Hi eQuester:<br><br>I know eQuest is qualified software for calculating Commercial Building Tax  Deductions.  eQuest use a standard Title 24. Tax  Deductions is based on ASHARE 90.1 for commercial buildings.<br><br>My question is how to compare a baseline model (actual situation) to ASHARE 90.1 in the eQuest?<br>
<br>Any suggestion and guidance are welcomed.<br><br>Yingqi Chen<br><br>The PERTAN GROUP<br>44 E. Main St.<br>Champaign ,IL 61820<br><br><br><div class="gmail_quote">On Tue, Feb 8, 2011 at 2:02 PM,  <span dir="ltr"><<a href="mailto:equest-users-request@lists.onebuilding.org">equest-users-request@lists.onebuilding.org</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">Send Equest-users mailing list submissions to<br>
        <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
<br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:equest-users-request@lists.onebuilding.org">equest-users-request@lists.onebuilding.org</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:equest-users-owner@lists.onebuilding.org">equest-users-owner@lists.onebuilding.org</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of Equest-users digest..."<br>
<br>
<br>
Today's Topics:<br>
<br>
   1. Parametric Run -Lighting Upgrade (pranita kothuru)<br>
   2. Re: HVAC System Lockout (Jeffrey Mancuso)<br>
   3. Re: Parametric Run -Lighting Upgrade (Jeremy McClanathan)<br>
   4. Re: Storefront and Curtainwall (Peter Hillermann)<br>
   5. Re: Storefront and Curtainwall (Peter Hillermann)<br>
   6. Radiant Heating and Cooling? (Ju-Yeon Julie Shin)<br>
   7. Re: Radiant Heating and Cooling? (Pasha Korber-Gonzalez)<br>
   8. Re: Radiant Heating and Cooling? (Arpan Bakshi)<br>
   9. Heating and Cooling Schedules (Cory Duggin)<br>
  10. Re: Heating and Cooling Schedules (John Aulbach)<br>
  11. Re: Heating and Cooling Schedules (Cory Duggin)<br>
  12. Re: Modeling Multstack Units in eQUEST (Steven Savich)<br>
  13. Re: Modeling Multstack Units in eQUEST (Dana Troy)<br>
  14. Re: Modeling Multstack Units in eQUEST (Nick Caton)<br>
  15. Re: Modeling Multistack Units in eQUEST (Bishop, Bill)<br>
<br>
<br>
----------------------------------------------------------------------<br>
<br>
Message: 1<br>
Date: Mon, 7 Feb 2011 15:08:33 -0500<br>
From: pranita kothuru <<a href="mailto:pranita.kothuru@gmail.com">pranita.kothuru@gmail.com</a>><br>
To: equest-users <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>
Subject: [Equest-users] Parametric Run -Lighting Upgrade<br>
Message-ID:<br>
        <AANLkTi=oG5PZ7osVJVy5LeqQ4CL_JwxenXUbVwZN=<a href="mailto:HyA@mail.gmail.com">HyA@mail.gmail.com</a>><br>
Content-Type: text/plain; charset="iso-8859-1"<br>
<br>
Hello All -<br>
<br>
I am trying to use the global parameters feature for the first time and<br>
simulate the upgrade in my lighting. I have the new watts/sqft number and<br>
was able to create the global parameter.<br>
<br>
I hit a brick wall at this point. What are the next steps  to ensure that my<br>
run captures this new wattage.<br>
<br>
Thanks!<br>
<br>
--<br>
<br>
*- Pranita *<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/199526ed/attachment.html" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/199526ed/attachment.html</a>><br>

