    You can certainly reference COOLING-CAPACITY for a SYSTEM component
    within a user-defined expression that populates COOLING-EIR for the
    same component.  All such references are classified as "local". 
    However, if COOLING-CAPACITY may not be defined then your expression
    would have to accommodate that (by checking for its validity) and
    you would likely have to set the return COOLING-EIR to something
    like "undefined" in that event that it is invalid.<br>
    If you would like this to work they way you have described it (via
    expressionized inputs), you might try something along these lines:<br>
    - install temporary/placeholder EIRs<br>
    - perform a "sizing" run on your model<br>
    - install cooling capacities (and perhaps air flows) based on the
    sizing run results<br>
    - then plug in your COOLING-EIR expressions (that depend on
    COOLING-CAPACITY)<br>
    If subsequent changes in your model cause you have to change one or
    more COOLING-CAPACITY inputs, then your expressions defined for
    COOLING-EIR should adjust accordingly.<br>
    <br>
    - Scott<br>
    <br>
    <br>
    On 5/18/2011 8:37 AM, Jeremy Poling wrote:
    <blockquote
cite="mid:FAFEA6DD2FFC2140A17D9A8E19187DE306FA33BB@EXCH-01.transwestern.net"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
..shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Verdana;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:"AvantGarde Bk BT";}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
h5
        {mso-style-priority:9;
        mso-style-link:"Heading 5 Char";
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:10.0pt;
        font-family:"Times New Roman","serif";}
p.MsoBodyText, li.MsoBodyText, div.MsoBodyText
        {mso-style-priority:99;
        mso-style-link:"Body Text Char";
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";}
p.msochpdefault, li.msochpdefault, div.msochpdefault
        {mso-style-name:msochpdefault;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:10.0pt;
        font-family:"Times New Roman","serif";}
span.balloontextchar0
        {mso-style-name:balloontextchar;
        font-family:"Tahoma","sans-serif";}
span.emailstyle19
        {mso-style-name:emailstyle19;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
span.emailstyle20
        {mso-style-name:emailstyle20;
        font-family:"Calibri","sans-serif";
        color:windowtext;
        font-weight:normal;
        font-style:normal;
        text-decoration:none none;}
span.EmailStyle23
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.EmailStyle24
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.Heading5Char
        {mso-style-name:"Heading 5 Char";
        mso-style-priority:9;
        mso-style-link:"Heading 5";
        font-weight:bold;}
span.BodyTextChar
        {mso-style-name:"Body Text Char";
        mso-style-priority:99;
        mso-style-link:"Body Text";}
..MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">That
            was the only problem in my mind – I figured a try and see
            approach would get to the bottom of it.  Scott is probably
            much more familiar with this than I am, but there are no
            problems referencing local keywords under the same parent
            from what I have seen.  You can setup a function that
            defines the WIDTH keyword of a window as a function of the
            HEIGHT keyword of the same window without a problem.  The
            issue I was worried about (and you are as well) would be
            using a local keyword as a reference when that keyword is
            determined by the program and not explicitly defined in the
            input file.  <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">It
            would probably take me at least a few hours of playing
            around with it to figure out if I can even reference the
            COOLING-CAPACITY keyword under the COOLING-EIR.  <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><b><span style="font-size: 7.5pt;
                font-family: "Verdana","sans-serif";
                color: rgb(31, 73, 125);">Jeremy R. Poling, PE, LEED
                AP+BDC</span></b><span style="color: rgb(31, 73, 125);"><br>
            </span><span style="color: rgb(31, 73, 125);"> <o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><o:p> </o:p></span></p>
        <div>
          <div style="border-right: medium none; border-width: 1pt
            medium medium; border-style: solid none none; border-color:
            rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color;
            padding: 3pt 0in 0in;">
            <p class="MsoNormal"><b><span style="font-size: 10pt;
                  font-family:
                  "Tahoma","sans-serif";">From:</span></b><span
                style="font-size: 10pt; font-family:
                "Tahoma","sans-serif";"> Bishop,
                Bill [<a class="moz-txt-link-freetext" href="mailto:wbishop@pathfinder-ea.com">mailto:wbishop@pathfinder-ea.com</a>] <br>
                <b>Sent:</b> Wednesday, May 18, 2011 8:52 AM<br>
                <b>To:</b> Jeremy Poling; Dahlstrom, Aaron;
                <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Cc:</b> Scott Criswell<br>
                <b>Subject:</b> RE: [Equest-users] Appendix G Baseline
                Systems 1 and 2 efficiency<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Jeremy,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Can
            a child component (COOLING-EIR) reference the keyword value
            of another child component (COOLING-CAPACITY) of the same
            parent?<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">In
            the case I’m describing, there is no keyword value for
            COOLING-CAPACITY, since it is calculated by the program, not
            entered. Is there any way to reference program output with a
            user input function?<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Thanks,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Bill<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><o:p> </o:p></span></p>
        <div>
          <div style="border-right: medium none; border-width: 1pt
            medium medium; border-style: solid none none; border-color:
            rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color;
            padding: 3pt 0in 0in;">
            <p class="MsoNormal"><b><span style="font-size: 10pt;
                  font-family:
                  "Tahoma","sans-serif";">From:</span></b><span
                style="font-size: 10pt; font-family:
                "Tahoma","sans-serif";"> Jeremy
                Poling [<a class="moz-txt-link-freetext" href="mailto:Jeremy.Poling@transwestern.net">mailto:Jeremy.Poling@transwestern.net</a>] <br>
                <b>Sent:</b> Tuesday, May 17, 2011 11:52 PM<br>
                <b>To:</b> Dahlstrom, Aaron; Bishop, Bill;
                <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> RE: [Equest-users] Appendix G Baseline
                Systems 1 and 2 efficiency<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div id="idOWAReplyText54174">
          <div>
            <p class="MsoNormal"><span style="font-size: 10pt;
                font-family: "Arial","sans-serif";
                color: black;">Have you thought about using a "user
                input function" to define the EIR?  I haven't used one
                this way yet, but there are a few examples out there in
                the help info.  In theory, you could setup a logic
                statement that checks the capacity and uses the EIR
                value appropriate for that size system.  I'd be willing
                to discuss the idea with you guys, but there'll be a
                certain amount of "if at first you don't succeed..."
