<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman,new york,times,serif;font-size:10pt">James:<br><br>If you are modeling to 90.1-2007 Appendix G, then you need to breakout the fan energy, so you cannot set it to 0 as suggested.  See G3.1.2.1.<br><br>Paul Diglio<br><div><br></div><div style="font-family: times new roman,new york,times,serif; font-size: 10pt;"><br><div style="font-family: times new roman,new york,times,serif; font-size: 12pt;"><font face="Tahoma" size="2"><hr size="1"><b><span style="font-weight: bold;">From:</span></b> Nick Caton <ncaton@smithboucher.com><br><b><span style="font-weight: bold;">To:</span></b> Kelsey VanTassel <KVanTassel@sustaineng.com>; James Hurley <JHurley@kohlerronan.com>; equest-users@lists.onebuilding.org<br><b><span style="font-weight: bold;">Sent:</span></b> Wed, March 2, 2011 4:39:41 PM<br><b><span style="font-weight:
 bold;">Subject:</span></b> Re: [Equest-users] EER<br></font><br>



 
 

<style>
<!--
 
 _filtered {font-family:Helvetica;panose-1:2 11 6 4 2 2 2 2 2 4;}
 _filtered {font-family:"MS Mincho";panose-1:2 2 6 9 4 2 5 8 3 4;}
 _filtered {font-family:"Cambria Math";panose-1:2 4 5 3 5 4 6 3 2 4;}
 _filtered {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}
 _filtered {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;}
 _filtered {font-family:"Stylus BT";panose-1:2 14 4 2 2 2 6 2 3 4;}
 _filtered {panose-1:2 2 6 9 4 2 5 8 3 4;}
 _filtered {font-family:Futura;}
 _filtered {font-family:"Futura Bk";}
 
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:"sans-serif";}
a:link, span.MsoHyperlink
        {color:blue;text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {margin:0in;margin-bottom:.0001pt;font-size:8.0pt;font-family:"sans-serif";}
span.BalloonTextChar
        {font-family:"sans-serif";}
span.EmailStyle19
        {font-family:"sans-serif";color:#365F91;}
span.EmailStyle20
        {font-family:"sans-serif";color:#1F497D;}
span.EmailStyle21
        {font-family:"sans-serif";color:#1F497D;}
.MsoChpDefault
        {font-size:10.0pt;}
 _filtered {margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {}
-->
</style>



<div class="Section1">

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">James,</span></p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Kelsey’s right – in detailed
mode such efficiency measures entered in wizard mode get split into fan energy
(kW/CFM) and heating (EIR/HIR) & cooling (EIR) efficiencies.  If entering
values for heating/cooling efficiency – pay mind to whether fan energy is included
in your EER figures (it usually is), and follow Kelsey’s advice to zero out the
fan energy if so.  </span></p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">  </span></p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">If you’re not in detailed yet, heating
and cooling efficiencies are handled most simply using Wizard Screen 3 of ##:</span></p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><img id="Picture_x0020_2" src="cid:1.3076380719@web83305.mail.sp1.yahoo.com" width="720" height="511"></span><span style="color: rgb(31, 73, 125);"></span></p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">  </span></p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">~Nick</span></p> 

<div>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><img id="_x0000_i1026" src="cid:2.3076380720@web83305.mail.sp1.yahoo.com" alt="cid:489575314@22072009-0ABB" width="119" height="37"></span><b><span style="font-family: "sans-serif"; color: rgb(45, 77, 94);"></span></b></p> 

<p class="MsoNormal"><b><span style="font-family: "sans-serif"; color: rgb(45, 77, 94);">  </span></b></p> 

<p class="MsoNormal"><b><span style="font-family: "sans-serif"; color: rgb(45, 77, 94);">NICK CATON, E.I.T.</span></b><b><span style="font-size: 12pt; font-family: "sans-serif"; color: rgb(45, 77, 94);"></span></b></p> 

<p class="MsoNormal"><span style="font-size: 7.5pt; color: rgb(204, 153, 0);">PROJECT ENGINEER</span></p> 

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">Smith &
Boucher Engineers</span><span style="font-size: 7.5pt; font-family: "serif"; color: rgb(204, 153, 0);"></span></p> 