<br>
------------------------------<br>
<br>
Message: 2<br>
Date: Mon, 7 Feb 2011 16:34:51 -0500<br>
From: "Jeffrey Mancuso" <<a href="mailto:jmancuso@aecpersonnelconsultants.com">jmancuso@aecpersonnelconsultants.com</a>><br>
To: "'Arpan Bakshi'" <<a href="mailto:arpanbakshi@gmail.com">arpanbakshi@gmail.com</a>>,   "'Cory Duggin'"<br>
        <<a href="mailto:crduggin@gmail.com">crduggin@gmail.com</a>><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] HVAC System Lockout<br>
Message-ID: <017401cbc70e$dae966f0$90bc34d0$@com><br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
Dear eQUEST community:<br>
<br>
<br>
<br>
Each month, we reach out to everyone to let them know about our featured<br>
position.   Our client is one of the premier energy consulting firms in NYC,<br>
and they are actively looking for an eQUEST Modeling Manager.  The position<br>
is still hands on, but also will focus on the management and direction of<br>
junior level personnel and to act as a mentor.  The requirements are a<br>
minimum of 5 years of experience with a strong background in the use of<br>
eQUEST.  They are involved in a diverse portfolio of work including<br>
healthcare, higher education, high rise, and various institutions.  Our<br>
client is considered one of the experts in the industry, and are even hired<br>
by other firms for complex projects which they are not equipped to handle.<br>
They are prepared to offer salaries that will easily exceed $100,000 for the<br>
right individual.  For an opportunity to discuss the position in more<br>
detail, please reply by email, or contact me on the numbers listed below.<br>
<br>
<br>
<br>
<br>
Regards,<br>
<br>
<br>
<br>
<br>
<br>
Jeffrey Mancuso<br>
<br>
(609) 893-6655 direct<br>
<br>
(267) 738-2052 cell<br>
<br>
<br>
<br>
From: <a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a><br>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>] On Behalf Of Arpan<br>
Bakshi<br>
Sent: Friday, February 04, 2011 4:50 PM<br>
To: Cory Duggin<br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] HVAC System Lockout<br>
<br>
<br>
<br>
Cory, I would recommend a test run, detaching all schedules, just to let the<br>
auto-size engine do its work; you should see comparable loads. I find<br>
uncoordinated schedules can cause all kinds of ruckus.<br>
<br>
On Fri, Feb 4, 2011 at 4:43 PM, Cory Duggin <<a href="mailto:crduggin@gmail.com">crduggin@gmail.com</a>> wrote:<br>
<br>
Based on what you have said, I think I just need a new heating and cooling<br>
schedule.  I found them in my component tree, but I am not sure how to do<br>
what I want because the annual schedule only specifies an ending month and<br>
day.  How do I know when that schedule starts?<br>
<br>
<br>
<br>
On Thu, Feb 3, 2011 at 9:24 PM, Nick Caton <<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>> wrote:<br>
<br>
Whoah buddy =)!<br>
<br>
<br>
<br>
First, let me give the preface that I'll be passing the 70hr mark for this<br>
workweek tonight, so I'm kind of in zombie-mode right now XD!<br>
<br>
<br>
<br>
Okay, I reckon you're hunting rabbits with a  bazooka by resorting to an<br>
absorption chiller/boiler setup to approximate your gas furnace!  I'd go<br>
ahead and save your work in a separate file for reference, then I'd step<br>
back to the wizards to try a packaged single-zone furnace with DX cooling<br>
for your 2-story zone, and a single-zone heatpump (DX/DX) for your garage.<br>
Make the systems "on" 24hrs with intermittent fan operation, and be sure<br>
you're not specifying "system per zone."  Use the shell wizard to be sure<br>
the zones are assigned to the right system.<br>
<br>
<br>
<br>
If you wish, you can restrict heating and cooling availability for each<br>
system, the way a residential thermostat has "heating" and "cooling" modes,<br>
with a COOLING-SCHEDULE and HEATING-SCHEDULE.  By default, heating and<br>
cooling are generally available whenever they're called for, but you can<br>
edit that without going to a chiller/boiler system ;).<br>
<br>
<br>
<br>
If you are finding your building is flip-flopping between heating and<br>
cooling hour-to-hour in the dead of summer, it might be a sign other items<br>
are off. check your envelope constructions/layers, and note that<br>
oversimplifying geometries/spaces (i.e. - one per floor) may result in a lot<br>
of thermal mass from partitions being excluded that would otherwise be a<br>
stabilizing presence.<br>
<br>
<br>
<br>
I'm copying the eQuest list, because I will be of little use to you others<br>
in the next 24 hours.  Our strength is in numbers, so do keep everyone in<br>
the loop as you work through this and you'll get the best chance of quality<br>
assistance - best of luck =)!<br>
<br>
<br>
<br>
Back to the grindstone.<br>
<br>
~Nick<br>
<br>
<br>
<br>
Error! Filename not specified.<br>
<br>
<br>
<br>
NICK CATON, E.I.T.<br>
<br>
PROJECT ENGINEER<br>
<br>
Smith & Boucher Engineers<br>
<br>
25501 west valley parkway<br>
<br>
olathe ks 66061<br>
<br>
direct 913 344.0036<br>
<br>
fax 913 345.0617<br>
<br>
 <<a href="http://www.smithboucher.com/" target="_blank">http://www.smithboucher.com/</a>> <a href="http://www.smithboucher.com" target="_blank">www.smithboucher.com</a><br>
<br>
<br>
<br>
From: Cory Duggin [mailto:<a href="mailto:crduggin@gmail.com">crduggin@gmail.com</a>]<br>
Sent: Thursday, February 03, 2011 1:23 PM<br>
To: Nick Caton<br>
Subject: Re: [Equest-users] HVAC System Lockout<br>
<br>
<br>
<br>
I am modeling a two story house with a one story garage that has been<br>
converted into a conditioned space.  It is setup so there are 3 zones.  One<br>
in each floor of the two story part and then the garage.  The real system in<br>
the house is one unit for the two story part that has gas heat, and the<br>
garage has its own small heat pump unit.  Since most people don't flip their<br>
thermostat back and forth between heat and cool, I don't want my systems<br>
suddenly switching to heat for an hour in the middle of summer because one<br>
of the zones got below set point.  I have now changed the system to a<br>
chilled water loop and a hot water loop.  Where the hot water is provided by<br>
a natural draft boiler and the chilled water is provided by a single effect<br>
absorption chiller.  I am trying to create a loads file that will have the<br>
load on the chiller rather than the load on each coil for each zone and also<br>
the heating load for all the zones, but I don't want it to be able to change<br>
from cooling to heating in the cooling season or vice versa.  Does that<br>
makes sense?  Thanks<br>
<br>
On Thu, Feb 3, 2011 at 11:19 AM, Nick Caton <<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>> wrote:<br>
<br>
Cory, your query needs more description to include what you're trying to<br>
model and what you've input, but if you've got simultaneous calls for<br>
heating and cooling being handled, it sounds like you have either a<br>
multi-zone system or multiple systems specified where you want only (1)<br>
single-zone system.<br>
<br>
<br>
<br>
If I were trying to model the behavior of the HVAC in my apartment<br>
accurately (a simple CV electric furnace with DX cooling controlled by a<br>
single remote thermostat), I'd group all conditioned spaces and their zones<br>
under a single system, taking care to assign the thermostat zone where the<br>
thermostat actually resides - it's the zone highlighted red in the graphic<br>
under the airside HVAC tab.<br>
<br>
<br>
<br>
I'd suggest revisiting the quantity and type of system you've specified<br>
first, and modify/reassign your systems/zones as necessary to see if that's<br>
where the problem resides.  If you're still having troubles, you'll need to<br>
provide a better description of what sort of system you're trying to model<br>
(layman's terms are fine in this forum) and what you've tried to specify on<br>
the model side.  Attaching your project's .inp/.pd2 files may encourage<br>
others to help troubleshoot also ;).<br>
<br>
<br>
<br>
Best of luck!<br>
<br>
<br>
<br>
~Nick<br>
<br>
<br>
<br>
Error! Filename not specified.<br>
<br>
<br>
<br>
NICK CATON, E.I.T.<br>
<br>
PROJECT ENGINEER<br>
<br>
Smith & Boucher Engineers<br>
<br>
25501 west valley parkway<br>
<br>
olathe ks 66061<br>
<br>
direct 913 344.0036<br>
<br>
fax 913 345.0617<br>
<br>
 <<a href="http://www.smithboucher.com/" target="_blank">http://www.smithboucher.com/</a>> <a href="http://www.smithboucher.com" target="_blank">www.smithboucher.com</a><br>
<br>
<br>
<br>
From: <a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a><br>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>] On Behalf Of Cory Duggin<br>
Sent: Wednesday, February 02, 2011 4:07 PM<br>
To: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: [Equest-users] HVAC System Lockout<br>
<br>
<br>
<br>
Is there a way I can create a schedule to lockout either the heating or<br>
cooling system based on the time of year?  I am modeling a residential<br>
system, so I don't want it to try and satisfy heating a cooling loads<br>
simultaneously in different zones.  Thanks<br>
<br>
--<br>
Cory Duggin, EI<br>
Tennessee Tech University<br>
Graduate Research Assistant<br>
Mechanical Engineering<br>
<br>
<br>
<br>
<br>
--<br>
Cory Duggin, EI<br>
Tennessee Tech University<br>
Graduate Research Assistant<br>
Mechanical Engineering<br>
<br>
<br>
<br>
<br>
--<br>
Cory Duggin, EI<br>
Tennessee Tech University<br>
Graduate Research Assistant<br>
Mechanical Engineering<br>
<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to<br>
<a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br>
<br>
<br>
<br>
--<br>
<br>
<br>
<br>
Arpan Bakshi<br>
<br>
646 704-2880<br>
<br>
<br>
<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/5518f048/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/5518f048/attachment-0001.htm</a>><br>

<br>
------------------------------<br>
<br>
Message: 3<br>
Date: Mon, 7 Feb 2011 13:39:16 -0800<br>
From: Jeremy McClanathan <jmcclanathan@CDiengineers.com><br>
To: 'pranita kothuru' <<a href="mailto:pranita.kothuru@gmail.com">pranita.kothuru@gmail.com</a>>, 'equest-users'<br>
        <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>
Subject: Re: [Equest-users] Parametric Run -Lighting Upgrade<br>
Message-ID:<br>
        <<a href="mailto:C066A738E8E11C4B8115F8D3E5F5FE062938F6FAEE@eldorado.cdiengineers.com">C066A738E8E11C4B8115F8D3E5F5FE062938F6FAEE@eldorado.cdiengineers.com</a>><br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
To assign the parameter:<br>
-right click on the input box you would like to assign the parameter to<br>
-choose Edit/View User Expression<br>
-Type    Parameter("Name of Global Parameter")   Note: The global parameter name is case sensitive.<br>
<br>
To use with a parametric run:<br>
-Create a parametric run<br>
-Create a new component and choose Global Parameter from component type drop down menu<br>
-change the value of the global parameter<br>
-run your model<br>
<br>
Using global parameters for schedules is a bit more tricky.  See the following post for using global parameters for schedules:<br>
<a href="http://www.esimforums.com/equest/viewtopic.php?f=70&t=108" target="_blank">http://www.esimforums.com/equest/viewtopic.php?f=70&t=108</a><br>
<br>
<br>
Jeremy<br>
<br>
___________________________________________<br>
Jeremy McClanathan, LEED(r) AP BD+C<br>
[cid:image001.jpg@01CBC6CA.C0A121F0]<br>
4200 194th St SW, Ste 200, Lynnwood, WA 98036<br>
P 425-672-1071 | F 425-778-8769<br>
P Please consider the environment before printing this email.<br>
<br>
From: pranita kothuru [mailto:<a href="mailto:pranita.kothuru@gmail.com">pranita.kothuru@gmail.com</a>]<br>
Sent: Monday, February 07, 2011 12:09 PM<br>
To: equest-users<br>
Subject: [Equest-users] Parametric Run -Lighting Upgrade<br>
<br>
Hello All -<br>
<br>
I am trying to use the global parameters feature for the first time and simulate the upgrade in my lighting. I have the new watts/sqft number and was able to create the global parameter.<br>
<br>
I hit a brick wall at this point. What are the next steps  to ensure that my run captures this new wattage.<br>
<br>
Thanks!<br>
<br>
--<br>
<br>
- Pranita<br>
<br>
<br>
This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws.  If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments.  If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies.<br>

-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/4bcdcec6/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/4bcdcec6/attachment-0001.htm</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: image001.jpg<br>
Type: image/jpeg<br>
Size: 1232 bytes<br>
Desc: image001.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/4bcdcec6/image001-0001.jpg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/4bcdcec6/image001-0001.jpg</a>><br>

