If these are new spaces that you created it may be that you have not assigned a zone name to them. To check, go into your air side of the HVAC system, and get into Create a Zone screen and see if those to spaces show up. If they do and you want them there then create their zones and move the to the HVAC system you want them to be in. <div>
<br></div><div>Carol<br><br><div class="gmail_quote">On Wed, Jun 1, 2011 at 8:12 AM, Nick Caton <span dir="ltr"><<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
Hi Ashok,<br>
<br>
Open your .BDL file (notepad), find the "ERROR" text and the adjacent<br>
description of the problem, and that should help you resolve exactly<br>
what the problem is. Alternatively, you may be able to use the dialog in<br>
front of you to navigate to the source of the error within the eQuest<br>
interface.<br>
<br>
Looks on the surface and by your description that one or more zones is<br>
referencing one or more spaces that don't exist anymore or have been<br>
renamed. You probably need to delete the offending zones & adjust<br>
systems as necessary, or else recreate/rename/reassign the<br>
offending/missing spaces.<br>
<br>
~Nick<br>
<br>
<br>
<br>
NICK CATON, E.I.T.<br>
PROJECT ENGINEER<br>
Smith & Boucher Engineers<br>
25501 west valley parkway<br>
olathe ks 66061<br>
direct <a href="tel:913%20344.0036" value="+19133440036">913 344.0036</a><br>
fax <a href="tel:913%20345.0617" value="+19133450617">913 345.0617</a><br>
<a href="http://www.smithboucher.com" target="_blank">www.smithboucher.com</a><br>
<br>
<br>
-----Original Message-----<br>
From: <a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a><br>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>] On Behalf Of ashok<br>
singh<br>
Sent: Wednesday, June 01, 2011 4:02 AM<br>
To: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: [Equest-users] Regarding error in modeling<br>
<div><div></div><div class="h5"><br>
Dear all,<br>
i am working on a mall, i have done zoning for this mall.<br>
but due to some changes in zoning , i have done rezoning of the mall.<br>
now this model is running and simulating, but further any change in<br>
this model, shows error(Same as i attached) and not let it simulate.<br>
<br>
From last three days i am facing this problem, please gude me.<br>
thanks in advance.<br>
<br>
Regards<br>
Ashok SIngh<br>
M.Tech,<br>
Energy Engg.<br>
</div></div><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>