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">25501 west
valley parkway</span></p> 

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">olathe ks 66061</span></p> 

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">direct 913
344.0036</span></p> 

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">fax 913
345.0617</span></p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><a rel="nofollow" title="blocked::www.smithboucher.com"><span style="font-size: 10pt;">www.smithboucher.com</span></a></span><u><span style="font-size: 10pt; color: blue;"> </span></u><span style="color: rgb(31, 73, 125);"></span></p> 

</div>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">  </span></p> 

<div>

<div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">

<p class="MsoNormal"><b><span style="font-size: 10pt; font-family: "sans-serif";">From:</span></b><span style="font-size: 10pt; font-family: "sans-serif";">
equest-users-bounces@lists.onebuilding.org
[mailto:equest-users-bounces@lists.onebuilding.org] <b>On Behalf Of </b>Kelsey
VanTassel<br>
<b>Sent:</b> Wednesday, March 02, 2011 3:28 PM<br>
<b>To:</b> James Hurley; equest-users@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Equest-users] EER</span></p> 

</div>

</div>

<p class="MsoNormal">  </p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">You assign the cooling EIR
(inverse of COP) under system>cooling>unitary power. Technically, you
should define the efficiency of the compressor separately from the fan power,
otherwise eQUEST will double-count the fan energy. If you use an overall system
EER, then you should set the fan power (kW/cfm) to zero.</span></p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">  </span></p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Furnace efficiency (heat input
ratio) is specified under system>heating>unitary power.</span></p> 

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">  </span></p> 

<div>

<p class="MsoNormal"><b><span style="font-size: 10pt; font-family: "sans-serif"; color: black;">Kelsey Van Tassel</span></b><b><span style="font-size: 12pt; font-family: "serif"; color: rgb(0, 0, 102);"></span></b></p> 

<p class="MsoNormal"><span style="font-size: 10pt; font-family: "sans-serif"; color: black;">Mechanical Engineer | <a rel="nofollow" ymailto="mailto:kvantassel@sustaineng.com" target="_blank" href="mailto:kvantassel@sustaineng.com">kvantassel@sustaineng.com</a></span><span style="font-size: 12pt; font-family: "serif"; color: rgb(0, 0, 102);"></span></p> 

<p class="MsoNormal"><span style="font-size: 10pt; font-family: "sans-serif"; color: black;">608.836.4488 ext. 20 | Fax: 608.836.4477</span></p> 

<p class="MsoNormal"><span style="font-size: 12pt; font-family: "serif"; color: rgb(0, 0, 102);">  </span></p> 

<p class="MsoNormal"><span style="font-size: 10pt; font-family: "sans-serif"; color: black;">Sustainable Engineering Group</span><span style="font-size: 12pt; font-family: "serif"; color: rgb(0, 0, 102);"></span></p> 

<p class="MsoNormal"><span style="font-size: 10pt; font-family: "sans-serif"; color: black;">901 Deming Way, Suite 201</span></p> 

<p class="MsoNormal"><span style="font-size: 10pt; font-family: "sans-serif"; color: black;">Madison, WI 53717</span></p> 

<p class="MsoNormal"><span style="font-size: 10pt; font-family: "sans-serif"; color: black;"><a rel="nofollow" target="_blank" href="http://www.sustaineng.com/">www.sustaineng.com</a></span></p> 

<p class="MsoNormal"><span style="font-size: 12pt; font-family: "serif"; color: black;"> </span><span style="font-size: 12pt; font-family: "serif"; color: rgb(0, 0, 102);"></span></p> 

</div>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">  </span></p> 

<div>

<div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">

<p class="MsoNormal"><b><span style="font-size: 10pt; font-family: "sans-serif";">From:</span></b><span style="font-size: 10pt; font-family: "sans-serif";">
equest-users-bounces@lists.onebuilding.org
[mailto:equest-users-bounces@lists.onebuilding.org] <b>On Behalf Of </b>James
Hurley<br>
<b>Sent:</b> Wednesday, March 02, 2011 3:07 PM<br>
<b>To:</b> equest-users@lists.onebuilding.org<br>
<b>Subject:</b> [Equest-users] EER</span></p> 

