Hi Matt,<br><br>eQUEST defaults to .5cfm/sf for supply flow for all buildings that I have modeled. I am not sure how many people notice that and revise it to a more realistic number. There is plenty of supporting documentation from ASHRAE which suggests much higher levels should be used. I believe that this default may be the cause of many zones being out of throttling range which gives us all fits. It also might be why your cfm is too low. A word to the wise is to always review eQUEST defaults for usability.<br>
<br>I'd love to hear other peoples thoughts on this particular one.<br><br>Carol<br><br><div class="gmail_quote">On Thu, Mar 24, 2011 at 11:51 AM, Matt Dwyer <span dir="ltr"><<a href="mailto:MDwyer@dwyer.com">MDwyer@dwyer.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;"><div link="blue" vlink="purple" lang="EN-US"><div><p class="MsoNormal">Small building, Constant volume, One of the zones supplies 1000 cfm of makeup air to another zone </p>
<p class="MsoNormal">Space zone loads are maybe 42 KBtu/hr (not counting ventilation loads). Why would equest suggest a 1200 cfm fan is a good baseline (80% outside air). What input is likely incorrect? </p><p class="MsoNormal">
</p><font color="#888888"><p class="MsoNormal">Matt</p><p class="MsoNormal"> </p><p class="MsoNormal"> </p></font></div></div><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>