Thanks, Nick. Good explanation. I agree with the use the Wizards to their fullest capability method, and that it's a moving target based mostly on the modeler's experience. For me, I have run into stability issues in the Wizards, e.g. screens freezing, files crashing, enough that I just don't trust them. I get out quickly.<br>
<br>Carol<br><br><div class="gmail_quote">On Wed, Apr 13, 2011 at 4:55 PM, Nick Caton <span dir="ltr"><<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<div link="blue" vlink="purple" lang="EN-US">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Travis, </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">To this latest question – you can go either way. Modeling
a separate zone for each VAV is more accurate and permits specifying varying
capacities/loads/scheduling within the spaces. I perceive this as a necessary
degree of accuracy for something like a LEED submittal. Calling it one zone
means you’re modeling one monster VAV which will approximate all 20 VAV’s
in combination, operating in sync. The capacities (heating/cooling/airflow)
will autosize large enough to handle all zones at once and you’d specify “representative”
efficiencies/scheduling/fan kw/cfm and so forth to roughly equate to a “typical”
unit. This level of accuracy is what I’d call normal/fine for modeling
to compare various HVAC systems to approximate relative changes to other
elements like LPD or setback scheduling. What level of accuracy you “need”
is entirely up to the modeler (and reviewer, if applicable).</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Regarding Carol’s response earlier:</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Carol is quite right and raises a point I forgot to mention –
the issues below are entirely “fixable” within detailed mode (as
with most things). I took an approach to outline “what went wrong”
in wizard mode however as it was apparent Travis had a clear goal and simply
missed something along the way, after seemingly doing everything else right. </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">I fully agree with Carol that these particular issues are just
as quick (if not quicker) to resolve in detailed mode. In my humble opinion
though, taking a few minutes to learn how to use the wizards correctly is worth
the extra effort as you won’t be making the same mistakes to fix in your
next models =). To be clear, there’s nothing in the wizards you can’t
do in detailed mode – the only compelling reason to “go back”
to wizards is if you (1) have nothing/little to lose (you haven’t done
much work in detailed mode) or (2) you feel the time saved making a change in
the wizards will outweigh the time lost re-doing the detailed mode work (like
when your zone map has completely changed up). </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">I prescribe to the following mantra: “Use the wizards to
their <u>fullest time-saving extent</u> prior to entering detailed mode.”
Another way to put is “do as much as you can that you can’t do
faster in detailed mode.” This is obviously a moving target that varies
project-by-project and with one’s experience level, but it’s what I
strive for and this philosophy illustrates that the question of when to get out
of the wizards never has a black and white answer.</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Some prefer to get out of wizards ASAP because they’re
very fast/comfortable with detailed edits, while others spend time wrestling
with the wizards far longer than they should to achieve things that are done more
quickly/easily in detailed mode. I was solidly in the latter camp when first
learning eQuest and feeling apprehensive about detailed mode, and I know others
have the same hurdle… but in time everyone strikes a personal balance and
preference – you really figure this stuff out with experience and trying
new things. I’m self-taught for the most part, but learning what is most
efficiently done before/after the wizards is an area of knowledge I would expect
to be covered in quality formal training at various levels, as this is the sort
of topic that otherwise requires “doing it wrong once” to really
learn.</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">I’ll be out of the office thru the rest of this week, but
Travis if you or anyone else is interested in how to accomplish the same edits
in detailed mode and can’t figure it out, simply ask! I’m sure
Carol and others would be willing to help as individual time allows ;). </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Happy to help and best of luck!</span></p><div class="im">
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">~Nick</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><img src="cid:image002.jpg@01CBFA0B.89E1EC20" alt="cid:489575314@22072009-0ABB" height="37" width="119"></span><b><span style="font-size:11.0pt;color:#2D4D5E"></span></b></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E">NICK CATON, E.I.T.</span></b><b><span style="color:#2D4D5E"></span></b></p>