<br>
------------------------------<br>
<br>
Message: 4<br>
Date: Mon, 7 Feb 2011 16:42:44 -0500<br>
From: "Peter Hillermann" <<a href="mailto:peterh@westallarchitects.com">peterh@westallarchitects.com</a>><br>
To: <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>>,<br>
        <<a href="mailto:eQUEST-users@onebuilding.org">eQUEST-users@onebuilding.org</a>><br>
Subject: Re: [Equest-users] Storefront and Curtainwall<br>
Message-ID:<br>
        <!&!AAAAAAAAAAAYAAAAAAAAAODey+9ZUTBBibNK3rV4Pv/CgAAAEAAAALx8s3y2obhDiVMO6+XzTZUBAAAAAA==@<a href="http://westallarchitects.com" target="_blank">westallarchitects.com</a>><br>
<br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
To All,<br>
<br>
<br>
<br>
I'm about to answer my own question. The ASTM E283 is the maximum allowable<br>
air infiltration for a weather tight system. The 0.06 CFM is a not to exceed<br>
number. What the vendor will typically write is follow ASTM E283 to make<br>
sure the system does not exceed 0.06 CFM of air infiltration. Its testing<br>
pressure differences across the building envelope.<br>
<br>
<br>
<br>
So the answer to my own question is 0.06 CFM is fine.<br>
<br>
<br>
<br>
Thanks,<br>
<br>
<br>
<br>
PETER HILLERMANN<br>
<br>
<br>
<br>
<a href="mailto:peterh@westallarchitects.com">peterh@westallarchitects.com</a><br>
<br>
<br>
<br>
westall<br>
<br>
architects<br>
<br>
3404 pierce drive<br>
<br>
chamblee, georgia 30341<br>
<br>
<br>
<br>
o 770.458.4113<br>
<br>
f  770.458.5352<br>
<br>
c 678.898.2936<br>
<br>
<br>
<br>
<a href="http://westallarchitects.com" target="_blank">westallarchitects.com</a><br>
<br>
Description: e-signatureDescription: USGBC-Logo<br>
<br>
<br>
<br>
From: <a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a><br>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>] On Behalf Of Peter<br>
Hillermann<br>
Sent: Monday, February 07, 2011 10:53 AM<br>
To: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>; <a href="mailto:eQUEST-users@onebuilding.org">eQUEST-users@onebuilding.org</a><br>
Subject: [Equest-users] Storefront and Curtainwall<br>
<br>
<br>
<br>
To All,<br>
<br>
<br>
<br>
Does anyone know what a good number of CFM is for air leakage in storefront<br>
and curtainwall systems. At the moment I am being told 0.06CFM and as an<br>
uneducated window system person I have no idea if that is appropriate. This<br>
is tested against a ASTM E 283 at a test pressure of 6.24 psf, which for me<br>
might as well have been written TYDOISJLAKHJSDMNKAPOD.<br>
<br>
<br>
<br>
Thanks,<br>
<br>
<br>
<br>
PETER HILLERMANN<br>
<br>
<br>
<br>
<a href="mailto:peterh@westallarchitects.com">peterh@westallarchitects.com</a><br>
<br>
<br>
<br>
westall<br>
<br>
architects<br>
<br>
3404 pierce drive<br>
<br>
chamblee, georgia 30341<br>
<br>
<br>
<br>
o 770.458.4113<br>
<br>
f  770.458.5352<br>
<br>
c 678.898.2936<br>
<br>
<br>
<br>
<a href="http://westallarchitects.com" target="_blank">westallarchitects.com</a><br>
<br>
Description: e-signatureDescription: USGBC-Logo<br>
<br>
<br>
<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0002.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0002.htm</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/gif<br>
Size: 2436 bytes<br>
Desc: not available<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0002.gif" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0002.gif</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 3222 bytes<br>
Desc: not available<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0004.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0004.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 3222 bytes<br>
Desc: not available<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0005.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0005.jpeg</a>><br>

<br>
------------------------------<br>
<br>
Message: 5<br>
Date: Mon, 7 Feb 2011 16:42:44 -0500<br>
From: "Peter Hillermann" <<a href="mailto:peterh@westallarchitects.com">peterh@westallarchitects.com</a>><br>
To: <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>>,<br>
        <<a href="mailto:eQUEST-users@onebuilding.org">eQUEST-users@onebuilding.org</a>><br>
Subject: Re: [Equest-users] Storefront and Curtainwall<br>
Message-ID:<br>
        <!&!AAAAAAAAAAAYAAAAAAAAAODey+9ZUTBBibNK3rV4Pv/CgAAAEAAAALx8s3y2obhDiVMO6+XzTZUBAAAAAA==@<a href="http://westallarchitects.com" target="_blank">westallarchitects.com</a>><br>
<br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
To All,<br>
<br>
<br>
<br>
I'm about to answer my own question. The ASTM E283 is the maximum allowable<br>
air infiltration for a weather tight system. The 0.06 CFM is a not to exceed<br>
number. What the vendor will typically write is follow ASTM E283 to make<br>
sure the system does not exceed 0.06 CFM of air infiltration. Its testing<br>
pressure differences across the building envelope.<br>
<br>
<br>
<br>
So the answer to my own question is 0.06 CFM is fine.<br>
<br>
<br>
<br>
Thanks,<br>
<br>
<br>
<br>
PETER HILLERMANN<br>
<br>
<br>
<br>
<a href="mailto:peterh@westallarchitects.com">peterh@westallarchitects.com</a><br>
<br>
<br>
<br>
westall<br>
<br>
architects<br>
<br>
3404 pierce drive<br>
<br>
chamblee, georgia 30341<br>
<br>
<br>
<br>
o 770.458.4113<br>
<br>
f  770.458.5352<br>
<br>
c 678.898.2936<br>
<br>
<br>
<br>
<a href="http://westallarchitects.com" target="_blank">westallarchitects.com</a><br>
<br>
Description: e-signatureDescription: USGBC-Logo<br>
<br>
<br>
<br>
From: <a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a><br>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>] On Behalf Of Peter<br>
Hillermann<br>
Sent: Monday, February 07, 2011 10:53 AM<br>
To: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>; <a href="mailto:eQUEST-users@onebuilding.org">eQUEST-users@onebuilding.org</a><br>
Subject: [Equest-users] Storefront and Curtainwall<br>
<br>
<br>
<br>
To All,<br>
<br>
<br>
<br>
Does anyone know what a good number of CFM is for air leakage in storefront<br>
and curtainwall systems. At the moment I am being told 0.06CFM and as an<br>
uneducated window system person I have no idea if that is appropriate. This<br>
is tested against a ASTM E 283 at a test pressure of 6.24 psf, which for me<br>
might as well have been written TYDOISJLAKHJSDMNKAPOD.<br>
<br>
<br>
<br>
Thanks,<br>
<br>
<br>
<br>
PETER HILLERMANN<br>
<br>
<br>
<br>
<a href="mailto:peterh@westallarchitects.com">peterh@westallarchitects.com</a><br>
<br>
<br>
<br>
westall<br>
<br>
architects<br>
<br>
3404 pierce drive<br>
<br>
chamblee, georgia 30341<br>
<br>
<br>
<br>
o 770.458.4113<br>
<br>
f  770.458.5352<br>
<br>
c 678.898.2936<br>
<br>
<br>
<br>
<a href="http://westallarchitects.com" target="_blank">westallarchitects.com</a><br>
<br>
Description: e-signatureDescription: USGBC-Logo<br>
<br>
<br>
<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0003.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0003.htm</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/gif<br>
Size: 2436 bytes<br>
Desc: not available<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0003.gif" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0003.gif</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 3222 bytes<br>
Desc: not available<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0006.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0006.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 3222 bytes<br>
Desc: not available<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0007.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110207/b14e489e/attachment-0007.jpeg</a>><br>

<br>
------------------------------<br>
<br>
Message: 6<br>
Date: Tue, 8 Feb 2011 20:40:36 +0900<br>
From: Ju-Yeon Julie Shin <<a href="mailto:juyeon519@hotmail.com">juyeon519@hotmail.com</a>><br>
To: <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>
Subject: [Equest-users] Radiant Heating and Cooling?<br>
Message-ID: <SNT123-W63FD33B233CE0F09F286DCF0EA0@phx.gbl><br>
Content-Type: text/plain; charset="ks_c_5601-1987"<br>
<br>
<br>
Hello everyone, this is Julie Shin.<br>
<br>
1. I am curious whether it is possible to add "radiant heating and cooling" for eQUEST simulations or not.<br>
If it is possible, could anyone please let me know how to do so?<br>
<br>
2. Is it also possible to add vertical louvers? I have tried adding horizontal louvers, but not the vertical ones.<br>
<br>
Thank you everyone and have a nice day.<br>
<br>
Julie Shin.<br>
<br>
<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/b29618b5/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/b29618b5/attachment-0001.htm</a>><br>