                involved to figure out the right code to grab the system
                capacity.</span><span style="font-size: 12pt;
                font-family: "Times New
                Roman","serif";"><o:p></o:p></span></p>
          </div>
          <div>
            <p class="MsoNormal"><span style="font-size: 12pt;
                font-family: "Times New
                Roman","serif";"> <o:p></o:p></span></p>
          </div>
          <div>
            <p class="MsoNormal"><span style="font-size: 10pt;
                font-family: "Arial","sans-serif";">I've
                been playing more with user input functions after seeing
                some examples of powerful ways they can remove some of
                the repetitive changes.  For example, for single-zone
                systems, you could theoretically program eQuest to
                auto-calculate the OA based on ASHRAE 62.1 requirements
                and the zone area and population.  You could probably do
                it for multi-zone systems also, but that gets into the
                complexity level of the ASHRAE 62.1 spreadsheet and it
                is probably less time to just do the calcs in the
                spreadsheet and input the results.</span><span
                style="font-size: 12pt; font-family: "Times New
                Roman","serif";"><o:p></o:p></span></p>
          </div>
          <div>
            <p class="MsoNormal"><span style="font-size: 12pt;
                font-family: "Times New
                Roman","serif";"> <o:p></o:p></span></p>
          </div>
        </div>
        <div id="idSignature77069">
          <div>
            <div>
              <div>
                <p class="MsoNormal"><b><span style="font-size: 7.5pt;
                      font-family:
                      "Verdana","sans-serif"; color:
                      black;">Jeremy R. Poling, PE, LEED AP+BDC</span></b><span
                    style="color: black;"><o:p></o:p></span></p>
              </div>
            </div>
          </div>
        </div>
        <div>
          <p class="MsoNormal"><span style="font-size: 12pt;
              font-family: "Times New
              Roman","serif";"><o:p> </o:p></span></p>
          <div class="MsoNormal" style="text-align: center;"
            align="center"><span style="font-size: 12pt; font-family:
              "Times New Roman","serif";">
              <hr width="100%" align="center" size="2"></span></div>
          <p class="MsoNormal" style="margin-bottom: 12pt;"><b><span
                style="font-size: 10pt; font-family:
                "Tahoma","sans-serif";">From:</span></b><span
              style="font-size: 10pt; font-family:
              "Tahoma","sans-serif";">
              <a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a> on behalf of
              Dahlstrom, Aaron<br>
              <b>Sent:</b> Tue 5/17/2011 10:31 PM<br>
              <b>To:</b> Bishop, Bill;
              <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
              <b>Subject:</b> Re: [Equest-users] Appendix G Baseline
              Systems 1 and 2 efficiency</span><span style="font-size:
              12pt; font-family: "Times New
              Roman","serif";"><o:p></o:p></span></p>
        </div>
        <div>
          <p class="MsoNormal"><span style="font-size: 12pt;">Bill:</span><o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal"><span style="font-size: 12pt;">Your
              procedure sounds very similar to ours.</span><o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal"><span style="font-size: 12pt;">Beyond the
              simple automation of a spreadsheet, and dual monitors to
              copy data from SIM to XLS quickly, we haven’t found any
              quicker ways to skin this cat.</span><o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <div>
            <p class="MsoNormal" style="line-height: 150%;"><b><span
                  style="font-size: 9pt; line-height: 150%; font-family:
                  "Verdana","sans-serif"; color:
                  gray;">Aaron Dahlstrom , PE, LEED® AP</span></b><o:p></o:p></p>
            <p class="MsoNormal" style="line-height: 150%;"><b><span
                  style="font-family: "AvantGarde Bk BT";
                  color: rgb(23, 54, 93);">In P</span></b><b><span
                  style="font-family: "AvantGarde Bk BT";
                  color: rgb(97, 148, 40);">o</span></b><b><span
                  style="font-family: "AvantGarde Bk BT";
                  color: rgb(23, 54, 93);">sse</span></b><span
                style="font-size: 9pt; line-height: 150%; font-family:
                "Verdana","sans-serif"; color:
                gray;"> – </span><span style="font-size: 8pt;
                line-height: 150%; font-family:
                "Verdana","sans-serif"; color:
                gray;">A subsidiary of</span><span style="font-size:
                9pt; line-height: 150%; font-family:
                "Verdana","sans-serif"; color:
                gray;"> </span><b><span style="font-size: 9pt;
                  line-height: 150%; font-family:
                  "Verdana","sans-serif"; color:
