<div dir="ltr"><font color="#000000" size="2" face="Tahoma">Vipul,</font></div>
<div dir="ltr"><font size="2" face="Tahoma"></font> </div>
<div dir="ltr"><font size="2" face="Tahoma">Does the air system have an airside economizer? If so, did you change the economizer low limit in the detailed interface? (Only the upper limit can be changed in the wizard, not the low limit.) The default is 40F,
so whenever it gets colder than that outside and there is still a cooling load from internal heat sources, the economizer will shut off and the chiller will come on to meet the load. The smallest number you can enter is 0, but if you delete the 40 and leave
the field blank, then there will be no lower limit. See the help screen.</font></div>
<div>
<div><font size="2" face="Tahoma">
<div>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">________________________________</span></font><font color="navy"><span style="COLOR: navy"></span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"><font color="navy"><span style="COLOR: navy">Keith Swartz</span></font><font color="navy"><span style="COLOR: navy">, P.E., LEED AP</span></font></span></font><font color="navy"><span style="COLOR: navy"></span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt"><br>
Energy Engineer / Senior Project Manager<br>
</span></font><strong><b><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"><font color="navy"><span style="COLOR: navy">Energy</span></font><font color="navy"><span style="COLOR: navy">
</span></font><font color="navy"><span style="COLOR: navy">Center</span></font><font color="navy"><span style="COLOR: navy"> of
</span></font><font color="navy"><span style="COLOR: navy">Wisconsin</span></font><font color="navy"><span style="COLOR: navy; FONT-WEIGHT: normal"><br>
</span></font><span style="FONT-WEIGHT: normal"></span></span></font></b></strong><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"><font color="navy"><span style="COLOR: navy">455 Science Drive, Suite 200</span></font><font color="navy"><span style="COLOR: navy">,
</span></font></span></font><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"><font color="navy"><span style="COLOR: navy">Madison</span></font><font color="navy"><span style="COLOR: navy">,
</span></font><font color="navy"><span style="COLOR: navy">WI</span></font><font color="navy"><span style="COLOR: navy">
</span></font><font color="navy"><span style="COLOR: navy">53711</span></font><br>
</span></font><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">Phone: 608.238.8276 x123<br>
Fax: 608.238.0523<br>
<br>
<strong><b><font face="Arial"><span style="FONT-FAMILY: Arial">The Buildings Team</span></font></b></strong></span></font><font color="navy"><span style="COLOR: navy"></span></font></p>
</div>
<div>
<p class="MsoNormal"><em><i><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">Design decisions through energy, economics and emissions analysis.</span></font></i></em><font color="navy"><span style="COLOR: navy"></span></font></p>
</div>
<div>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt"><a href="http://www.ecw.org/Buildings" target="_blank"><font color="#0000ff" face="Times New Roman"><span style="FONT-FAMILY: 'Times New Roman'">www.ecw.org/Buildings</span></font></a>
</span></font></p>
</div>
<p class="MsoNormal"><font color="navy" size="3" face="Times New Roman"><span style="COLOR: navy; FONT-SIZE: 12pt"><br>
</span></font><b><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt; FONT-WEIGHT: bold"><font color="navy"><span style="COLOR: navy">Energy</span></font><font color="navy"><span style="COLOR: navy">
</span></font><font color="navy"><span style="COLOR: navy">Center</span></font><font color="navy"><span style="COLOR: navy">
</span></font><font color="navy"><span style="COLOR: navy">University<br>
</span></font></span></font></b><i><font color="navy" size="2" face="Arial"><span style="FONT-STYLE: italic; FONT-FAMILY: Arial; COLOR: navy; FONT-SIZE: 10pt">Your gateway to sustainable design training and online education programs.<br>
</span></font></i><span style="COLOR: navy"><a title="http://www.ecw.org/university/" href="http://www.ecw.org/university/" target="_blank"><font color="#0000ff" size="2"><span style="FONT-SIZE: 10pt"><span title="http://www.ecw.org/university/">www.ecw.org/university/</span></span></font></a></span></p>
</font></div>
</div>
<div style="DIRECTION: ltr" id="divRpF262290">
<hr tabindex="-1">
<font size="2" face="Tahoma"><b>From:</b> Vipul Babriya [vipulbabriya@aol.com]<br>
<b>Sent:</b> Tuesday, April 05, 2011 11:12 AM<br>
<b>To:</b> equest-users@lists.onebuilding.org<br>
<b>Subject:</b> [Equest-users] Engine Driven Chiller-Gas Cooling Modeling<br>
</font><br>
</div>
<div></div>
<div><font color="black" size="2" face="Arial, Helvetica, sans-serif">
<div><br>
</div>
<div><font size="2"><font face="Arial, Helvetica, sans-serif">Hello All,<br>
<br>
I am modeling engine driven chiller in eQUEST for multifamily residential building which has Natural Gas as fuel.<br>
I have entered HIR at rated conditions into chiller property window in DD mode. </font>
</font><font size="2"><font face="Arial, Helvetica, sans-serif">Chiller is the only source for cooling in the model.<br>
</font></font><font size="2"><font face="Arial, Helvetica, sans-serif">When i ran the simulation, i would get space cooling usage in winter months. I don't understand why am i getting space cooling during winter months.
<br>
Do anybody has any idea ?<br>
<br>
Thanks,<br>
Vipul<br>