What about if the exhaust fans use 1 hp or less? Does everyone follow the directions in 6.5.3.1.1?<br><br>Beelzebub<br><br><div class="gmail_quote">On Wed, Jun 22, 2011 at 10:59 AM, Demba Ndiaye <span dir="ltr"><<a href="mailto:Demba.Ndiaye@setty.com">Demba.Ndiaye@setty.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<div link="blue" vlink="purple" lang="EN-US"><div><p class="MsoNormal"><span style="color:#1F497D">I second Nick’s approach: put the exhaust flows where you think the air will come from. <u></u><u></u></span></p><p class="MsoNormal">
<span style="color:#1F497D"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1F497D">In my experience, that is the best way to handle air transfer through exhaust in eQuest.<u></u><u></u></span></p><p class="MsoNormal">
<span style="color:#1F497D"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1F497D">And I believe that the wizard is also doing it for you if you specify zonal exhaust before leaving it …<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1F497D">______________<u></u><u></u></span></p><p class="MsoNormal"><span style="color:#1F497D">Demba NDIAYE<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><div><div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in"><p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Nick Caton<br>
<b>Sent:</b> Wednesday, June 22, 2011 1:07 PM<br><b>To:</b> Bishop, Bill; Anthony Hardman; Seun Odukomaiya; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a></span></p>
<div><div></div><div class="h5"><br><b>Subject:</b> Re: [Equest-users] eQuest Accounting for Exhaust Fan Energy for LEED<u></u><u></u></div></div><p></p></div></div><div><div></div><div class="h5"><p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="color:#1F497D">I’ve run into this at least once, and an approach that has worked for me is a riff on Bill’s first suggestion. Start with: where is the air coming from?<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1F497D">If the negative space is a bathroom that in reality is drawing air from an adjacent open office space under the same system, why not specify the exhaust (wholly or in part) in the open office space? Perhaps another large minimum-airflow space under the same system would work as well? Airflows and cooling requirements should balance out at the system level provided the exhaust does not exceed the local zone airflow rate.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1F497D">The balance of airflows may not work for every case, but this can potentially be the simplest approach. Consider carefully whether the quantity and scheduling of the exhaust will cause it to exceed the hourly supply air rate for the zone(s) you’re considering.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1F497D">`Nick<u></u><u></u></span></p><p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p>
<div><p class="MsoNormal"><span style="color:#1F497D"><img src="cid:image001.jpg@01CC30E4.A8737F40" alt="cid:489575314@22072009-0ABB" height="37" width="119"></span><b><span style="color:#2D4D5E"><u></u><u></u></span></b></p>
<p class="MsoNormal"><b><span style="color:#2D4D5E"><u></u> <u></u></span></b></p><p class="MsoNormal"><b><span style="font-size:12.0pt;color:#2D4D5E">NICK CATON, P.E.<u></u><u></u></span></b></p><p class="MsoNormal"><span style="font-size:7.5pt;color:#CC9900">SENIOR ENGINEER<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:7.5pt;color:#CC9900"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">Smith & Boucher Engineers</span><span style="font-size:7.5pt;font-family:"Times New Roman","serif";color:#CC9900"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">25501 west valley parkway, suite 200<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">olathe, ks 66061<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">direct <a href="tel:913.344.0036" value="+19133440036" target="_blank">913.344.0036</a><u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">fax <a href="tel:913.345.0617" value="+19133450617" target="_blank">913.345.0617</a><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size:10.0pt">www.smithboucher.com</span></a></span><u><span style="font-size:10.0pt;color:blue"> </span></u><span style="color:#1F497D"><u></u><u></u></span></p>
</div><p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><div><div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in"><p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Bishop, Bill<br>
<b>Sent:</b> Wednesday, June 22, 2011 10:43 AM<br><b>To:</b> Anthony Hardman; Seun Odukomaiya; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> Re: [Equest-users] eQuest Accounting for Exhaust Fan Energy for LEED<u></u><u></u></span></p>
</div></div><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal"><span style="color:#1F497D">Seun,<u></u><u></u></span></p><p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><p class="MsoNormal">
<span style="color:#1F497D">I’ve used a few different approaches to address the situation of a zonal exhaust fan that has a flow rate close to, or larger than, the supply air flow to that zone:<u></u><u></u></span></p><p class="MsoNormal">
<span style="color:#1F497D"> - Model the zone as being part of the zone that it draws transfer air from. (An example would be a single zone representing a corridor and a janitor closet.)<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"> - Increase the supply air flow to the zone with the exhaust fan, and decrease it by the same amount in the zone that it draws transfer air from.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"> - Create a different thermostat schedule(s) to allow the temperature to float more, and use the same schedule in both Baseline and Proposed. (If appropriate, for example, use a 60°F heating setpoint.)<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"> - Make the zone with exhaust fan an unconditioned zone. This might be appropriate for a trash/recycling or soiled linen room where you are not trying to condition it within a certain temperature range.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1F497D">Regards,<u></u><u></u></span></p><p class="MsoNormal"><span style="color:#1F497D">Bill<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><div><p class="MsoNormal"><span style="color:#1F497D"><img src="cid:image002.jpg@01CC30E4.A8737F40" alt="Signature in jpg form" border="0" height="123" width="496"><u></u><u></u></span></p>
</div><p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><div><div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in"><p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Anthony Hardman<br>
