I am having a problem with a fluid cooler on a project.  The fluid 
cooler is a closed circuit cooler that provides heat rejection for a 
heat pump loop.  I can get the model to run if I omit the heat exchanger
 which is integral to the fluid cooler or if I provide a Wet Schedule, 
but delete the heat exchanger.  I realize that neither one of these 
options will give me the results that I truly need, but it sort of works
 for some comparative purposes.  I have also tried this on 3.63 with the
 same results.<br>
<br>When I run either of the options identified above, I get the following messages:<br><br> **CAUTION********************<div id=":1nw">**************************************************<br>             In curve: FluidCooler-FluidCap-fRng&WB     the dependent value<br>

             is exceeding the limits.<br>             Value/Min/Max/First time:          4.981          0.000          3.000   1/27/16<br>CURINV: No real root for CURVE: <br> 1  0.449745  0.027043 -0.000444 -0.028325  0.000285  0.001570<br>

<br>The CAUTION I can get around.  But the CURINV, which relates to the 
FluidCooler-FluidCap-fAPP&WB performance curve, typically ends up as
 thousands of lines in the output file.  I have yet been able to 
identify the cause.<br>
<br>When I add the heat exchanger, the model crashes and I get the following error:<br> ***ERROR*********************<div>**************************************************<br>

             Heat-Exchanger: FluidCooler-DryHX                has inconsistent<br>             input parameters for flow calculations<br>                   Mode     SupTi     DemTi     DemTo<br>                      3     39.00     82.00     82.00</div>

<br clear="all">The values for SupTi, DemTi and DemTo will vary depending on other parameters that I may change, but DemTi always equals DemTo.<br><br>I
 can provide the input and pd2 files if necessary, but hesitate due to size and complexity of the building 
model, but it's what I have to deal with.<br>
<br>I also note that the pan losses/pan heater are not accounted for in the model.  I am not sure if this feature is supported at this time or not.  The unit has an electric pan heater, which I input.  I have tried both defaulting the values and inputting the pan loss, but neither results in any energy use for the heater.  </div>