<div>Hi Shuichi,</div>
<div> </div>
<div>Below is a link to an additional source from a previous post that helps explain how to model UFAD and/or displacement ventilation.  Their method is very similar to yours, in that you split the equipment loads between the plenum and the space.  In particular, there is a section which explains pretty clearly how to model UFAD in eQUEST.  This may be repeat info to you, but it may be able to help.  </div>

<div> </div>
<div><a href="http://www.archenergy.com/ieq-k12/Public/Proj2_Deliverables/D2.9c_FinalDVDesignGuide_2006-0630.pdf">http://www.archenergy.com/ieq-k12/Public/Proj2_Deliverables/D2.9c_FinalDVDesignGuide_2006-0630.pdf</a></div>

<div> </div>
<div> </div>
<div>Best, Patrick</div>
<div><br><br> </div>
<div class="gmail_quote">On Fri, Jun 17, 2011 at 3:07 AM, Shuichi Hendrickson <span dir="ltr"><<a href="mailto:Shuichi.Hendrickson@erm.com">Shuichi.Hendrickson@erm.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-AU" vlink="purple" link="blue">
<div>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB">Hello all,</span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB">I am attempting to model a data center in eQuest for LEED. This will be a first attempt at modelling a data center for me and I am in hopes someone could provide some sage advice on the subject. </span></font></p>

<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB">My understanding is that the data center will be a standard hot/cold aisle configuration with underfloor cooling (UFAD). The CRACs are on CHW and the CHW plant consists of multiple chillers, as well as, dedicated chillers for ice storage.</span></font></p>

<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB">Recognizing that eQuest doesn’t consider fluid air dynamics or temperature stratification resultant from UFAD, I am considering using the UFAD modelling guidance in the EDR Design Guidelines: HVAC Simulation Guidance (<a href="http://www.energydesignresources.com/resources/publications/design-guidelines/design-guidelines-hvac-simulation-guidelines.aspx" target="_blank">http://www.energydesignresources.com/resources/publications/design-guidelines/design-guidelines-hvac-simulation-guidelines.aspx</a>)</span></font></p>

<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB">This document addresses UFAD, but not specific to data center or hot/cold aisle. What Ive gotten out of the guidance is that for comfort UFAD applications, the upper portion of a room (non occupied ) space is defined as plenum and the internal loadings for the room are apportioned between the occupied zone and plenum. It seems to me that this method could be appropriate for hot/cold aisle scenarios as well, with the hot aisle as the plenum and cold as space. From the guidance equipments loads are suggested to be apportioned 67% space 33% plenum for comfort applications. </span></font></p>

<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB">My understanding of hot/cold aisle configurations is that cold air is supplied on the front side of the server racks, pulled through the racks by the server internal cooling fans, and exhausted in to the hot aisle. Following from this logic it seems to me that the equip load should apportioned mostly to the plenum (hot aisle). </span></font></p>

<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB">Does anyone have a better suggestion for load proportioning for a datacenter?  Am I over complicating this?</span></font></p>

<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB">My next challenge is modelling the Ice storage. I have 6 chillers of which 2 are dual mode CHW and Ice making. My guess is that I will have to model the dual mode units as 4 chillers (2 for CHW and 2 for ice) because of the different efficiencies and supply temps, while somehow using to the equip controls to make sure the chillers are not operating simultaneously. </span></font></p>

<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB">This will be another first attempt for me. If anyone knows of any useful modelling guidance docs or has any advice on this it would be highly appreciated.</span></font></p>

<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB">Thank you in advance and regards,</span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt" lang="EN-GB"> </span></font></p>
<p style="TEXT-JUSTIFY: inter-ideograph; TEXT-ALIGN: justify; LAYOUT-GRID-MODE: char" class="MsoNormal"><b><font color="gray" size="2" face="Book Antiqua"><span style="FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-GB">Shuichi Hendrickson</span></font></b><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="EN-GB"></span></font></p>

<p style="TEXT-JUSTIFY: inter-ideograph; TEXT-ALIGN: justify; LAYOUT-GRID-MODE: char" class="MsoNormal"><font color="gray" size="2" face="Book Antiqua"><span style="FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt" lang="EN-GB">Environmental Engineer, LEED AP</span></font><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="EN-GB"></span></font></p>

<p style="TEXT-JUSTIFY: inter-ideograph; TEXT-ALIGN: justify; LAYOUT-GRID-MODE: char" class="MsoNormal"><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="EN-GB"><br>
</span></font><b><font color="gray" size="2" face="Book Antiqua"><span style="FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt; FONT-WEIGHT: bold" lang="EN-GB">ERM Japan</span></font></b><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="EN-GB"></span></font></p>

<p style="TEXT-JUSTIFY: inter-ideograph; TEXT-ALIGN: justify; LAYOUT-GRID-MODE: char" class="MsoNormal"><font color="gray" size="2" face="Book Antiqua"><span style="FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt" lang="EN-GB">The Landmark Tower </span></font><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="EN-GB"></span></font></p>