                  rgb(204, 0, 0);">AKF</span></b><span style="font-size:
                9pt; line-height: 150%; font-family:
                "Verdana","sans-serif"; color:
                gray;">| 1500 Walnut Street, Suite 1414, Philadelphia,
                PA 19102 </span><o:p></o:p></p>
            <p class="MsoNormal" style="line-height: 150%;"><span
                style="font-size: 9pt; line-height: 150%; font-family:
                "Verdana","sans-serif"; color:
                gray;">d: 215-282-6753| m: 267-507-5470| In Posse:
                215-282-6800| AKF: 215-735-7290</span><o:p></o:p></p>
            <p class="MsoNormal"><span style="font-size: 9pt;
                font-family: "Verdana","sans-serif";
                color: gray;">e: <a class="moz-txt-link-abbreviated" href="mailto:ADahlstrom@in-posse.com">ADahlstrom@in-posse.com</a> | in posse web:
                <a moz-do-not-send="true"
                  href="http://www.in-posse.com/">www.in-posse.com</a> |
                akf web: <a moz-do-not-send="true"
                  href="http://www.akfgroup.com/">www.akfgroup.com</a></span><o:p></o:p></p>
            <p class="MsoNormal"> <o:p></o:p></p>
            <p class="MsoNormal"> <o:p></o:p></p>
          </div>
          <p class="MsoNormal"> <o:p></o:p></p>
          <div>
            <div style="border-right: medium none; border-width: 1pt
              medium medium; border-style: solid none none;
              border-color: rgb(181, 196, 223) -moz-use-text-color
              -moz-use-text-color; padding: 3pt 0in 0in;">
              <p class="MsoNormal"><b><span style="font-size: 10pt;
                    font-family:
                    "Tahoma","sans-serif";">From:</span></b><span
                  style="font-size: 10pt; font-family:
                  "Tahoma","sans-serif";">
                  <a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
                  [<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On
                    Behalf Of </b>Bishop, Bill<br>
                  <b>Sent:</b> Tuesday, May 17, 2011 3:43 PM<br>
                  <b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                  <b>Subject:</b> [Equest-users] Appendix G Baseline
                  Systems 1 and 2 efficiency</span><o:p></o:p></p>
            </div>
          </div>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal">Appendix G Baseline Systems 1 (PTAC) and
            2 (PTHP) have cooling efficiencies (and for PTHP, heating
            efficiencies) that vary with cooling capacity per Table
            6.8.1D. Since each thermal block is modeled with its own
            system, you can end up modeling as many as 100 or more
            systems per project. For LEED projects (or other App. G
            models), I have been calculating and manually entering
            values for cooling EIR for every single system, based on
            capacities reported in the SV-A reports. I factor in the
            unique fan power (per G3.1.2.9) for each system and remove
            its contribution from the efficiency, since fan power is
            included in EER and needs to be separated per G3.1.2.1. Once
            you enter efficiency for each system, just about any change
            you make in the model changes the supply flow rate and/or
            system capacities, which means you need to redo all the
            efficiency calculations.<o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal">Does this method seem correct?<o:p></o:p></p>
          <p class="MsoNormal">Has anyone figured out a way to automate
            this process? (And by “automate”, I don’t mean give it to
            the intern.)<o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal">Thanks,<o:p></o:p></p>
          <p class="MsoNormal">Bill<o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal"><img id="Picture_x0020_1"
              src="cid:part1.05070809.01090701@doe2.com" alt="Signature
              in jpg form" width="496" border="0" height="123"><o:p></o:p></p>
          <p class="MsoNormal"> <o:p></o:p></p>
          <p class="MsoNormal"><span style="font-size: 12pt;
              font-family: "Times New
              Roman","serif";"><br clear="all">
              This e-mail may contain information that is confidential,
              privileged or otherwise protected from disclosure. If you
              are not an intended recipient of this e-mail, do not
              duplicate or redistribute it by any means. Please delete
              it and any attachments and notify the sender that you have
              received it in error. Unintended recipients are prohibited
              from taking action on the basis of information in this
              e-mail. E-mail messages may contain computer viruses or
              other defects, may not be accurately replicated on other
              systems, or may be intercepted, deleted or interfered
              without the knowledge of the sender or the intended
              recipient. If you are not comfortable with the risks
              associated with e-mail messages, you may decide not to use
              e-mail to communicate with In Posse. <o:p></o:p></span></p>
        </div>
      </div>