I am having issues with the heat exchanger for a fluid cooler (closed circuit cooling tower) in eQuest 3.64. I can run the simulation without the heat exchanger, but get a series of the following message:<br>CURINV: No real root for CURVE: <br>
1 0.449745 0.027043 -0.000444 -0.028325 0.000285 0.001570<br>which appears to be from the FluidCooler-FluidCap-fApp&WB performance curve. This is likely due in part to operating the system at freezing temperatures with the spray pump on.<br>
<br>If I add the heat exchanger so that I have a dry cooler for the winter months (set the Wet Schedule to 60F), I get the following error:<br> ***ERROR***********************************************************************<br>
Heat-Exchanger: FluidCooler-DryHX has inconsistent<br> input parameters for flow calculations<br> Mode SupTi DemTi DemTo<br> 3 39.00 82.00 82.00<br>
I allow everything for the heat exchanger to default as well as the performance curves for the fluid cooler. The values for SupTi, DemTi and DemTo will vary somewhat, but DemTi always equals DemTo, which I think may be a problem.<br>
<br>The fluid cooler serves a heat pump loop that also serves as the condenser water loop for a chiller. I'm trying to maintain the HP loop temperature between 75 and 85F with additional heat provided by a boiler. I have attached the .inp and .pd2 files if they may be of help.<br>
<br>Any help would be appreciated.<br clear="all"><br>-- <br>Ron Pecarina, PE, CEM, LEED-AP<br>Energy and Sustainable Design Consultants, Inc.<br>1128 Noblewood Drive<br>Billings, MT 59101<br><a href="tel:406-208-0227" value="+14062080227" target="_blank">406-208-0227</a><br>