    <font size="+1">Yes, no pilot energy, and for the HIR, I haven't
      checked this with 90.1, but baseline I assume would be natural
      draft, non condensing, which would be 1.25.  Then you can take
      credit for the higher efficiencies of the newer boiler/furnace
      designs.  Someone, Honeywell? is also making an iris shut-off for
      the bottom of your chimney so it is only drawing when the
      boiler/hot water tank is operating.<br>
      Bruce<br>
    </font><br>
    On 23/06/2011 01:43 PM, Carol Gardner wrote:
    <blockquote
      cite="mid:BANLkTikN4YfusuQpQrFpvSfW6T9GHzw2og@mail.gmail.com"
      type="cite"> Hi Bill,<br>
      <br>
      I agree with your conclusions but got curious about boilers and
      pilot lights and their usage. I have to admit to being fairly
      ignorant when it comes to gas using equipment. So I did what I
      usually do and Googled <i>energy use of a pilot light</i> and
      came across this nice little website:<br>
      <a moz-do-not-send="true"
href="http://energyexperts.org/EnergySolutionsDatabase/ResourceDetail.aspx?id=4407"
        target="_blank">http://energyexperts.org/EnergySolutionsDatabase/ResourceDetail.aspx?id=4407</a><br>
      that had a link to a nice little calculator that can be used to
      calculate pilot light energy use:<br>
      <a moz-do-not-send="true"
        href="http://www.wisconsinpublicservice.com/home/gas_calculator.aspx"
        target="_blank">http://www.wisconsinpublicservice.com/home/gas_calculator.aspx</a><br>
      When you are in the calculator there is "more info" next to the
      furnace line and it includes the following information "natural
      gas furnaces and boilers have been required to have pilotless
      ignitions since 1980". That would mean that the eQUEST default
      should be modified to be 0, right?<br>
      <br>
      Carol<br>
      <br>
      <div class="gmail_quote">On Wed, Jun 22, 2011 at 6:43 AM, Bishop,
        Bill <span dir="ltr"><<a moz-do-not-send="true"
            href="mailto:wbishop@pathfinder-ea.com" target="_blank">wbishop@pathfinder-ea.com</a>></span>
        wrote:<br>
        <blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt
          0.8ex; border-left: 1px solid rgb(204, 204, 204);
          padding-left: 1ex;">
          <div bgcolor="white" link="blue" vlink="purple" lang="EN-US">
            <div>
              <p class="MsoNormal"><span style="color: rgb(31, 73,
                  125);">Thanks Bruce.</span></p>
              <p class="MsoNormal"><span style="color: rgb(31, 73,
                  125);"> </span></p>
              <p class="MsoNormal"><span style="color: rgb(31, 73,
                  125);">I appreciate your insight on the reasonable
                  range of furnace efficiencies. I was more concerned
                  with how to model the baseline per minimum ASHRAE
                  efficiencies. Using my question numbering, I’m going
                  with these answers:</span></p>
              <p><span style="color: rgb(31, 73, 125);"><span>1.)<span
                      style="font: 7pt "Times New Roman";">   
                    </span></span></span><span style="color: rgb(31, 73,
                  125);">Warm Air Furnace</span></p>
              <p><span style="color: rgb(31, 73, 125);"><span>2.)<span
                      style="font: 7pt "Times New Roman";">   
                    </span></span></span><span style="color: rgb(31, 73,
                  125);">No pilot light</span></p>
              <p><span style="color: rgb(31, 73, 125);"><span>3.)<span
                      style="font: 7pt "Times New Roman";">   
                    </span></span></span><span style="color: rgb(31, 73,
                  125);">HIR=1.25</span></p>
              <p class="MsoNormal"><span style="color: rgb(31, 73,
                  125);"> </span></p>
              <p class="MsoNormal"><span style="color: rgb(31, 73,
                  125);">Bill</span></p>
              <p class="MsoNormal"><span style="color: rgb(31, 73,
                  125);"> </span></p>
              <div>
                <div style="border-right: medium none; border-width: 1pt
                  medium medium; border-style: solid none none;
                  border-color: rgb(181, 196, 223) -moz-use-text-color
                  -moz-use-text-color; padding: 3pt 0in 0in;">
                  <p class="MsoNormal"><b><span style="font-size: 10pt;
                        color: windowtext;">From:</span></b><span
                      style="font-size: 10pt; color: windowtext;"> Bruce
                      Easterbrook [mailto:<a moz-do-not-send="true"
                        href="mailto:bruce5@bellnet.ca" target="_blank">bruce5@bellnet.ca</a>]
                      <br>
                      <b>Sent:</b> Tuesday, June 21, 2011 8:57 PM<br>
                      <b>To:</b> Bishop, Bill<br>
                      <b>Cc:</b> eQUEST Users List<br>
                      <b>Subject:</b> Re: [Equest-users] Furnace AFUE,
                      Et, HIR and furnace fuel auxiliary</span></p>
                </div>
              </div>
              <div>
                <div>
                  <p class="MsoNormal"> </p>
                  <p class="MsoNormal"><span style="font-size: 13.5pt;">Hi
                      Bill,<br>
                      I don't have a project to pull up to get to these
                      inputs.  I believe I normally enter the AFUE, and
                      78% is an medium oil number and a low gas number. 
