<div>I personally find it tedious and confusing to change HVAC Equipment types using parametric runs. There are just too many BDL keywords that have to be manaaged when changing between different equipment types. I choose to lessen my own hassles and risk for errors and bad output data in this way:</div>
<div> </div>
<ol>
<li>I get my model file set with all the base inputs that I want to look at in both comparisons.</li>
<li>I do a "save as" of my file with all the other ECM parametrics already in them (everything but the HVAC changes.)</li>
<li>With this new copy of my file I go ahead and change the HVAC systems and equipment within the model file directly (not in the parametric runs).</li>
<li>With this newly adjusted file you have two options to work from:</li>
<ul>
<li> First you can continue working from two files for your comparison, knowing which file is representing what project case.</li>
<li>OR--you can take the newly created .inp file from the adjusted file, and go back to your originial model file and then reference this new adjusted .inp file as the .inp file for the parametric run for this ECM that is a change in chiller types. By referencing the adjusted inp. file in your parametric case you have accomplished setting up your system change as an ECM parametric with in your model file, but you avoided all the difficulty of looking up BDL key-words that you would have had to use for the parametric inputs.</li>
</ul></ol>
<div> </div>
<div>This explanation maybe a little vague, especially if you are not familiar with how to reference other .inp files into your model file. But if I were in your shoes---these are the two options I would consider and attempt to use to complete the task at hand. I hope it is helpful to you.</div>
<div> </div>
<div>Regards,</div>
<div>Pasha</div>
<div> </div>
<div class="gmail_quote">On Thu, Mar 10, 2011 at 3:13 AM, marwan farhat <span dir="ltr"><<a href="mailto:marwan.farhat01@gmail.com">marwan.farhat01@gmail.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div dir="ltr">
<div>Dear all,</div>
<div> </div>
<div>I am trying to do a parametric run for another Hvac system, changing the VAV DX to chiller with air handling units, can you please send some information or some snap shots of the program showing how it is done.</div>
<div>It is a bit confusing in the tutorial version 3.62 ( the reference of an external INP file ?!?!)</div>
<div> </div>
<div>Thank you and best regards.</div>
<div> </div><font color="#888888">
<div>Marwan Farhat</div></font></div><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>