<b>Sent:</b> Wednesday, June 22, 2011 10:45 AM<br><b>To:</b> 'Seun Odukomaiya'; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> Re: [Equest-users] eQuest Accounting for Exhaust Fan Energy for LEED<u></u><u></u></span></p>
</div></div><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal"><span style="color:#1F497D">I’ve run into the same problem too. One thing I’ve tried is to decrease the zone level EA cfm until the unmet hours are reasonable, and then increase the kw/cfm the commensurate amount. That way, at least there’s some zone level exhaust airflow and the SV-A report shows EA fan power equal to what is on the exhaust fan schedule. A narrative to the GBCI reviewer explaining the simulation limitations would hopefully suffice. <u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><div><p class="MsoNormal"><b><span style="color:#0F243E">Anthony Hardman, PE<u></u><u></u></span></b></p><p class="MsoNormal"><b><span style="font-size:9.0pt;color:#0F243E">LEED AP BD&C</span><span style="color:#0F243E"><u></u><u></u></span></b></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#0F243E">Building Performance Analyst<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:#0F243E"><u></u> <u></u></span></p><p class="MsoNormal">
<b><span style="color:#00B050">THE GREEN ENGINEER, LLP<u></u><u></u></span></b></p><p class="MsoNormal"><b><span style="color:#00B050">Sustainable Design Consulting – Energy Modeling – LEED Project Management </span></b><span style="color:#1F497D"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#0F243E">50 Beharrell St<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:#0F243E">Concord, MA 01742<u></u><u></u></span></p><p class="MsoNormal">
<span style="font-size:10.0pt;color:#0F243E">O: <a href="tel:978%2F610-2801" value="+19786102801" target="_blank">978/610-2801</a><u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:#0F243E">C: <a href="tel:720%2F840-7862" value="+17208407862" target="_blank">720/840-7862</a><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#0F243E"><u></u> <u></u></span></p><p class="MsoNormal"><a href="http://www.greenengineer.com/" target="_blank"><span style="font-size:10.0pt;text-decoration:none"><img src="cid:image003.jpg@01CC30E4.A8737F40" alt="Description: TGE Logo" border="0" height="28" width="29"></span></a><a href="http://www.linkedin.com/in/ahardman81" target="_blank"><span style="color:#1F497D;text-decoration:none"><img src="cid:image004.jpg@01CC30E4.A8737F40" alt="Description: images5" border="0" height="28" width="31"></span></a><a href="http://twitter.com/#%21/a_Hardman" target="_blank"><span style="text-decoration:none"><img src="cid:image005.jpg@01CC30E4.A8737F40" alt="Description: t4" border="0" height="28" width="29"></span></a><span style="color:#1F497D"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#0F243E"><u></u> <u></u></span></p></div><p class="MsoNormal"><span style="color:#1F497D"><u></u> <u></u></span></p><div><div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Seun Odukomaiya<br>
<b>Sent:</b> Wednesday, June 22, 2011 8:15 AM<br><b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] eQuest Accounting for Exhaust Fan Energy for LEED<u></u><u></u></span></p>
</div></div><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">eQuesters<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">I'm having some difficulty with properly modeling exhaust fans in for LEED and I'm hoping someone can provide me with some guidance. <u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Here's my problem: I can enter the exhaust volumes and associated KW/cfm for each zone where necessary, but some of the spaces have design exhaust volumes greater than design supply air volumes (negative pressure rooms). If I select "infiltration" or "balanced infiltration" as the source of exhaust makeup for these zones, then the unmet hours for that zone become very high. If I select "air handler" as the source of makeup air, then eQuest increases the design supply air volume to match the exhaust air volume for that zone. This is problematic because the SV-A reports now have values that do not match my mechanical schedules. Additionally, the energy consumption associated with those systems increases as a result of the increased supply air volume. All in all, it's just not an accurate representation of the design. Most of these zones are expected to make up the air through zonal air transfer (something I realize eQuest is unable to do).<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">At this point, I'm considering adding the exhaust energy as a direct load to my meter along with appropriate usage schedules, and associating it to "ventilation fans". I believe the net effect on energy consumption and peak demand should be the same as if the exhaust fans were explicitly modeled. However, I'm curious as to any dynamic system or thermal effects that I may be circumventing by not explicitly modeling the exhaust fans for each zone. My gut feeling is that there shouldn't be much of an effect, but I'm just not sure. I'm also concerned that by modeling exhaust energy as a direct load, rather than explicitly, the SV-A reports won't show any exhaust volumes and thereby call attention as to the validity of the model.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">At this point, I would like the guidance of some of the members on this forum that have more experience with these issues. Is this even an acceptable way to account for exhaust fan energy for LEED? I'm open to any suggestions from anyone who has run into these issues and/or may have experience in how to deal with it.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Thanks in advance<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal"><b><span style="color:#17365D">Seun Odukomaiya, EIT, LEED AP</span></b><span style="font-size:10.0pt;color:#17365D"> |<i> Mechanical Engineer</i> | </span><b><span style="color:#17365D">L’Acquis Consulting Engineers</span></b><b><span style="font-size:10.0pt;color:#17365D"> </span></b><span style="font-size:10.0pt;color:#17365D">|<a href="tel:%28317%29%20706-2075%20Ext.%20255" value="+13177062075" target="_blank">(317) 706-2075 Ext. 255</a> | </span><span style="color:#17365D"><a href="http://www.laceindy.com/" target="_blank"><span style="color:#17365D">www.lacquis.com</span></a></span><span style="font-size:10.0pt"> | <span style="color:#17365D">To transmit large files, please use:</span> <span style="color:#17365D"><a href="http://lacquis.leapfile.net/" target="_blank"><span style="color:#17365D">http://lacquis.leapfile.net</span></a></span><span style="color:navy"><u></u><u></u></span></span></p>
<p class="MsoNormal"><u></u> <u></u></p></div></div></div></div><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>