                      Typically most gas units on the market will give
                      you a 92% AFUE for a condensing unit and a few are
                      running in the 94% range.  Oil you can get into
                      the 84% range.  Don't do condensing oil, no one is
                      using the correct steel in the heat exchangers and
                      they rot out after a few years.  No units run with
                      a pilot light anymore and you can see why, it is
                      all spark ignition.  I normally use a warm air
                      furnace on a PSZ.  Use 78% for oil and 92% for
                      gas, no pilot light for either.  You can adjust
                      everything later on the heating/unitary power
                      tab.  Grain of salt, I don't do LEED work, just
                      90.1.  For the project I have open I have a HIR of
                      1.08 and 0 auxiliary, gas.   So I probably input
                      92% AFUE in the wizard, no pilot light.<br>
                      Bruce Easterbrook P.Eng.<br>
                      Abode Engineering<br>
                    </span><br>
                    On 21/06/2011 10:12 AM, Bishop, Bill wrote: </p>
                  <p class="MsoNormal">When selecting “furnace” for the
                    heat source, eQUEST adds 800 Btu/h for furnace fuel
                    auxiliary (pilot light) as default. The default 800
                    Btu/h adds 12% to my baseline heating energy, so it
                    is not trivial.</p>
                  <p class="MsoNormal">ASHRAE Standard 90.1, Table
                    6.8.1E lists minimum furnace efficiency
                    requirements.</p>
                  <p class="MsoNormal">What should I enter for Furnace
                    HIR and Furnace Fuel Auxiliary for Baseline System 3
                    (PSZ-AC) and the new 90.1-2010 Baseline System 9
                    (Heating & Ventilation; Warm-air furnace,
                    gas-fired)?</p>
                  <p class="MsoNormal"> </p>
                  <p class="MsoNormal">First, which equipment type
                    applies? Table 6.8.1E has three gas-fired equipment
                    types – Warm Air Furnace, Warm Air Duct Furnace, and
                    Warm Air Unit Heaters. I think both Systems 3 and 9
                    would be Warm Air Furnace, since packaged (System 3)
                    and ventilation (System 9) systems would seem to
                    preclude duct furnaces and unit heaters.</p>
                  <p class="MsoNormal"> </p>
                  <p class="MsoNormal">Second, does the note, “Units
                    must also include an interrupted or intermittent
                    ignition device (IID)” mean that no pilot light
                    should be modeled? This note to Table 6.8.1E does
                    not apply to Warm Air Furnaces <225,000 Btu/h in
                    90.1-2004 or 90.1-2007, but applies to all Warm Air
                    Furnaces in 90.1-2010. This is a LEED 2.2 project
                    but the building is currently under construction.</p>
                  <p class="MsoNormal"> </p>
                  <p class="MsoNormal">Third, Warm Air Furnace minimum
                    efficiency is 78% AFUE or 80% E<sub>t</sub> . Should
                    I use HIR=1.282 (78%) or HIR=1.25?</p>
                  <p class="MsoNormal"> </p>
                  <p class="MsoNormal">Thanks for your thoughts,</p>
                  <p class="MsoNormal">Bill</p>
                  <p class="MsoNormal"> </p>
                  <p class="MsoNormal"><img
                      src="cid:part1.06030009.01050109@bellnet.ca"
                      alt="Signature in jpg form" height="123"
                      width="496"></p>
                  <p class="MsoNormal"> </p>
                  <pre> </pre>
                  <pre> </pre>
                  <pre>_______________________________________________</pre>
                  <pre>Equest-users mailing list</pre>
                  <pre><a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a></pre>
                  <pre>To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></pre>
                </div>
              </div>
            </div>
          </div>
          <br>
          _______________________________________________<br>
          Equest-users mailing list<br>
          <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
            target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
          To unsubscribe from this mailing list send  a blank message to
          <a moz-do-not-send="true"
            href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG"
            target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <br clear="all">
      <br>
      -- <br>
      Carol Gardner PE<br>
    </blockquote>
  </body>
</html>