<p class="MsoNormal"><span style="font-size:7.5pt;color:#CC9900">PROJECT ENGINEER</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">Smith & Boucher Engineers</span><span style="font-size:7.5pt;color:#CC9900"></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">25501 west valley parkway</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">olathe ks 66061</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">direct <a href="tel:913%20344.0036" value="+19133440036" target="_blank">913 344.0036</a></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">fax <a href="tel:913%20345.0617" value="+19133450617" target="_blank">913 345.0617</a></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size:10.0pt">www.smithboucher.com</span></a></span><u><span style="font-size:10.0pt;color:blue"> </span></u><span style="font-size:11.0pt;color:#1F497D"></span></p>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
</div><div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Travis
Rhodes<br>
<b>Sent:</b> Wednesday, April 13, 2011 6:24 PM</span></p><div><div></div><div class="h5"><br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Difference between wizard and detailed mode</div></div><p></p>
</div>
</div><div><div></div><div class="h5">
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">I apologize for these soft ball questions in advance, but
I’m very appreciative of the help. If one of the 60 ton package units
supplies 20 VAV boxes, do I need to model 20 zones with the 60 ton as the
parent unit to these zones, or can I tell eQuest somewhere that there are 20
VAV boxes with 20 thermostats in one single zone?</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Copperplate Gothic Light";color:#1F497D">Travis Rhodes</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">ENERGY ADVISOR</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="tel:%28916%29732-5274" value="+19167325274" target="_blank">(916)732-5274</a></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="mailto:trhodes@smud.org" target="_blank">trhodes@smud.org</a></span></p>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Travis Rhodes<br>
<b>Sent:</b> Wednesday, April 13, 2011 2:52 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Difference between wizard and detailed mode</span></p>
</div>
</div>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">The reason is because I’ve never used eQuest before and
figured I’d start with the wizard to see how far I would get. </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Nick, thanks for the help, I’ll see how far I can get now.
</span><span style="font-size:11.0pt;font-family:Wingdings;color:#1F497D">J</span><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Copperplate Gothic Light";color:#1F497D">Travis Rhodes</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">ENERGY ADVISOR</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="tel:%28916%29732-5274" value="+19167325274" target="_blank">(916)732-5274</a></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="mailto:trhodes@smud.org" target="_blank">trhodes@smud.org</a></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> Carol Gardner
[mailto:<a href="mailto:cmg750@gmail.com" target="_blank">cmg750@gmail.com</a>] <br>
<b>Sent:</b> Wednesday, April 13, 2011 2:28 PM<br>
<b>To:</b> Nick Caton<br>
<b>Cc:</b> Travis Rhodes; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Difference between wizard and detailed mode</span></p>
</div>
<p class="MsoNormal"> </p>
<p class="MsoNormal" style="margin-bottom:12.0pt">Why not just do it detailed
edit? It's pretty easy to do there so I'm wondering if you have a reason I am
not thinking about for going back into the wizards.<br>
<br>
Carol</p>
<div>
<p class="MsoNormal">On Wed, Apr 13, 2011 at 2:21 PM, Nick Caton <<a href="mailto:ncaton@smithboucher.com" target="_blank">ncaton@smithboucher.com</a>> wrote:</p>
<div>
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Hey Travis,</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">What you’ve currently got is:</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">-</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">A 60ton unit for each floor’s core
zone (2 total)</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">-</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">A series of 5 and 7.5 ton units each
serving one perimeter zone (8 total) </span><span style="font-size:11.0pt;font-family:Wingdings;color:#1F497D">ß</span><span style="font-size:11.0pt;color:#1F497D"> note: cooling capacities appear to have been edited after the
wizards</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">-</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">Total units: 10</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">-</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">Picture:</span></p>
<p class="MsoNormal"><img src="cid:image003.png@01CBFA0B.89E1EC20" border="0" height="370" width="616"></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">It sounds like the desired is to have:</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">-</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">A 60ton unit for each floor’s core
zone (2 total)</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">-</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">15 ton units each serving two perimeter
zones (4 total)</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">-</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">Total units: 6</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">To pull this off you need to</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">1.</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">Go back to wizards</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">2.</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">Review/Correct the tonnage for the
