<div>I want to compare RTU (DX cooling with evaporatively cooled condenser) with different compressors and am thinking of using curves this time around. </div><div>I would like to confirm if the following is correct - </div>
<div>1. The first curve is EIR - f(t ent wb, t ent cond). I am assuming that t ent wb is the wet-bulb temperature of air entering the coil (i.e. the mixed air wet bulb temperature) - 67 F wet bulb ARI condition - and t ent cond is the OA dry bulb (95 F ARI condition).</div>
<div>2. For EIR vs PLR, the above ARI conditions should be kept constant and use the EIR for varying capacity.</div><div> </div><div>Thanks,</div><div>-Rohini</div>