Riley,<br><br>If the over all U value and SC reported at the end of the LV-D report for each exposure match yours, I wouldn't worry about it. When you are looking at each window you are probably seeing some sort of adjustment for area.<br>
<br>Carol<br><br><div class="gmail_quote">On Thu, Mar 24, 2011 at 2:29 PM, Mehta, Gaurav <span dir="ltr"><<a href="mailto:Gaurav.Mehta@stantec.com">Gaurav.Mehta@stantec.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<div link="blue" vlink="purple" lang="EN-US"><div><p class="MsoNormal"><span style="font-size:10.0pt;color:blue">Use the formula below to convert Glazing U-value to Conductance.</span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:blue"> </span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:blue">Conductance = 1/((1/Glazing U)-0.2)</span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:blue"> </span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:blue">This formula  is from the DOE-2 Reference manual.</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:blue"> </span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:blue">Best regards,</span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:blue"> </span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:blue">Gaurav</span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:blue"> </span></p><div><div><p class="MsoNormal"><b><span style="font-size:9.0pt;color:black">Gaurav Mehta, LEED® AP BD+C</span></b><span style="font-size:9.0pt;color:black"><br>
Sustainable Building Analyst<br>Stantec</span></p></div><div><p class="MsoNormal"><span style="font-size:9.0pt;color:gray">1932 First Avenue Suite 307<br>Seattle WA 98101<br>Ph: <a href="tel:%28206%29%20770-7779" target="_blank">(206) 770-7779</a><br>
Fx: <a href="tel:%28206%29%20770-5941" target="_blank">(206) 770-5941</a><br><a href="mailto:Gaurav.Mehta@stantec.com" target="_blank">Gaurav.Mehta@stantec.com</a></span></p></div><div><p class="MsoNormal"><span style="font-size:13.0pt;color:blue"><a href="http://www.stantec.com" target="_blank"><b><span style="color:#993333;text-decoration:none">stantec</span></b><span style="color:#003F6E;text-decoration:none">.com</span></a> </span></p>
</div><div><p class="MsoNormal"><span style="font-size:9.0pt;color:black"> </span></p></div><div><p class="MsoNormal"><span style="font-size:9.0pt;color:black">The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.</span></p>
</div><div><p class="MsoNormal"><span style="font-size:9.0pt;color:black"> </span></p></div><p class="MsoNormal"><span style="font-size:13.5pt;font-family:Webdings;color:#008040">ü</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif";color:blue"> </span><span style="font-size:10.0pt;color:#008040">Please consider the environment before printing this email.</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif";color:blue"> </span></p>
</div><p class="MsoNormal"><span style="font-size:9.0pt;color:black"> </span><span style="font-size:10.0pt;color:blue"></span></p><div><div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in"><p class="MsoNormal">
<b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Riley Beise<br>
<b>Sent:</b> Thursday, March 24, 2011 2:12 PM<br><b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] Simplified Method Glass Conductance Entry</span></p>
</div></div><div><div></div><div class="h5"><p class="MsoNormal"> </p><p class="MsoNormal"><span lang="EN-CA">Hi all,</span></p><p class="MsoNormal"><span lang="EN-CA"> </span></p><p class="MsoNormal"><span lang="EN-CA">I’d like to be able to enter my total glazing U values in one place for simplicity.  I set my frame widths to zero and defined my window glass type in “simplified” where I entered my total window U value in the “Glass Conductance” field.  When I check my LV-D report it shows my windows having a lower U value than what I entered.  I understand there are some variables at play here that are likely the cause (air film resistance and windspeed of rating (summer vs winter as shown in the topic help).  I don’t understand what is going on here.  </span></p>
<p class="MsoNormal"><span lang="EN-CA"> </span></p><p class="MsoNormal"><span lang="EN-CA">So, </span></p><p class="MsoNormal"><span lang="EN-CA"> </span></p><p class="MsoNormal"><span lang="EN-CA">Can someone shed some light on why my LV-D window U values don’t match my “Glass Conductance” value in these circumstances?</span></p>
<p class="MsoNormal"><span lang="EN-CA"> </span></p><p class="MsoNormal"><span lang="EN-CA">And, how would you recommend I enter my windows if I have the overall U value already from product data?  </span></p><p class="MsoNormal">
<span lang="EN-CA"> </span></p><p class="MsoNormal"><span lang="EN-CA">Thanks</span></p><p class="MsoNormal"><span lang="EN-CA"> </span></p><p class="MsoNormal"><span lang="EN-CA">Riley</span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:black" lang="EN-CA"> </span></p>
<p class="MsoNormal"><span style="font-size:7.5pt;color:green" lang="EN-GB">___________________________________ </span><span style="font-size:12.0pt;font-family:"Times New Roman","serif";color:black" lang="EN-CA"></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:black" lang="EN-CA">Riley Beise, EIT, <i>LEED GA</i></span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:black" lang="EN-CA">Green Building Specialist</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif";color:black" lang="EN-CA"></span></p>
<p class="MsoNormal"><span style="color:black" lang="EN-CA"> </span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:black" lang="EN-CA">Enermodal Engineering Ltd. </span><span style="color:black" lang="EN-CA"></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:black" lang="EN-CA">602-2303 4th St. SW, Calgary AB T2S 2S7</span><span style="color:black" lang="EN-CA"><br></span><span style="font-size:10.0pt;color:black" lang="EN-CA">p. <a href="tel:403-244-0474" target="_blank">403-244-0474</a> ext. 435</span><span style="color:black" lang="EN-CA"></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:black" lang="EN-CA">f. <a href="tel:403-244-0475" target="_blank">403-244-0475</a></span><span style="color:black" lang="EN-CA"></span></p><p class="MsoNormal"><span style="font-size:10.0pt;color:black" lang="EN-CA">e. <a href="mailto:bpapau@enermodal.com" target="_blank">rbeise@enermodal.com</a></span><span style="color:black" lang="EN-CA"></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:black" lang="EN-CA"><a title="blocked::http://www.enermodal.com/
http://www.enermodal.com/
blocked::http://www.enermodal.com/"><span style="color:black">www.enermodal.com</span></a> </span><span style="color:black" lang="EN-CA"></span></p><p class="MsoNormal"><span lang="EN-CA"> </span></p></div></div></div></div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>