<font size="+1">I have yet to try what you are doing but you would
need to treat each building separately. The number of floors in
the building will determine your baseline building as Nick pointed
out. Your method to deliver conditioned air to each zone in each
building is going to be separate even though you may use a plant
to provide for example, hot and cold water to both buildings. I
haven't looked ahead to see if you are going to run into a system
type conflict between the 2 buildings but if you do just use
common sense and determine what is the best way to go to maximize
energy efficiency. None of the "rules" are written in stone.
They are bendable if you have a good argument and can back it up
with hard data which eQuest will give you.<br>
Bruce Easterbrook P.Eng.<br>
Abode Engineering<br>
</font><br>
On 26/05/2011 12:07 AM, Praveen Jain wrote:
<blockquote
cite="mid:BANLkTin9YR9kkt5tJZNPNCgxTd9akxaPBg@mail.gmail.com"
type="cite">Thanks for your reply<br>
<br>
Nick, I have created both building in one single model to take
benefit of shading of building also as one single leed project.<br>
I am still not able to decide while choosing baseline building;
number of floors should be sum of all floor in project or maximum
number of floor of building.<br>
<br>
--<br>
With Regards<br>
Praveen<br>
<br>
<div class="gmail_quote">On Wed, May 25, 2011 at 7:22 PM, Nick
Caton <span dir="ltr"><<a moz-do-not-send="true"
href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>></span>
wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid
rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left:
1ex;">
<div link="blue" vlink="purple" lang="EN-US">
<div>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);">That’s what I’d do (but I’d also
ask the lists to be sure)!</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);">The only real distinction (and
potential for a problem) here is
that you have two buildings in one model. Provided
you continue to treat each
building separately, both in building your baseline
and in documentation, I don’t
see any base reason why a reviewer would reject the
models.</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);">Can anyone share a successful
2-building-1-model submittal
experience to confirm this alone isn’t an issue?</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);">~Nick</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);"><img
src="cid:part1.01040402.09010404@bellnet.ca"
alt="cid:489575314@22072009-0ABB" height="37"
width="119"></span><b><span style="font-size: 11pt;
color: rgb(45, 77, 94);"></span></b></p>
<p class="MsoNormal"><b><span style="font-size: 11pt;
color: rgb(45, 77, 94);"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size: 11pt;
color: rgb(45, 77, 94);">NICK CATON, E.I.T.</span></b><b><span
style="color: rgb(45, 77, 94);"></span></b></p>
<p class="MsoNormal"><span style="font-size: 7.5pt; color:
rgb(204, 153, 0);">PROJECT ENGINEER</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color:
rgb(45, 77, 94);">Smith & Boucher Engineers</span><span
style="font-size: 7.5pt; color: rgb(204, 153, 0);"></span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color:
rgb(45, 77, 94);">25501 west valley parkway</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color:
rgb(45, 77, 94);">olathe ks 66061</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color:
rgb(45, 77, 94);">direct 913 344.0036</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color:
rgb(45, 77, 94);">fax 913 345.0617</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);"><a moz-do-not-send="true"
href="http://www.smithboucher.com"
title="blocked::www.smithboucher.com"
target="_blank"><span style="font-size: 10pt;">www.smithboucher.com</span></a></span><u><span
style="font-size: 10pt; color: blue;"> </span></u><span
style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color:
rgb(31, 73, 125);"> </span></p>
<div style="border-style: solid none none; border-color:
rgb(181, 196, 223) -moz-use-text-color
-moz-use-text-color; border-width: 1pt medium medium;
padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span
style="font-size: 10pt;">
<a moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org"
target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org"
target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>varun
kulkarni<br>
<b>Sent:</b> Wednesday, May 25, 2011 6:59 AM<br>
<b>To:</b> Praveen Jain<br>
<b>Cc:</b> <a moz-do-not-send="true"
href="mailto:equest-users@lists.onebuilding.org"
target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] ASHRAE90.1
Baseline System</span></p>
</div>
<div>
<div class="h5">
<p class="MsoNormal"> </p>
<div>
<p class="MsoNormal">Prateek,</p>
</div>
<div>
<p class="MsoNormal">The first column for table
G3.1.1A says for Non residential
5 floors or less and 25,000 SF to 150,000 SF. I
think your sytem should fall
under this and so Baseline System 6 should be the
right choice. I
dont know if adding the floors on the two
buildings is a good idea !!
</p>
</div>
<div>
<p class="MsoNormal">Anyone else in support or in
disagreement with my comment ?</p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal">On Wed, May 25, 2011 at 4:53
AM, Praveen Jain <<a moz-do-not-send="true"
href="mailto:praveenjain83@gmail.com"
target="_blank">praveenjain83@gmail.com</a>>
wrote:</p>
</div>
<div>
<blockquote style="border-style: none none none
solid; border-color: -moz-use-text-color
-moz-use-text-color -moz-use-text-color rgb(204,
204, 204); border-width: medium medium medium 1pt;
padding: 0in 0in 0in 6pt; margin-left: 4.8pt;
margin-right: 0in;">
<p class="MsoNormal"><span style="font-size:
10pt;">Dear All,</span></p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="font-size:
10pt;">I am working on a project which has two
towers within
the same LEED boundary. One tower is 3 stories
and another is 4 stories. Total
conditioned area of the project is 70000 ft<sup>2</sup>.
Heating type of my
project is Electric.</span></p>
<p class="MsoNormal"><span style="font-size:
10pt;">In this case, what can be project
baseline system?
Should I choose baseline system 6 or baseline
System 8?</span></p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="font-size:
10pt;">Thanks in Advance</span></p>
<p class="MsoNormal" style="margin-bottom: 12pt;"><br
clear="all">
<span style="color: rgb(136, 136, 136);"><br>
-- <br>
with regards,<br>
Praveen K. Jain<br>
Roorkee<br>
</span><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a
blank message to <a moz-do-not-send="true"
href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG"
target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>
</blockquote>
</div>
<p class="MsoNormal"><br>
<br clear="all">
<br>
-- </p>
<p style="margin: 0in 0in 0.0001pt;"><a
moz-do-not-send="true"
name="130276d9be44cc01_SafeHtmlFilter_SafeHtmlFilter__MailAutoS"><span>Thanks
and
Best Regards,</span></a></p>
<p style="margin: 0in 0in 0.0001pt;"><span> </span></p>
<p style="margin: 0in 0in 0.0001pt;"><span>Sincerely,</span></p>
<p style="margin: 0in 0in 0.0001pt;"><span>Varun
Kulkarni , M.S. , EIT</span></p>
<p style="margin: 0in 0in 0.0001pt;"><span> </span></p>
<p style="margin: 0in 0in 0.0001pt;"><span>Note:
Please do not print, unless required.</span></p>
<p> </p>
<p class="MsoNormal"> </p>
</div>
</div>
</div>
</div>
</blockquote>
</div>
<br>
<br clear="all">
<br>
-- <br>
with regards,<br>
Praveen K. Jain<br>
Roorkee<br>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>