<br>
------------------------------<br>
<br>
Message: 7<br>
Date: Tue, 8 Feb 2011 09:26:01 -0700<br>
From: Pasha Korber-Gonzalez <<a href="mailto:pasha.pkconsulting@gmail.com">pasha.pkconsulting@gmail.com</a>><br>
To: Ju-Yeon Julie Shin <<a href="mailto:juyeon519@hotmail.com">juyeon519@hotmail.com</a>><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Radiant Heating and Cooling?<br>
Message-ID:<br>
        <AANLkTine6swraj0nN=<a href="mailto:dEVPQ3twMVYcK4oNpx%2BnKSOA4N@mail.gmail.com">dEVPQ3twMVYcK4oNpx+nKSOA4N@mail.gmail.com</a>><br>
Content-Type: text/plain; charset="iso-8859-1"<br>
<br>
Hi Julie,<br>
<br>
<br>
   1. You can "represent" radiant ht & clg in eQuest, by modifying a system<br>
   to *act* like a radiant system, however be mindful that because DOE2<br>
   can't do this explicitly there will be some discrepancies from real life,<br>
   but it still can be a fairly realistic representation and measurment of the<br>
   system performance.  To do this you will want to choose a Fan Coil system<br>
   for your HVAC type and turn down your fan power in the FC units to zero.<br>
   You will also want to probably use a DOAS & Dummy Zone approach for your<br>
   ventilation systems.  This is an approach to use in eQuest.   I can send you<br>
   an example file of a Dummy zone for you to look through and learn from.  You<br>
   will also want to read about the FC system in another DOE2 document I will<br>
   also send you (off list).  Once you understand how DOE2 represent a Fan Coil<br>
   system, then you will understand how you can change it to better act like a<br>
   radiant system.   Others might consider using the PIU system in eQuest, but<br>
   I have found by my experience that PIU's are better for representing Active<br>
   Chilled Beam systems, and Fan Coils are better to represent radiant only<br>
   systems.  I'm happy to share more of my sim experience with radiant systems,<br>
   but I'm also curious to hear other's simulators experiences<br>
   with representing radiant systems in eQuest too.<br>
   2. When you say "louvers" I'm assuming you are referencing external<br>
   shading devices.  Yes you can input vertical exterior shades on the outside<br>
   of your building by using the Building Shade inputs.  This can only be done<br>
   in DDedit mode, and the inputs are based on your XYZ coordinates of the<br>
   building space. I will send you a 3rd document (Modeling Procedures Quck Ref<br>
   Guide) and you can learn how to input these shades in Chapter 8 of the<br>
   document.<br>
<br>
Feel free to write back to the list or to me if you have more questions.<br>
You will find lots of great simulators who are always more than willing to<br>
share thier experiences with new users.<br>
<br>
Hope this helps,<br>
Pasha<br>
<br>
Korber Energy Consultants<br>
<a href="http://www.korberenergy.com" target="_blank">www.korberenergy.com</a><br>
<br>
2011/2/8 Ju-Yeon Julie Shin <<a href="mailto:juyeon519@hotmail.com">juyeon519@hotmail.com</a>><br>
<br>
> Hello everyone, this is Julie Shin.<br>
><br>
> 1. I am curious whether it is possible to add "radiant heating and cooling"<br>
> for eQUEST simulations or not.<br>
> If it is possible, could anyone please let me know how to do so?<br>
><br>
> 2. Is it also possible to add vertical louvers? I have tried adding<br>
> horizontal louvers, but not the vertical ones.<br>
><br>
> Thank you everyone and have a nice day.<br>
><br>
> Julie Shin.<br>
><br>
><br>
><br>
> _______________________________________________<br>
> Equest-users mailing list<br>
> <a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
> To unsubscribe from this mailing list send  a blank message to<br>
> <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
><br>
><br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/d6637387/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/d6637387/attachment-0001.htm</a>><br>

<br>
------------------------------<br>
<br>
Message: 8<br>
Date: Tue, 8 Feb 2011 11:41:23 -0500<br>
From: Arpan Bakshi <<a href="mailto:arpanbakshi@gmail.com">arpanbakshi@gmail.com</a>><br>
To: Pasha Korber-Gonzalez <<a href="mailto:pasha.pkconsulting@gmail.com">pasha.pkconsulting@gmail.com</a>><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Radiant Heating and Cooling?<br>
Message-ID:<br>
        <AANLkTi=<a href="mailto:QF17QkSOoszThFKeUEbPh8CS-jh3W_hPRADmj@mail.gmail.com">QF17QkSOoszThFKeUEbPh8CS-jh3W_hPRADmj@mail.gmail.com</a>><br>
Content-Type: text/plain; charset="iso-8859-1"<br>
<br>
Julie,<br>
<br>
Adding to the radiant system discussion, consider modeling seconary loops<br>
which are then attached to the fan coil units. This will help define radiant<br>
system flow parameters independent of your primary loops and also since you<br>
have turned down the supply fan, the supply temperatures inputs you would<br>
typically used in an air only system would not apply.<br>
<br>
<br>
<br>
On Tue, Feb 8, 2011 at 11:26 AM, Pasha Korber-Gonzalez <<br>
<a href="mailto:pasha.pkconsulting@gmail.com">pasha.pkconsulting@gmail.com</a>> wrote:<br>
<br>
> Hi Julie,<br>
><br>
><br>
>    1. You can "represent" radiant ht & clg in eQuest, by modifying a<br>
>    system to *act* like a radiant system, however be mindful that<br>
>    because DOE2 can't do this explicitly there will be some discrepancies from<br>
>    real life, but it still can be a fairly realistic representation and<br>
>    measurment of the system performance.  To do this you will want to choose a<br>
>    Fan Coil system for your HVAC type and turn down your fan power in the FC<br>
>    units to zero.  You will also want to probably use a DOAS & Dummy Zone<br>
>    approach for your ventilation systems.  This is an approach to use in<br>
>    eQuest.   I can send you an example file of a Dummy zone for you to look<br>
>    through and learn from.  You will also want to read about the FC system in<br>
>    another DOE2 document I will also send you (off list).  Once you understand<br>
>    how DOE2 represent a Fan Coil system, then you will understand how you can<br>
>    change it to better act like a radiant system.   Others might consider using<br>
>    the PIU system in eQuest, but I have found by my experience that PIU's are<br>
>    better for representing Active Chilled Beam systems, and Fan Coils are<br>
>    better to represent radiant only systems.  I'm happy to share more of my sim<br>
>    experience with radiant systems, but I'm also curious to hear other's<br>
>    simulators experiences with representing radiant systems in eQuest too.<br>
>    2. When you say "louvers" I'm assuming you are referencing external<br>
>    shading devices.  Yes you can input vertical exterior shades on the outside<br>
>    of your building by using the Building Shade inputs.  This can only be done<br>
>    in DDedit mode, and the inputs are based on your XYZ coordinates of the<br>
>    building space. I will send you a 3rd document (Modeling Procedures Quck Ref<br>
>    Guide) and you can learn how to input these shades in Chapter 8 of the<br>
>    document.<br>
><br>
> Feel free to write back to the list or to me if you have more questions.<br>
> You will find lots of great simulators who are always more than willing to<br>
> share thier experiences with new users.<br>
><br>
> Hope this helps,<br>
> Pasha<br>
><br>
> Korber Energy Consultants<br>
> <a href="http://www.korberenergy.com" target="_blank">www.korberenergy.com</a><br>
><br>
> 2011/2/8 Ju-Yeon Julie Shin <<a href="mailto:juyeon519@hotmail.com">juyeon519@hotmail.com</a>><br>
><br>
>> Hello everyone, this is Julie Shin.<br>
>><br>
>> 1. I am curious whether it is possible to add "radiant heating and<br>
>> cooling" for eQUEST simulations or not.<br>
>> If it is possible, could anyone please let me know how to do so?<br>
>><br>
>> 2. Is it also possible to add vertical louvers? I have tried adding<br>
>> horizontal louvers, but not the vertical ones.<br>
>><br>
>> Thank you everyone and have a nice day.<br>
>><br>
>> Julie Shin.<br>
>><br>
>><br>
>><br>
>> _______________________________________________<br>
>> Equest-users mailing list<br>
>> <a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
>> To unsubscribe from this mailing list send  a blank message to<br>
>> <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
>><br>
>><br>
><br>
> _______________________________________________<br>
> Equest-users mailing list<br>
> <a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
> To unsubscribe from this mailing list send  a blank message to<br>
> <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
><br>
><br>
<br>
<br>
--<br>
<br>
Arpan Bakshi<br>
646 704-2880<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/a6143f54/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/a6143f54/attachment-0001.htm</a>><br>