<p style="TEXT-JUSTIFY: inter-ideograph; TEXT-ALIGN: justify; LAYOUT-GRID-MODE: char" class="MsoNormal"><font color="gray" size="2" face="Book Antiqua"><span style="FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt">Yokohama</span></font><font color="gray" size="2" face="Book Antiqua"><span style="FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt"> 19F</span></font><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt"></span></font></p>

<p style="TEXT-JUSTIFY: inter-ideograph; TEXT-ALIGN: justify; LAYOUT-GRID-MODE: char" class="MsoNormal"><font color="gray" size="2" face="Book Antiqua"><span style="FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt">2-2-1-1, Minatomirai, Nish</span></font><font color="gray" size="2" face="Book Antiqua"><span style="FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt" lang="PT-BR">i-ku</span></font><font face="MS Pゴシック"><span style="FONT-FAMILY: 'MS PGothic'" lang="PT-BR"></span></font></p>

<p style="TEXT-JUSTIFY: inter-ideograph; TEXT-ALIGN: justify; LAYOUT-GRID-MODE: char" class="MsoNormal"><font color="gray" size="2" face="Book Antiqua"><span style="FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt" lang="PT-BR">Yokohama, 220-8119, Japan</span></font><font size="2" face="Century"><span style="FONT-FAMILY: Century; FONT-SIZE: 10.5pt" lang="PT-BR"></span></font></p>

<p style="TEXT-JUSTIFY: inter-ideograph; TEXT-ALIGN: justify; LAYOUT-GRID-MODE: char" class="MsoNormal"><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="PT-BR"><br>
</span></font><font color="gray" size="2" face="Book Antiqua"><span style="FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt" lang="PT-BR">T:<a href="tel:%2B81%280%2945-640-3780" target="_blank" value="+81456403780">+81(0)45-640-3780</a> <br>
F:<a href="tel:%2B81%280%2945-640-3781" target="_blank" value="+81456403781">+81(0)45-640-3781</a><br></span></font><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="EN-GB"><a title="mailto:shuichi.hendrickson@erm.com
mailto:first.lastnamemasashi.hishiyama@erm.com
mailto:first.lastname@erm.com" href="mailto:shuichi.hendrickson@erm.com" target="_blank"><span lang="PT-BR">shuichi.hendrickson@erm.com</span></a></span></font><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="PT-BR"> <br>
</span></font><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="EN-GB"><a title="http://www.erm.com/" href="http://www.erm.com/" target="_blank"><span lang="PT-BR">www.erm.com</span></a></span></font><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="EN-GB"> </span></font><font color="black" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: black; FONT-SIZE: 10pt" lang="PT-BR"></span></font></p>

<p style="LAYOUT-GRID-MODE: char" class="MsoNormal"><i><font color="gray" size="2" face="Book Antiqua"><span style="FONT-STYLE: italic; FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10pt" lang="EN-GB">Ranked No1 All-Environmental Firm: ENR Magazine (2004, 2005, 2006, 2007)<br>
Environmental Adviser of the Year: Acquisitions Monthly (2005, 2006, 2008)</span></font></i><i><font color="gray" size="2" face="Book Antiqua"><span style="FONT-STYLE: italic; FONT-FAMILY: 'Book Antiqua'; COLOR: gray; FONT-SIZE: 10.5pt" lang="EN-GB"></span></font></i></p>

<p style="TEXT-JUSTIFY: inter-ideograph; TEXT-ALIGN: justify; LAYOUT-GRID-MODE: char" class="MsoNormal"><font color="teal" size="1" face="Webdings"><span style="FONT-FAMILY: Webdings; COLOR: teal; FONT-SIZE: 8pt" lang="EN-US">P</span></font><font color="teal" size="1" face="MS ゴシック"><span style="FONT-FAMILY: 'MS Gothic'; COLOR: teal; FONT-SIZE: 8pt" lang="EN-US"> </span></font><font color="teal" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: teal; FONT-SIZE: 8pt" lang="EN-US">Please consider the environment before printing this email</span></font><font face="MS Pゴシック"><span style="FONT-FAMILY: 'MS PGothic'" lang="EN-US"></span></font></p>

<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt" lang="EN-GB"> </span></font></p></div><br>
<hr>
<font color="gray" size="1" face="Arial"><br>This electronic mail message may contain information which is (a) LEGALLY PRIVILEGED, PROPRIETARY IN NATURE, OR OTHERWISE PROTECTED BY LAW FROM DISCLOSURE, and (b) intended only for the use of the Addressee (s) names herein. If you are not the Addressee (s), or the person responsible for delivering this to the Addressee (s), you are hereby notified that reading, copying, or distributing this message is prohibited. If you have received this electronic mail message in error, please contact us immediately and take the steps necessary to delete the message completely from your computer system. Thank you.<br>
<br>Please visit ERM's web site: <a href="http://www.erm.com/" target="_blank">http://www.erm.com</a><br></font></div><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br><br clear="all"><br>-- <br>
Patrick J Keeney<br>MArch-MSSD Candidate<br>410-299-5627<br>