<br><font size=2 face="sans-serif">Having the U Value change with temperature
would turn the basic 1D heat equation into a non-linear differential equation,
which would not be solvable by the convolution method used by DOE2. You
would need a finite difference wall model to account for a changing U value.
Maybe try some other software out there, but an hourly analysis of
this type will take a while to run.<br>
</font>
<table align=left>
<tr>
<td bgcolor=white><font size=2 color=#808080 face="Verdana"><b>Aaron Powers</b></font>
<tr>
<td bgcolor=white><font size=1 color=#808080 face="Verdana"><b>Johnson
Controls | Building Efficiency</b></font>
<tr>
<td bgcolor=white><font size=1 color=#808080 face="Verdana">Energy Solutions
Engineer</font>
<tr>
<td bgcolor=white><font size=1 color=#808080 face="Verdana">6935 Appling
Farms Pkwy # 112, Memphis, TN 38104</font>
<tr>
<td bgcolor=white><font size=1 color=#808080 face="Verdana">901 359 4255</font>
<tr>
<td bgcolor=white><a href=mailto:aaron.powers@jci.com><font size=1 color=blue face="Verdana"><u>aaron.powers@jci.com</u></font></a></table>
<br>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">"Harrity, Sean" <SHarrity@cosentini.com></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">"equest-users@lists.onebuilding.org"
<equest-users@lists.onebuilding.org></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">04/18/2011 01:49 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[Equest-users] U value temperature dependence
in eQUEST</font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=2 face="Arial">Hi,</font>
<br><font size=2 face="Arial"> </font>
<br><font size=2 face="Arial">Does anyone know if and how eQUEST accounts
for the temperature dependence of U values? For instance, some manufacturers
specify a summer design condition U value that is different from a winter
design condition U value. Ideally I would like to have eQUEST calculate
the hourly U value based on the hourly temperature to get accurate skin
loads throughout the whole year. If anyone knows how this can be done,
please let me know.</font>
<br><font size=2 face="Arial"> </font>
<br><font size=2 face="Arial">Thanks,</font>
<br><font size=2 face="Arial">Sean</font>
<br><font size=2 face="Arial"> </font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=1 color=#0060a0 face="Arial"><b>Sean Harrity</b></font><font size=1 color=#8f8f8f face="Arial">
|</font><font size=1 face="Arial"> </font><font size=1 color=#8f8f8f face="Arial"><b>Mechanical
Engineer</b><br>
Phone: 212-615-3923 | Fax: 212-615-3700</font><font size=1 face="Arial"><br>
sharrity@cosentini.com<br>
</font><font size=1 color=#8f8f8f face="Arial"><b><br>
Cosentini Associates - A Tetra Tech Company</b><br>
Two Pennsylvania Plaza - Third Floor - New York, NY 10121</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href=http://www.cosentini.com/><font size=1 color=blue face="Arial"><u>www.cosentini.com</u></font></a><font size=1 color=#8f8f8f face="Arial"><br>
</font>
<br><font size=3 face="Times New Roman"> </font>
<p><font size=3><br>
NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if any)
are intended solely for the use of the addressees hereof. In addition,
this message and the attachments (if any) may contain information that
is confidential, privileged and exempt from disclosure under applicable
law. If you are not the intended recipient of this message, you are prohibited
from reading, disclosing, reproducing, distributing, disseminating or otherwise
using this transmission. Delivery of this message to any person other than
the intended recipient is not intended to waive any right or privilege.
If you have received this message in error, please promptly notify the
sender by reply E-mail and immediately delete this message from your system.
</font><tt><font size=2>_______________________________________________<br>
Equest-users mailing list<br>
</font></tt><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"><tt><font size=2>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</font></tt></a><tt><font size=2><br>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<br>
</font></tt>
<p>
<p>