<br>
------------------------------<br>
<br>
Message: 9<br>
Date: Tue, 8 Feb 2011 11:10:57 -0600<br>
From: Cory Duggin <<a href="mailto:crduggin@gmail.com">crduggin@gmail.com</a>><br>
To: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: [Equest-users] Heating and Cooling Schedules<br>
Message-ID:<br>
        <AANLkTi=Wh75yr=<a href="mailto:0x9An5%2BX2wsJ9w%2BGgRHs9CQWU0R5w1@mail.gmail.com">0x9An5+X2wsJ9w+GgRHs9CQWU0R5w1@mail.gmail.com</a>><br>
Content-Type: text/plain; charset="iso-8859-1"<br>
<br>
I edited the heating and cooling schedules in my simulation and reran, but<br>
the results didn't change.  I made new schedules for the times of the year<br>
when I don't want either heating or cooling running by moving the set<br>
point temperature up or down during those months.  How do I tell what<br>
equipment is running on the schedule besides the name?  Does the program<br>
depend on the format of the name to tell what equipment should use it?<br>
 Thanks<br>
<br>
--<br>
Cory Duggin, EI<br>
Tennessee Tech University<br>
Graduate Research Assistant<br>
Mechanical Engineering<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/4d6e88b9/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/4d6e88b9/attachment-0001.htm</a>><br>

<br>
------------------------------<br>
<br>
Message: 10<br>
Date: Tue, 8 Feb 2011 09:15:43 -0800 (PST)<br>
From: John Aulbach <<a href="mailto:jra_sac@yahoo.com">jra_sac@yahoo.com</a>><br>
To: Cory Duggin <<a href="mailto:crduggin@gmail.com">crduggin@gmail.com</a>>,<br>
        <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Heating and Cooling Schedules<br>
Message-ID: <<a href="mailto:738287.21226.qm@web52808.mail.re2.yahoo.com">738287.21226.qm@web52808.mail.re2.yahoo.com</a>><br>
Content-Type: text/plain; charset="iso-8859-1"<br>
<br>
Cory:<br>
<br>
I think we need to know exactly what schedules you changed. The thermostat<br>
settings? The fan schedule? Can you provide us with a .PD2 and .INP file for us<br>
to see?<br>
<br>
<br>
<br>
<br>
________________________________<br>
From: Cory Duggin <<a href="mailto:crduggin@gmail.com">crduggin@gmail.com</a>><br>
To: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Sent: Tue, February 8, 2011 9:10:57 AM<br>
Subject: [Equest-users] Heating and Cooling Schedules<br>
<br>
I edited the heating and cooling schedules in my simulation and reran, but the<br>
results didn't change. ?I made new schedules for the times of the year when I<br>
don't want either heating or cooling running by moving the?set point?temperature<br>
up or down during those months. ?How do I tell what equipment is running on the<br>
schedule besides the name? ?Does the program depend on the format of the name to<br>
tell what equipment should use it? ?Thanks<br>
<br>
--<br>
Cory Duggin, EI<br>
Tennessee Tech University<br>
Graduate Research Assistant<br>
Mechanical Engineering<br>
<br>
<br>
<br>
<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/a9dc87b9/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/a9dc87b9/attachment-0001.htm</a>><br>

<br>
------------------------------<br>
<br>
Message: 11<br>
Date: Tue, 8 Feb 2011 11:31:33 -0600<br>
From: Cory Duggin <<a href="mailto:crduggin@gmail.com">crduggin@gmail.com</a>><br>
To: John Aulbach <<a href="mailto:jra_sac@yahoo.com">jra_sac@yahoo.com</a>><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Heating and Cooling Schedules<br>
Message-ID:<br>
        <AANLkTikfvVriuX1kba_KLuMGk315A8w5jYa4pViG=<a href="mailto:ufW@mail.gmail.com">ufW@mail.gmail.com</a>><br>
Content-Type: text/plain; charset="iso-8859-1"<br>
<br>
I edited the schedules labeled heating and cooling for both system zones.<br>
 Thanks<br>
<br>
On Tue, Feb 8, 2011 at 11:15 AM, John Aulbach <<a href="mailto:jra_sac@yahoo.com">jra_sac@yahoo.com</a>> wrote:<br>
<br>
> Cory:<br>
><br>
> I think we need to know exactly what schedules you changed. The thermostat<br>
> settings? The fan schedule? Can you provide us with a .PD2 and .INP file for<br>
> us to see?<br>
><br>
>  ------------------------------<br>
> *From:* Cory Duggin <<a href="mailto:crduggin@gmail.com">crduggin@gmail.com</a>><br>
> *To:* <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
> *Sent:* Tue, February 8, 2011 9:10:57 AM<br>
> *Subject:* [Equest-users] Heating and Cooling Schedules<br>
><br>
> I edited the heating and cooling schedules in my simulation and reran, but<br>
> the results didn't change.  I made new schedules for the times of the year<br>
> when I don't want either heating or cooling running by moving the set<br>
> point temperature up or down during those months.  How do I tell what<br>
> equipment is running on the schedule besides the name?  Does the program<br>
> depend on the format of the name to tell what equipment should use it?<br>
>  Thanks<br>
><br>
> --<br>
> Cory Duggin, EI<br>
> Tennessee Tech University<br>
> Graduate Research Assistant<br>
> Mechanical Engineering<br>
><br>
><br>
<br>
<br>
--<br>
Cory Duggin, EI<br>
Tennessee Tech University<br>
Graduate Research Assistant<br>
Mechanical Engineering<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/d81b21e4/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/d81b21e4/attachment-0001.htm</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: CurrieComplete10_chiller.pd2<br>
Type: application/octet-stream<br>
Size: 15014 bytes<br>
Desc: not available<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/d81b21e4/CurrieComplete10_chiller-0001.pd2" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/d81b21e4/CurrieComplete10_chiller-0001.pd2</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: CurrieComplete10_chiller.inp<br>
Type: application/octet-stream<br>
Size: 56144 bytes<br>
Desc: not available<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/d81b21e4/CurrieComplete10_chiller-0001.inp" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/d81b21e4/CurrieComplete10_chiller-0001.inp</a>><br>

