see attached hotel1.imp file.<br>
<br>
the file you send is in wizard mode. creating/assigning meters is much
easier in detailed mode.<br>
<br>
4 meters created: <br>
<br>
em2 = utility<br>
pmpi = submeter for pumping<br>
plhw = submeter for plant chillers<br>
flrs = submeter for the different floors.<br>
<br>
you have a master fm1 meter (fuel = gas) so the boilers/hot water
defaults to this.<br>
<br>
open the .inp file in notepad, you can "find" the meter definitions in
the electric meters section (elec-meter).<br>
just below that section is the pumps section & you'll note the chw,
hw, and cw loop pumps are assigned to elec-meter = "PMPI" <br>
<br>
open the .inp file w/equest (it will probably prompt you to save as a
new project) & stay in detailed edit mode. once in you can pick
the airside tab & open the properties for any of the equipment and
change the meter assignments. may be easier in spreadsheet view.<br>
<br>
On 3/19/11 10:24 AM, Varkie C Thomas wrote:
<blockquote cite="mid:fb15fd0424c96.4d84a080@iit.edu" type="cite">
<p>I still cannot do the metering without getting error messages.
Attached is the project (case study for the website <a
moz-do-not-send="true" href="http://bepan.info/">http://bepan.info/</a>
) description and eQ .inp & .pd2 files. I want to meter EACH</p>
<p>(1) pumping station (CHW, HW & DHW)</p>
<p>(2) plant equipment (Chillers, Boilers, DHW-heater)</p>
<p>(3) system serving floors for Mechanical, UG-parking, Lobby,
Retail, Htl-Functions, Htl-Rooms, Restaurant.</p>
<p>The project objective is to compare alternative systems (4P-FCU,
WSHP, PTAC, ) for the hotel rooms. Metering examples in the DOE22
manuals are of no help compared to the DOE21E Supplement. I will
making it work in DOE21E first</p>
<p>Varkie</p>