<div>Hey, Xiaoyang,</div><div><br></div>View the report <b>PV-A: Plant Design Parameters</b>. If there is water loop in the model, there will be a "circulation loops" section which contain a keyword "Loop Flow (Gal/Min)".<div>

<br></div><div><b>Loop Flow (Gal/Min)</b>:is the flow at the larger of the HEATING-CAPACITY or COOLING-CAPACITY, at the design loop temperature change. (Page 167, DOE2.2 Volume4: Libraries & Reports)<br><div><br clear="all">

Best Regards,<div><br></div><div>Grammy, Jiang</div><br>
<br><br><div class="gmail_quote">On Thu, May 12, 2011 at 03:45, xiaoyang shi <span dir="ltr"><<a href="mailto:xs2144@gmail.com">xs2144@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">

Hi folks,<br><br>From equest output Air-side HVAC summary, we can get the design air flow rate "cfm". <br><br>However, in the Water-side HVAC summary, there is nothing. Where could we get the water design flow rate?<br>


<br>Thank you very much.<br><br><input type="hidden"><input type="hidden"><div></div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div></div>