reheat coils don’t kick on.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125); FONT-SIZE: 10pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="COLOR: rgb(199,91,18)">William Mak, LEED AP BD+C</span></b><span style="COLOR: rgb(31,73,125); FONT-SIZE: 9pt"><br></span><span style="COLOR: black; FONT-SIZE: 8pt">Mechanical Design Engineer</span><span style="COLOR: black; FONT-SIZE: 9pt"><br>
</span><span style="COLOR: rgb(31,73,125); FONT-SIZE: 9pt"><br></span><b><span style="COLOR: rgb(199,91,18); FONT-SIZE: 10pt">EPSTEIN</span></b><span style="COLOR: rgb(31,73,125); FONT-SIZE: 9pt"><br></span><span style="COLOR: black; FONT-SIZE: 8pt">Architecture<br>
</span><span style="COLOR: rgb(199,91,18); FONT-SIZE: 8pt">Interiors</span><span style="COLOR: black; FONT-SIZE: 8pt"><br>Engineering<br></span><span style="COLOR: rgb(199,91,18); FONT-SIZE: 8pt">Construction</span><span style="COLOR: black; FONT-SIZE: 8pt"><u></u><u></u></span></p>

<p class="MsoNormal"><span style="COLOR: black; FONT-SIZE: 8pt">Sustainability<br><br>600 West Fulton Street<br>Chicago, Illinois 60661-1259<br><br>D: (312) 429-8116<br>F: (312) 429-8800</span><span style="COLOR: rgb(31,73,125); FONT-SIZE: 8pt"><u></u><u></u></span></p>

<p class="MsoNormal"><span style="COLOR: black; FONT-SIZE: 8pt">E:</span><span style="COLOR: rgb(0,112,192); FONT-SIZE: 8pt"> <a href="mailto:wmak@epsteinglobal.com" rel="nofollow" target="_blank"><span style="COLOR: blue">wmak@epsteinglobal.com</span></a></span><span style="COLOR: black; FONT-SIZE: 8pt"><br>
W:</span><span style="COLOR: rgb(199,91,18); FONT-SIZE: 8pt"> <a href="http://www.epsteinglobal.com/" rel="nofollow" target="_blank"><span style="COLOR: rgb(199,91,18)">www.epsteinglobal.com</span></a></span><span style="COLOR: black; FONT-SIZE: 9pt"><br>
<br></span><span style="FONT-FAMILY: Webdings; COLOR: rgb(0,176,80); FONT-SIZE: 10pt">þ</span><span style="COLOR: black; FONT-SIZE: 8pt"> Epstein is a firm believer in sustainability. We ask that you please consider the environment before printing this e-mail.<u></u><u></u></span></p>

<p class="MsoNormal"><span style="COLOR: rgb(31,73,125); FONT-SIZE: 10pt"><u></u> <u></u></span></p>
<div style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">From:</span></b><span style="FONT-SIZE: 10pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" rel="nofollow" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" rel="nofollow" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>DongEun Kim<br>
<b>Sent:</b> Thursday, June 23, 2011 11:58 PM<br><b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" rel="nofollow" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] VAV with Electric Reheat<u></u><u></u></span></p>
</div>
<div>
<div></div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt">Hi all,</span><u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal"><span style="COLOR: navy">Can anyone give me an advice regarding a problem described below?</span><u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt">I need to model a VAV system with chilled water coil and hot water coil, and also with Electric Reheating.</span><u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt">As a start,  I selected  'VAV with HW Reheat' system.</span><u></u><u></u></p></div>
<div>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt"> </span><u></u><u></u></p></div>
<div>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt">However, I've realized that the system only generates a reheating coil without a main hot water coil(heating coil).</span><u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt">So I installed  'heating coil'  in the detailed mode, and then,</span> <span style="COLOR: navy">I  changed the zone heat source to be 'electric'.</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt">However when I take a look at the result, there came two problems.</span><u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt">1. Heating was mainly done by reheating coil not by main heating coil.</span><u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt">2. Reheating didn't seem to use electricity.</span><u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">Any advice will be greatly appreciated.<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">Thank you in advance.<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">~DE <u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal"><span style="COLOR: navy">Kim, DongEun(DE) | Research Engineer, LEED AP<br>Annex R&D Institute, HIMEC(Hanil Mech. & Elec. Consultants)</span><u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div></div></div></div></div></blockquote></div><br></div></div></div></div></div></div></blockquote></div><br>