Hi Patrick,<div><br></div><div>It sure looks like you accidentally deleted something, and possibly only one thing, and are now getting what I'll call a rolling error. The best thing to do would be to zip up your .inp and .pd2 files and send them to us. </div>
<div><br></div><div>Carol<br><br><div class="gmail_quote">On Wed, Jun 1, 2011 at 12:06 PM, Patrick Keeney <span dir="ltr"><<a href="mailto:38keeney@cardinalmail.cua.edu">38keeney@cardinalmail.cua.edu</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;"><div>Hello All,</div>
<div> </div>
<div>At the moment, I am working through my first complete e-Quest model so please excuse my many questions. In general, are there any good help sites or resources. But, I have quesions regarding the errors that I am receiving:</div>
<div> </div>
<div>1) Below in bold is the transcript from the first error. Specifically, I don't recall being asked to input anything regarding the annual schedule. I've tried to find where I can control and fix this input, but have had no such luck. </div>
<div> </div>
<div><strong>Line 1038: Annual Schedule<br>Line 1038: Error Encountered:<br>"" = SPACE<br>== *****************************************************************************<br>NAME IS REQUIRED FOR THIS COMMAND<br>
Line 1038: Error Encountered:<br>"" = SPACE<br>**** ===== *********************************************************************<br>TYPE NOT FIRST KEYWORD<br>Line 1061: Error Encountered:<br> ..<br>TYPE must be specified for this command<br clear="all">
</strong></div>
<div><strong></strong> </div>
<div><strong></strong> </div>
<div>2) Regarding my second error, there are a slew of errors regarding a missing parent space (see below transcript in bold). But in checking the model, I can't find anything....probably because I don't know where to look.</div>
<div><strong></strong> </div>
<div><strong></strong> </div>
<div><strong>Line 1078: Error Encountered:<br>"1FFlr (G.N1.U1)" = UNDERGROUND-WALL<br>A PARENT SPACE must be defined before you can define this UNDERGROUND-WALL<br>Line 1083: Error Encountered:<br>"1FWest Wall (G.N1.E1)" = EXTERIOR-WALL<br>
A PARENT SPACE must be defined before you can define this EXTERIOR-WALL<br>Line 1089: Error Encountered:<br>"1FEast Wall (G.N1.E2)" = EXTERIOR-WALL<br>A PARENT SPACE must be defined before you can define this EXTERIOR-WALL<br>
Line 1095: Error Encountered:<br>"1FNorth Wall (G.N1.E3)" = EXTERIOR-WALL<br>A PARENT SPACE must be defined before you can define this EXTERIOR-WALL<br>Line 1101: Error Encountered:<br>"1FNorth Win (G.N1.E3.W1)" = WINDOW<br>
A PARENT EXTERIOR-WALL must be defined before you can define this WINDOW<br>Line 1113: Error Encountered:<br>"1FNorth Win (G.N1.E3.W2)" = WINDOW<br>A PARENT EXTERIOR-WALL must be defined before you can define this WINDOW<br>
Line 1125: Error Encountered:<br>"1FNorth Door (G.N1.E3.D1)" = DOOR<br>A PARENT EXTERIOR-WALL must be defined before you can define this DOOR<br>Line 1132: Error Encountered:<br>"1FCeiling (G.N1.I1)" = INTERIOR-WALL<br>
A PARENT SPACE must be defined before you can define this INTERIOR-WALL</strong></div>
<div> </div>
<div> </div>
<div> </div>
<div> </div>
<div> </div>
<div>Thanks for all help.</div>
<div><br>-- <br>Patrick J Keeney<br>MArch-MSSD Candidate<br><a href="tel:410-299-5627" value="+14102995627" target="_blank">410-299-5627</a><br></div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
</div>