smaller units, as necessary (wizard inputs don’t reflect 15 tons all
around)</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">3.</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">Select “system per site” in
the first screen of each system (note: you’ve got “system per
zone” selected currently, which assigns one system of the specified sort
to each zone in the shell associated… this is the main source of your
system quantity issue).</span></p>
<p><span style="font-size:11.0pt;color:#1F497D">4.</span><span style="font-size:7.0pt;color:#1F497D"> </span><span style="font-size:11.0pt;color:#1F497D">Assign the perimeter zones to the
appropriate systems (looks like you’ve already done this correctly,
but review to be sure assignments are correct).</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">When finished and on exiting the DD
wizard, you should observe the correct quantity of systems and zone assignments
on review of the airside HVAC tab/component tree.</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Best of luck!</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">~Nick</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><img src="cid:image002.jpg@01CBFA0B.89E1EC20" alt="cid:489575314@22072009-0ABB" border="0" height="37" width="119"></span></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E">NICK CATON, E.I.T.</span></b></p>
<p class="MsoNormal"><span style="font-size:7.5pt;color:#CC9900">PROJECT ENGINEER</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">Smith & Boucher Engineers</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">25501 west valley parkway</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">olathe ks 66061</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">direct <a href="tel:913%20344.0036" target="_blank">913 344.0036</a></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">fax <a href="tel:913%20345.0617" target="_blank">913 345.0617</a></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size:10.0pt">www.smithboucher.com</span></a></span><u><span style="font-size:10.0pt;color:blue"> </span></u></p>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of
</b>Travis Rhodes<br>
<b>Sent:</b> Wednesday, April 13, 2011 12:08 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a></span></p>
<div>
<p class="MsoNormal"><br>
<b>Subject:</b> Re: [Equest-users] Difference between wizard and detailed mode</p>
</div>
</div>
</div>
<div>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Thanks</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Copperplate Gothic Light";color:#1F497D">Travis
Rhodes</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">ENERGY ADVISOR</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="tel:%28916%29732-5274" target="_blank">(916)732-5274</a></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="mailto:trhodes@smud.org" target="_blank">trhodes@smud.org</a></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> Carol
Gardner [mailto:<a href="mailto:cmg750@gmail.com" target="_blank">cmg750@gmail.com</a>]
<br>
<b>Sent:</b> Wednesday, April 13, 2011 10:05 AM<br>
<b>To:</b> Travis Rhodes<br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Difference between wizard and detailed mode</span></p>
</div>
<p class="MsoNormal"> </p>
<p class="MsoNormal" style="margin-bottom:12.0pt">Hi
Travis,<br>
<br>
You need to attach the .inp file that this .pd2 file uses, too.<br>
<br>
Carol</p>
<div>
<p class="MsoNormal">On
Wed, Apr 13, 2011 at 9:56 AM, Travis Rhodes <<a href="mailto:TRhodes@smud.org" target="_blank">TRhodes@smud.org</a>> wrote:</p>
<div>
<div>
<p class="MsoNormal">I’m
trying to set up a really simple 2 story building with 6 rooftop units. Two 60
tons supply cooling only to the core of the two floors and the 4 15 ton units
take care of the perimeter. One unit supplies air to two walls on the first
floor and another unit takes the other two walls on that floor. This is
repeated on the second floor. In the wizard I set it up exactly like this and
inputted the performance data for each unit and named each unit but when I go
to detailed mode to modify the schedules to reflect the controls of the system
it has broken everything out completely different than what I assumed I had set
up in the wizard. I’ve attached the .pd2 file, I don’t know if this
is sufficient for anyone to look at what I’ve done.</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">I
appreciate anyone help on this. </p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="font-size:10.0pt">Error! Filename not specified.</span></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"> </p>
</div>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>
</div>
<p class="MsoNormal"><br>
<br clear="all">
<br>
-- <br>
Carol Gardner PE</p>
</div>
</div>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>
</div>
<p class="MsoNormal"><br>
<br clear="all">
<br>
-- <br>
Carol Gardner PE</p>
</div></div></div>
</div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; left: -5000px;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup{position: absolute;z-index: 9999;padding: 0px 0px;margin-left: 0px;margin-top: 0px;overflow: hidden;word-wrap: break-word;color: black;font-size: 10px;text-align: left;line-height: 130%;}</style>