you can sub-meter each shell.  just be careful on how many meters you
apply to a model though.  25 meter limit max.  you can make more but
the energy & $ applied to meters in excess of the 25 limit won't
report.  typically i just create these in detailed mode by copying
& pasting in from my own set of masters.  though i should note i do
use the wizard to create the external lighting power meter so the
schedule is already setup when i transition to detailed mode.  then i
assign the external power schedules to the meters i create for external
power. <br>
<br>
look in the DOE22Vol1-Basics.pdf file you can download from the same
site as equest.  page 164 has an example that won't cut & paste
here properly so here's one i've used before.<br>
<br>
em1 = master meter<br>
em-3 & em-4 are two different buildings assigned to em1<br>
em-3- submeters are assigned to em-3<br>
em-4- submeters are assigned to em-4<br>
<br>
e-tr is the tradable exterior lighting power meter<br>
e-nt is the non-tradable exterior lighting power meter<br>
<br>
"EM1" = ELEC-METER      <br>
   TYPE             = UTILITY<br>
   BLDG/SUB-METERS  = ( "EM-3", "EM-4" )<br>
   ..<br>
"EM-3" = ELEC-METER      <br>
   TYPE             = BUILDING<br>
   SUB-METERS       = ( "EM-3-1", "EM-3-LTG", "EM-3-PRC" )<br>
   ..<br>
"EM-4" = ELEC-METER      <br>
   TYPE             = BUILDING<br>
   SUB-METERS       = ( "EM-CORE", "EM-4-1", "EM-4-LTG", "EM-4-PRC", <br>
         "EM-CORE-LTG", "EM-CORE-PRC" )<br>
   ..<br>
"EM-3-1" = ELEC-METER      <br>
   TYPE             = SUB-METER<br>
   ..<br>
"EM-3-LTG" = ELEC-METER      <br>
   TYPE             = SUB-METER<br>
   ..<br>
"EM-3-PRC" = ELEC-METER      <br>
   TYPE             = SUB-METER<br>
   ..<br>
"EM-CORE" = ELEC-METER      <br>
   TYPE             = SUB-METER<br>
   ..<br>
"EM-4-1" = ELEC-METER      <br>
   TYPE             = SUB-METER<br>
   ..<br>
"EM-4-LTG" = ELEC-METER      <br>
   TYPE             = SUB-METER<br>
   ..<br>
"EM-4-PRC" = ELEC-METER      <br>
   TYPE             = SUB-METER<br>
   ..<br>
"EM-CORE-LTG" = ELEC-METER      <br>
   TYPE             = SUB-METER<br>
   ..<br>
"EM-CORE-PRC" = ELEC-METER      <br>
   TYPE             = SUB-METER<br>
   ..<br>
"E-TR" = ELEC-METER      <br>
   TYPE             = UTILITY<br>
   EXTERIOR-POWER   = ( 5.723 )<br>
   EXTERIOR-SCH     = ( "Ext Lighting Sch" )<br>
   EXTERIOR-EU      = ( EXT-USAGE )<br>
   ..<br>
"E-NT" = ELEC-METER      <br>
   TYPE             = UTILITY<br>
   EXTERIOR-POWER   = ( 1.42 )<br>
   EXTERIOR-SCH     = ( "Ext Lighting Sch" )<br>
   EXTERIOR-EU      = ( EXT-USAGE )<br>
   ..<br>
<br>
On 3/14/11 1:30 PM, Varkie C Thomas wrote:
<blockquote cite="mid:fb0f978b253c9.4d7e3483@iit.edu" type="cite">
  <p>How do you sub-meter (electric and fuel) a System or an Equipment
in Plant?  Can you sub-meter each Shell?  Which summary report gives
the energy use per month by sub-meter?  Is there documentation on how
to do this? </p>
  <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
  </pre>
</blockquote>
<br>
</body>
</html>