Travis<div><br></div><div>With a 157' x 157' floor plate and a 12'-0" floor to floor height, you have tipped your internal-external gain scale, heavily on the internal gain side!</div><div><br></div><div>Beyond load implications the building will provide no access to views or daylight for most of its occupants.</div>
<div><br></div><div>Now if this is actually a cross-section of a tower you are simulating, than you will want to make sure the first level does not have ground exposure and the top and bottom slabs of the model are thermally inert.</div>
<div><br></div><div><br></div><div><br><br><div class="gmail_quote">On Tue, May 3, 2011 at 11:58 AM, Carol Gardner <span dir="ltr"><<a href="mailto:cmg750@gmail.com">cmg750@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
Travis,<br><br>I'm not sure what standard you are modeling to but I've never seen one that allows you to set 5 foot perimeters; not sure why you would want to either. So, just about all of your people, lighting, equipment, etc., are there in the core space.<br>
<br>Try a 15 foot perimeter and see if that helps.<br><font color="#888888"><br>Carol</font><div><div></div><div class="h5"><br><br><div class="gmail_quote">On Tue, May 3, 2011 at 8:45 AM, Travis Rhodes <span dir="ltr"><<a href="mailto:TRhodes@smud.org" target="_blank">TRhodes@smud.org</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div link="blue" vlink="purple" lang="EN-US">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">I accidentally sent this to Carol only, but if anyone else wants to take a look at it that would be appreciated.
</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> Carol Gardner [mailto:<a href="mailto:cmg750@gmail.com" target="_blank">cmg750@gmail.com</a>]
<br></span></p><div>
<b>Sent:</b> Monday, May 02, 2011 4:26 PM<br>
<b>To:</b> Charles Land<br>
</div><b>Cc:</b> Travis Rhodes; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Odd peak cooling day<p></p>
</div><div><div></div><div>
<p class="MsoNormal"> </p>
<p class="MsoNormal" style="margin-bottom:12.0pt">Are you willing to send us your .inp and .pd2 files?<br>
<br>
Carol</p>
<div>
<p class="MsoNormal">On Mon, May 2, 2011 at 11:55 AM, Charles Land <<a href="mailto:cland@geo-marine.com" target="_blank">cland@geo-marine.com</a>> wrote:</p>
<div>
<div>
<p class="MsoNormal"><span style="color:#1F497D">I see that this is the peak load for a single space which is a core space. Does this space have any exterior walls, and is there a 2<sup>nd</sup> floor
above this space. If its an interior area the outside weather conditions shouldn’t have any effect on the cooling load for this space.</span></p>
<p class="MsoNormal"><span style="color:#1F497D"> </span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Travis Rhodes<br>
<b>Sent:</b> Monday, May 02, 2011 2:40 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Odd peak cooling day</span></p>
</div>
</div>
<div>
<p class="MsoNormal"> </p>
<p class="MsoNormal">I don’t know where I’ve gone wrong, but my peak cooling day is happening in December. The output is saying that there is a huge internal heat load from occupants on that day. As
far as I can tell the occupant schedule is correct. Any insight into this is appreciated.
</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"><img alt="outlook sig" border="0" height="132" width="268"></span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"> </p>
</div>
</div>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>
</div>
<p class="MsoNormal"><br>
<br clear="all">
<br>
-- <br>
Carol Gardner PE</p>
</div></div></div>
</div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div></div>
</div></div><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br><div><br></div><div><b><font size="2"><br></font></b></div><div><b><p>Arpan Bakshi<span style="border-collapse:collapse;font-family:arial, sans-serif;font-weight:normal"></span><b style="font-weight:normal"><span style="border-collapse:collapse;font-family:arial, sans-serif;font-weight:normal"><i> </i>LEED AP BD+C</span></b><span style="color:rgb(64, 64, 64);font-size:12px;font-weight:normal"></span></p>
</b></div><br>
</div>