<br>
------------------------------<br>
<br>
Message: 12<br>
Date: Tue, 8 Feb 2011 09:57:10 -0800<br>
From: "Steven Savich" <<a href="mailto:ssavich@systemswestengineers.com">ssavich@systemswestengineers.com</a>><br>
To: <<a href="mailto:dtroy@glumac.com">dtroy@glumac.com</a>><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Modeling Multstack Units in eQUEST<br>
Message-ID: <005401cbc7b9$9e075930$da160b90$@com><br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
Dana,<br>
<br>
What solution did you end up using to model the Multistack heat pump chiller<br>
coupled to a vertical bore field in eQuest?<br>
<br>
Any pointers would be greatly appreciated.<br>
<br>
Thanks,<br>
Steven<br>
<br>
<br>
Steven Savich, LEED AP<br>
<br>
Systems West Engineers<br>
<br>
411 High Street<br>
<br>
Eugene, OR  97401-2427<br>
<br>
(541) 342-7210<br>
<br>
(541) 342-7220 (fax)<br>
<br>
<br>
<br>
<br>
Has anyone had any luck modeling a Multistack<br>
(<a href="http://www.multistack.com/" target="_blank">http://www.multistack.com/</a>) unit in eQUEST?<br>
<br>
<br>
<br>
We have a project that uses a Multistack unit to provide hot and chilled<br>
water to a project and is coupled to a vertical bore field. eQUEST does<br>
not have the capability to model system directly, so I have been trying<br>
to look into other methods, all which are falling short. So far I have<br>
tried:<br>
<br>
<br>
<br>
*         Using the "Loop-to-Loop Heat Pump" chiller; however, this<br>
system does not work like the Multistack, as the Multistack does not<br>
have internal heat exchange, has multiple compressor stages which are<br>
all piped in parallel with the condenser water, and can only be<br>
connected to a Lake/Well loop.<br>
<br>
*         Using a separate chilled water loop and hot water loop, each<br>
of which are connected to a WLHP loop with a vertical bore HX. This<br>
would be perfect, as I can put as many chillers and boilers on the loops<br>
as there are stages in the Multistack; however, eQUEST does not have a<br>
heat-pump boiler, so the boiler cannot be connected to the vertical bore<br>
field.<br>
<br>
*         Using a dummy space/zone/system connected to a dummy heat<br>
recovery chiller. The chiller would then reject heat to the hot water<br>
loop that supplies the rest of the building. This would work, however<br>
the chiller demand is driven by the cooling load of the dummy system and<br>
it is impossible to create a dummy cooling load that would exactly match<br>
the heating load required by the hot water loop.<br>
<br>
*         And finally, using a domestic hot water loop because the<br>
boiler type can be set to "heat pump", however, the heat cannot be<br>
rejected to a condenser water loop.<br>
<br>
<br>
<br>
So I guess the question I am asking is has anyone either successfully<br>
modeled the Multistack unit OR modeled a heat pump boiler?<br>
<br>
<br>
<br>
Thanks in advance.<br>
<br>
<br>
<br>
-Dana<br>
<br>
<br>
Dana Troy<br>
Energy Analyst<br>
LEED(r) Accredited Professional<br>
<br>
  <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
<br>
________________________________<br>
<br>
320 SW Washington, Suite 200<br>
Portland, OR 97204-2640<br>
T.  503.227.5280  F. 503.274.7674<br>
<br>
Thinking. Inside the building.<br>
<a href="http://www.glumac.com" target="_blank">www.glumac.com</a> <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/f2ef97ef/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/f2ef97ef/attachment-0001.htm</a>><br>

<br>
------------------------------<br>
<br>
Message: 13<br>
Date: Tue, 8 Feb 2011 10:07:48 -0800<br>
From: "Dana Troy" <<a href="mailto:DTroy@glumac.com">DTroy@glumac.com</a>><br>
To: <<a href="mailto:ssavich@systemswestengineers.com">ssavich@systemswestengineers.com</a>><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Modeling Multstack Units in eQUEST<br>
Message-ID:<br>
        <<a href="mailto:1253D478FBC8C741B18466AB40B5CCD4051EEFE1@pdxmail1.glumac.com">1253D478FBC8C741B18466AB40B5CCD4051EEFE1@pdxmail1.glumac.com</a>><br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
Steven,<br>
<br>
<br>
<br>
We successfully developed a methodology for simulating ground-coupled<br>
Multistack heat pumps in eQUEST. I have included below portions of our<br>
SEED Report (Oregon's stated required program for publicly funded<br>
buildings). A lot of the text is specific to the project we were working<br>
on, but the general idea is there.<br>
<br>
<br>
<br>
The project ended up pursuing a standard chilled/heating water<br>
arrangement for the final design, so the Multistack heat pump was not<br>
installed.<br>
<br>
<br>
<br>
I hope this information helps.<br>
<br>
<br>
<br>
Regards,<br>
Dana<br>
<br>
<br>
<br>
<br>
<br>
Heating and cooling will be provided by hot and chilled water,<br>
respectively, from a ground-coupled heat pump Multistack unit and will<br>
be connected to a condenser water vertical bore field. A Multistack unit<br>
is essentially a unit that contains a number of heat pump modules linked<br>
together in parallel. Depending on the load, each module can provide<br>
either heating water or chilled water. The condenser water loop is then<br>
connected to a vertical bore field onsite, where 200 ft deep bores<br>
located 20 feet on center is anticipated. The Multistack on this project<br>
utilizes seven modules.<br>
<br>
<br>
<br>
As eQUEST cannot directly model a Multistack unit, an alternate approach<br>
had to be taken in order to approximate the operation of the equipment.<br>
In summary, the Multistack was modeled in eQUEST by simulating each<br>
module of the Multistack as an individual chiller for heating and<br>
cooling. A general diagram on how the system is modeled in eQUEST can be<br>
seen in Figure 8 on the following page while more detailed explanations<br>
can be seen on the following pages.<br>
<br>
<br>
<br>
<br>
<br>
Figure: How the Multistack was simulated in eQUEST<br>
<br>
<br>
<br>
<br>
<br>
Chilled water<br>
<br>
The chillers have a total flow of approximately 640 gpm and provide<br>
45-degree chilled water with a 57-degree return water temperature.<br>
Connected to the chilled water loop are two pumps, in parallel that<br>
provide the 640 gpm flow.<br>
<br>
<br>
<br>
Each chiller module is modeled as an electric hermetic centrifugal<br>
chiller with a capacity of 70 tons. Each stage is scheduled remain off<br>
until the stage before has been loaded to 100% and has an EER of 23 (EIR<br>
of 0.1483).<br>
<br>
<br>
<br>
Default capacity curves were used for the preliminary analysis, however,<br>
customizes curves will be used once the information becomes available. A<br>
screenshot of the eQUEST layout in the Water-Side HVAC tab can be seen<br>
below in Figure 9.<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
Heating water<br>
<br>
Since there is no heat pump boiler, an alternative method had to be<br>
developed to simulate the production of hot water. The heat pump chiller<br>
(LOOP-TO-LOOP-HP) in eQUEST is a heat pump that provides heating and<br>
chilled water simultaneously, with the larger load rejecting heat to the<br>
smaller load. This system could not be used for both the heating and<br>
cooling of the Multistack unit because it internal heat recovery when<br>
the dominant load rejects or adds heat to the small load. The Multistack<br>
has multiple smaller modules that operate in either cooling or heating<br>
only, and therefore do not provide integral heat recovery.<br>