</div>

</div>

<p class="MsoNormal">  </p> 

<p class="MsoNormal"><span style="color: rgb(54, 95, 145);">  </span></p> 

<p class="MsoNormal"><span style="color: rgb(54, 95, 145);">  </span></p> 

<p class="MsoNormal"><span style="color: rgb(54, 95, 145);">Where in eQuest can you assign
an EER of a DX coil or the Efficiency of a furnace?</span></p> 

<p class="MsoNormal"><span style="color: rgb(54, 95, 145);">  </span></p> 

<p class="MsoNormal"><span style="color: rgb(54, 95, 145);">  </span></p> 

<p class="MsoNormal"><span style="color: rgb(54, 95, 145);">  </span></p> 

<p class="MsoNormal"><span style="color: rgb(54, 95, 145);">  </span></p> 

<p class="MsoNormal"><span style="color: rgb(54, 95, 145);">  </span></p> 

<p class="MsoNormal"><span style="color: black;"><img id="Picture_x0020_1" src="cid:3.3076380720@web83305.mail.sp1.yahoo.com" alt="cid:image001.png@01CA94FC.558724B0" border="0" width="131" height="135"></span></p> 

<p class="MsoNormal"><span style="font-size: 8.5pt; font-family: "Futura Bk"; color: black;">  </span></p> 

<p class="MsoNormal"><span style="font-size: 8.5pt; font-family: "Futura Bk"; color: black;">  </span></p> 

<p class="MsoNormal"><b><span style="font-size: 9pt; font-family: Futura; color: rgb(94, 136, 161);">JAMES HURLEY</span></b><span style="font-size: 9pt; font-family: "sans-serif"; color: black;"></span></p> 

<p class="MsoNormal"><span style="font-size: 8.5pt; font-family: Futura; color: rgb(64, 64, 64);">Kohler
Ronan, LLC | </span><span style="color: black;"><a rel="nofollow" target="_blank" href="http://www.kohlerronan.com"><span style="font-size: 8.5pt;">www.kohlerronan.com</span></a></span><span style="font-size: 9pt; font-family: "sans-serif"; color: black;"></span></p> 

<p class="MsoNormal"><span style="font-size: 9pt; color: black;"><a rel="nofollow" ymailto="mailto:jhurley@kohlerronan.com" target="_blank" href="mailto:jhurley@kohlerronan.com">j<span style="font-size: 8pt;">hurley@kohlerronan.com</span></a></span></p> 

<p class="MsoNormal"><span style="font-size: 9pt; color: black;">  </span></p> 

<p class="MsoNormal"><span style="font-size: 8.5pt; font-family: Futura; color: rgb(64, 64, 64);">1370
Broadway, New York, NY 10018</span><span style="font-size: 9pt; font-family: "sans-serif"; color: black;"></span></p> 

<p class="MsoNormal"><span style="font-size: 8.5pt; font-family: Futura; color: rgb(64, 64, 64);">212.695.2422
 F 212.695.2423</span><span style="font-size: 9pt; font-family: "sans-serif"; color: black;"></span></p> 

<p class="MsoNormal"><span style="font-size: 9pt; font-family: "sans-serif"; color: black;">  </span></p> 

<p class="MsoNormal"><span style="font-size: 8.5pt; font-family: Futura; color: rgb(64, 64, 64);">301
Main Street, Danbury, CT 06810</span><span style="font-size: 9pt; font-family: "sans-serif"; color: black;"></span></p> 

<p class="MsoNormal"><span style="font-size: 8.5pt; font-family: Futura; color: rgb(64, 64, 64);">203.778.1017
 F 203.778.1018</span><span style="font-size: 9pt; font-family: "sans-serif"; color: black;"></span></p> 

<p class="MsoNormal"><span style="font-size: 9pt; font-family: "sans-serif"; color: black;">  </span></p> 

<p class="MsoNormal"><span style="font-size: 8.5pt; font-family: Futura; color: rgb(64, 64, 64);">Please
consider the environment before printing this e-mail.</span><span style="font-size: 9pt; font-family: "sans-serif"; color: black;"></span></p> 

<p class="MsoNormal">  </p> 

</div>

</div></div>
</div></body></html>