size=2 face=Arial>Jamie,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=130122715-09052011><FONT color=#0000ff 
size=2 face=Arial>After you've run your model click on the component tree a the 
bottom left. Click on water side and find the pump you want to learn about in 
the tree on the left (or the picture in the large "P&ID" in the middle). 
Double click on it, then click on the curve tab. This will show you the name of 
the curve associated with the equipment. You need to remember the name, go back 
to the tree and under the "Performance Curves" folder, find the curve and double 
click it. There you can find information about the curve in 
question.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=130122715-09052011><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=130122715-09052011><FONT color=#0000ff 
size=2 face=Arial>Note that to edit the curve (vs just look at it) you need to 
be in detailed data edit mode. Might be worth reading up a bit in the 
documentation about the two modes and when you want to switch between. Once you 
switch from data back to the wizard, you'll lose the detailed data you've 
entered...</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=130122715-09052011><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=130122715-09052011><FONT color=#0000ff 
size=2 face=Arial>hope that helps,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=130122715-09052011><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=130122715-09052011><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=130122715-09052011>
<DIV align=left><FONT face=Arial>Erik Turner <FONT size=1>EIT, LEED 
AP+BD+C</FONT></FONT></DIV>
<DIV align=left><FONT size=2 face=Arial></FONT> </DIV>
<DIV align=left><FONT size=2 face=Arial>Mechanical Engineer<BR>Robison 
Engineering</FONT></DIV>
<DIV align=left><FONT size=2 face=Arial>P: (206) 364-3343</FONT></DIV>
<DIV align=left><FONT size=2 face=Arial>F: (206) 364-3363</FONT></DIV>
<DIV align=left><A href="http://www.robisonengineering.com/"><FONT color=#000000 
size=2 face=Arial>www.robisonengineering.com</FONT></A></DIV></SPAN></DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> equest-users-bounces@lists.onebuilding.org 
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>jaime 
perpinan<BR><B>Sent:</B> Friday, May 06, 2011 3:40 PM<BR><B>To:</B> 
equest-users@lists.onebuilding.org<BR><B>Subject:</B> [Equest-users] performance 
or pump curve<BR></FONT><BR></DIV>
<DIV></DIV>Hello<BR><BR>Im a newby to eQuest and email list trying to find out 
about performance and pump curves. Im currently run simulation on a H2o screw 
pump and trying to figure out how to view the performance curves. Any 
information is welcome<BR><BR>Thank you<BR><BR>J<BR></BODY></HTML>