<br>
<br>
<br>
Since the LOOP-TO-LOOP-HP needs to be connected to a chilled water loop<br>
to work properly in eQUEST, the chillers had to be connected to a<br>
"dummy" chilled water loop. In order to avoid a "loop has zero flow"<br>
error, the loop had a minimal process chilled water flow that reset down<br>
to zero after the first hour of the year. The chillers were then<br>
connected to the hot water loop that serves the building. Since the hot<br>
water demand will always be higher than the dummy process chilled water<br>
flow the chillers will be driven by the hot water loop.<br>
<br>
<br>
<br>
The chillers have a flow of 715 gpm and provide 110-degree hot water<br>
with a 90-degree return water temperature. Connected to the hot water<br>
loop are two pumps, in parallel, that provide the 715 gpm flow.<br>
<br>
<br>
<br>
In eQUEST, it is required that secondary hot water pumps and chilled<br>
water pumps be connected to each heat pump chiller. Since the design is<br>
a variable primary flow and the chilled water is a dummy load, the<br>
secondary hot water pump power and the dummy chilled water pump power<br>
was zeroed out.<br>
<br>
eQUEST also does not allow the heat pump chiller to be connected to any<br>
condenser water loop except the type "LAKE/WELL". In order to keep the<br>
ground coupled performance level, both the chilled water and heating<br>
water chillers connected to lake/well loops. Details of the condenser<br>
water loop can be seen in the next section. A screenshot of the eQUEST<br>
layout in the Water-Side HVAC tab can be seen below in Figure 9.<br>
<br>
<br>
<br>
Also included in the design is a hot water condensing boiler to provide<br>
additional heating capacity during extreme peaking cooling. Since eQUEST<br>
uses TMY2 weather data that generally uses hourly averages, extreme cold<br>
days are never modeled, and therefore the boiler never turns on.<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
Condenser water<br>
<br>
Due to modeling limitations of the heat pump chiller, each condenser<br>
water loop was modeled as a LAKE/WELL loop. Each heating and cooling<br>
module was given its own loop to track and verify performance in the<br>
hourly reports. Each loop was scheduled to supply 55-degree condenser<br>
water back to the chillers, as scheduled in drawings.<br>
<br>
<br>
<br>
The design consists of two condenser water loops connected in parallel.<br>
In the model, the two pumps were divided up amongst the chillers, with<br>
each pump set to single speed. Since each pump would only turn on when<br>
the chiller it was attached to was operating, it would loosely represent<br>
a variable speed drive pump with multiple stages.<br>
<br>
<br>
<br>
<br>
<br>
Dana Troy<br>
Senior Energy Analyst<br>
LEED AP(r)<br>
<br>
  <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
<br>
________________________________<br>
<br>
320 SW Washington, Suite 200<br>
Portland, OR 97204-2640<br>
T.  503.227.5280  F. 503.274.7674<br>
<br>
Thinking. Inside the building.<br>
<a href="http://www.glumac.com" target="_blank">www.glumac.com</a> <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
<br>
<br>
<br>
<br>
From: Steven Savich [mailto:<a href="mailto:ssavich@systemswestengineers.com">ssavich@systemswestengineers.com</a>]<br>
Sent: Tuesday, February 08, 2011 9:57 AM<br>
To: Dana Troy<br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Modeling Multstack Units in eQUEST<br>
<br>
<br>
<br>
Dana,<br>
<br>
What solution did you end up using to model the Multistack heat pump<br>
chiller coupled to a vertical bore field in eQuest?<br>
<br>
Any pointers would be greatly appreciated.<br>
<br>
Thanks,<br>
Steven<br>
<br>
<br>
Steven Savich, LEED AP<br>
<br>
Systems West Engineers<br>
<br>
411 High Street<br>
<br>
Eugene, OR  97401-2427<br>
<br>
(541) 342-7210<br>
<br>
(541) 342-7220 (fax)<br>
<br>
<br>
<br>
<br>
Has anyone had any luck modeling a Multistack<br>
(<a href="http://www.multistack.com/" target="_blank">http://www.multistack.com/</a>) unit in eQUEST?<br>
<br>
<br>
<br>
We have a project that uses a Multistack unit to provide hot and chilled<br>
water to a project and is coupled to a vertical bore field. eQUEST does<br>
not have the capability to model system directly, so I have been trying<br>
to look into other methods, all which are falling short. So far I have<br>
tried:<br>
<br>
<br>
<br>
*         Using the "Loop-to-Loop Heat Pump" chiller; however, this<br>
system does not work like the Multistack, as the Multistack does not<br>
have internal heat exchange, has multiple compressor stages which are<br>
all piped in parallel with the condenser water, and can only be<br>
connected to a Lake/Well loop.<br>
<br>
*         Using a separate chilled water loop and hot water loop, each<br>
of which are connected to a WLHP loop with a vertical bore HX. This<br>
would be perfect, as I can put as many chillers and boilers on the loops<br>
as there are stages in the Multistack; however, eQUEST does not have a<br>
heat-pump boiler, so the boiler cannot be connected to the vertical bore<br>
field.<br>
<br>
*         Using a dummy space/zone/system connected to a dummy heat<br>
recovery chiller. The chiller would then reject heat to the hot water<br>
loop that supplies the rest of the building. This would work, however<br>
the chiller demand is driven by the cooling load of the dummy system and<br>
it is impossible to create a dummy cooling load that would exactly match<br>
the heating load required by the hot water loop.<br>
<br>
*         And finally, using a domestic hot water loop because the<br>
boiler type can be set to "heat pump", however, the heat cannot be<br>
rejected to a condenser water loop.<br>
<br>
<br>
<br>
So I guess the question I am asking is has anyone either successfully<br>
modeled the Multistack unit OR modeled a heat pump boiler?<br>
<br>
<br>
<br>
Thanks in advance.<br>
<br>
<br>
<br>
-Dana<br>
<br>
<br>
Dana Troy<br>
Energy Analyst<br>
LEED(r) Accredited Professional<br>
<br>
  <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
<br>
________________________________<br>
<br>
320 SW Washington, Suite 200<br>
Portland, OR 97204-2640<br>
T.  503.227.5280  F. 503.274.7674<br>
<br>
Thinking. Inside the building.<br>
<a href="http://www.glumac.com" target="_blank">www.glumac.com</a> <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0001.htm</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 3422 bytes<br>
Desc: image010.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0004.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0004.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/gif<br>
Size: 1425 bytes<br>
Desc: image011.gif<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0001.gif" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0001.gif</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 50724 bytes<br>
Desc: image002.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0005.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0005.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 27732 bytes<br>
Desc: image004.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0006.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0006.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 43024 bytes<br>
Desc: image006.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0007.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/2499b9e4/attachment-0007.jpeg</a>><br>

<br>
------------------------------<br>
<br>
Message: 14<br>
Date: Tue, 8 Feb 2011 12:36:08 -0600<br>
From: "Nick Caton" <<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>><br>
To: "Dana Troy" <<a href="mailto:DTroy@glumac.com">DTroy@glumac.com</a>>,     <<a href="mailto:ssavich@systemswestengineers.com">ssavich@systemswestengineers.com</a>><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Modeling Multstack Units in eQUEST<br>
Message-ID:<br>
        <<a href="mailto:FCEBC0C28321F7479789B25A13030F6902C3C006@sandbinc2.sbi.smithboucher.com">FCEBC0C28321F7479789B25A13030F6902C3C006@sandbinc2.sbi.smithboucher.com</a>><br>
<br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
Very busy week here, but I have to take a minute to say:  Dana, that is<br>
a really nice write up!  Thanks so much for sharing with the community<br>
=).<br>
<br>
<br>
<br>
~Nick<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
NICK CATON, E.I.T.<br>
<br>
PROJECT ENGINEER<br>
<br>
Smith & Boucher Engineers<br>
<br>
25501 west valley parkway<br>
<br>
olathe ks 66061<br>
<br>
direct 913 344.0036<br>
<br>
fax 913 345.0617<br>
<br>
<a href="http://www.smithboucher.com" target="_blank">www.smithboucher.com</a><br>
<br>
<br>
<br>
From: <a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a><br>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>] On Behalf Of Dana<br>
Troy<br>
Sent: Tuesday, February 08, 2011 12:08 PM<br>
To: <a href="mailto:ssavich@systemswestengineers.com">ssavich@systemswestengineers.com</a><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Modeling Multstack Units in eQUEST<br>
<br>
<br>
<br>
Steven,<br>
<br>
<br>
<br>
We successfully developed a methodology for simulating ground-coupled<br>
Multistack heat pumps in eQUEST. I have included below portions of our<br>
SEED Report (Oregon's stated required program for publicly funded<br>
buildings). A lot of the text is specific to the project we were working<br>
on, but the general idea is there.<br>
<br>
<br>
<br>
The project ended up pursuing a standard chilled/heating water<br>
arrangement for the final design, so the Multistack heat pump was not<br>
installed.<br>
<br>
<br>
<br>
I hope this information helps.<br>
<br>
<br>
<br>
Regards,<br>
Dana<br>
<br>
<br>
<br>
<br>
<br>
Heating and cooling will be provided by hot and chilled water,<br>
respectively, from a ground-coupled heat pump Multistack unit and will<br>
be connected to a condenser water vertical bore field. A Multistack unit<br>
is essentially a unit that contains a number of heat pump modules linked<br>
together in parallel. Depending on the load, each module can provide<br>
either heating water or chilled water. The condenser water loop is then<br>
connected to a vertical bore field onsite, where 200 ft deep bores<br>
located 20 feet on center is anticipated. The Multistack on this project<br>
utilizes seven modules.<br>
<br>
<br>
<br>
As eQUEST cannot directly model a Multistack unit, an alternate approach<br>
had to be taken in order to approximate the operation of the equipment.<br>
In summary, the Multistack was modeled in eQUEST by simulating each<br>
module of the Multistack as an individual chiller for heating and<br>
cooling. A general diagram on how the system is modeled in eQUEST can be<br>
seen in Figure 8 on the following page while more detailed explanations<br>
can be seen on the following pages.<br>
<br>
<br>
<br>
<br>
<br>
Figure: How the Multistack was simulated in eQUEST<br>
<br>
<br>
<br>
<br>
<br>
Chilled water<br>
<br>
The chillers have a total flow of approximately 640 gpm and provide<br>
45-degree chilled water with a 57-degree return water temperature.<br>
Connected to the chilled water loop are two pumps, in parallel that<br>
provide the 640 gpm flow.<br>
<br>
<br>
<br>
Each chiller module is modeled as an electric hermetic centrifugal<br>
chiller with a capacity of 70 tons. Each stage is scheduled remain off<br>
until the stage before has been loaded to 100% and has an EER of 23 (EIR<br>
of 0.1483).<br>
<br>
<br>
<br>
Default capacity curves were used for the preliminary analysis, however,<br>
customizes curves will be used once the information becomes available. A<br>
screenshot of the eQUEST layout in the Water-Side HVAC tab can be seen<br>
below in Figure 9.<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
Heating water<br>
<br>
Since there is no heat pump boiler, an alternative method had to be<br>
developed to simulate the production of hot water. The heat pump chiller<br>
(LOOP-TO-LOOP-HP) in eQUEST is a heat pump that provides heating and<br>
chilled water simultaneously, with the larger load rejecting heat to the<br>
smaller load. This system could not be used for both the heating and<br>
cooling of the Multistack unit because it internal heat recovery when<br>
the dominant load rejects or adds heat to the small load. The Multistack<br>
has multiple smaller modules that operate in either cooling or heating<br>
only, and therefore do not provide integral heat recovery.<br>
<br>
<br>
<br>
Since the LOOP-TO-LOOP-HP needs to be connected to a chilled water loop<br>
to work properly in eQUEST, the chillers had to be connected to a<br>
"dummy" chilled water loop. In order to avoid a "loop has zero flow"<br>
error, the loop had a minimal process chilled water flow that reset down<br>
to zero after the first hour of the year. The chillers were then<br>
connected to the hot water loop that serves the building. Since the hot<br>
water demand will always be higher than the dummy process chilled water<br>
flow the chillers will be driven by the hot water loop.<br>
<br>
<br>
<br>
The chillers have a flow of 715 gpm and provide 110-degree hot water<br>
with a 90-degree return water temperature. Connected to the hot water<br>
loop are two pumps, in parallel, that provide the 715 gpm flow.<br>
<br>
<br>
<br>
In eQUEST, it is required that secondary hot water pumps and chilled<br>
water pumps be connected to each heat pump chiller. Since the design is<br>
a variable primary flow and the chilled water is a dummy load, the<br>
secondary hot water pump power and the dummy chilled water pump power<br>
was zeroed out.<br>
<br>
eQUEST also does not allow the heat pump chiller to be connected to any<br>
condenser water loop except the type "LAKE/WELL". In order to keep the<br>
ground coupled performance level, both the chilled water and heating<br>
water chillers connected to lake/well loops. Details of the condenser<br>
water loop can be seen in the next section. A screenshot of the eQUEST<br>
layout in the Water-Side HVAC tab can be seen below in Figure 9.<br>
<br>
<br>
<br>
Also included in the design is a hot water condensing boiler to provide<br>
additional heating capacity during extreme peaking cooling. Since eQUEST<br>
uses TMY2 weather data that generally uses hourly averages, extreme cold<br>
days are never modeled, and therefore the boiler never turns on.<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
Condenser water<br>
<br>
Due to modeling limitations of the heat pump chiller, each condenser<br>
water loop was modeled as a LAKE/WELL loop. Each heating and cooling<br>
module was given its own loop to track and verify performance in the<br>
hourly reports. Each loop was scheduled to supply 55-degree condenser<br>
water back to the chillers, as scheduled in drawings.<br>
<br>
<br>
<br>
The design consists of two condenser water loops connected in parallel.<br>
In the model, the two pumps were divided up amongst the chillers, with<br>
each pump set to single speed. Since each pump would only turn on when<br>
the chiller it was attached to was operating, it would loosely represent<br>
a variable speed drive pump with multiple stages.<br>
<br>
<br>
<br>
<br>
<br>
Dana Troy<br>
Senior Energy Analyst<br>
LEED AP(r)<br>
<br>
  <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
<br>
________________________________<br>
<br>
320 SW Washington, Suite 200<br>
Portland, OR 97204-2640<br>
T.  503.227.5280  F. 503.274.7674<br>
<br>
Thinking. Inside the building.<br>
<a href="http://www.glumac.com" target="_blank">www.glumac.com</a> <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
<br>
<br>
<br>
<br>
From: Steven Savich [mailto:<a href="mailto:ssavich@systemswestengineers.com">ssavich@systemswestengineers.com</a>]<br>
Sent: Tuesday, February 08, 2011 9:57 AM<br>
To: Dana Troy<br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Modeling Multstack Units in eQUEST<br>
<br>
<br>
<br>
Dana,<br>
<br>
What solution did you end up using to model the Multistack heat pump<br>
chiller coupled to a vertical bore field in eQuest?<br>
<br>
Any pointers would be greatly appreciated.<br>
<br>
Thanks,<br>
Steven<br>
<br>
<br>
Steven Savich, LEED AP<br>
<br>
Systems West Engineers<br>
<br>
411 High Street<br>
<br>
Eugene, OR  97401-2427<br>
<br>
(541) 342-7210<br>
<br>
(541) 342-7220 (fax)<br>
<br>
<br>
<br>
<br>
Has anyone had any luck modeling a Multistack<br>
(<a href="http://www.multistack.com/" target="_blank">http://www.multistack.com/</a>) unit in eQUEST?<br>
<br>
<br>
<br>
We have a project that uses a Multistack unit to provide hot and chilled<br>
water to a project and is coupled to a vertical bore field. eQUEST does<br>
not have the capability to model system directly, so I have been trying<br>
to look into other methods, all which are falling short. So far I have<br>
tried:<br>
<br>
<br>
<br>
*         Using the "Loop-to-Loop Heat Pump" chiller; however, this<br>
system does not work like the Multistack, as the Multistack does not<br>
have internal heat exchange, has multiple compressor stages which are<br>
all piped in parallel with the condenser water, and can only be<br>
connected to a Lake/Well loop.<br>
<br>
*         Using a separate chilled water loop and hot water loop, each<br>
of which are connected to a WLHP loop with a vertical bore HX. This<br>
would be perfect, as I can put as many chillers and boilers on the loops<br>
as there are stages in the Multistack; however, eQUEST does not have a<br>
heat-pump boiler, so the boiler cannot be connected to the vertical bore<br>
field.<br>
<br>
*         Using a dummy space/zone/system connected to a dummy heat<br>
recovery chiller. The chiller would then reject heat to the hot water<br>
loop that supplies the rest of the building. This would work, however<br>
the chiller demand is driven by the cooling load of the dummy system and<br>
it is impossible to create a dummy cooling load that would exactly match<br>
the heating load required by the hot water loop.<br>
<br>
*         And finally, using a domestic hot water loop because the<br>
boiler type can be set to "heat pump", however, the heat cannot be<br>
rejected to a condenser water loop.<br>
<br>
<br>
<br>
So I guess the question I am asking is has anyone either successfully<br>
modeled the Multistack unit OR modeled a heat pump boiler?<br>
<br>
<br>
<br>
Thanks in advance.<br>
<br>
<br>
<br>
-Dana<br>
<br>
<br>
Dana Troy<br>
Energy Analyst<br>
LEED(r) Accredited Professional<br>
<br>
  <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
<br>
________________________________<br>
<br>
320 SW Washington, Suite 200<br>
Portland, OR 97204-2640<br>
T.  503.227.5280  F. 503.274.7674<br>
<br>
Thinking. Inside the building.<br>
<a href="http://www.glumac.com" target="_blank">www.glumac.com</a> <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0001.htm</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 1459 bytes<br>
Desc: image001.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0005.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0005.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 50724 bytes<br>
Desc: image002.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0006.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0006.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 27732 bytes<br>
Desc: image003.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0007.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0007.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 43024 bytes<br>
Desc: image004.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0008.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0008.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 3422 bytes<br>
Desc: image005.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0009.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0009.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/gif<br>
Size: 1425 bytes<br>
Desc: image006.gif<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0001.gif" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/c754f2c3/attachment-0001.gif</a>><br>

<br>
------------------------------<br>
<br>
Message: 15<br>
Date: Tue, 8 Feb 2011 14:22:32 -0500<br>
From: "Bishop, Bill" <<a href="mailto:wbishop@pathfinder-ea.com">wbishop@pathfinder-ea.com</a>><br>
To: <<a href="mailto:ssavich@systemswestengineers.com">ssavich@systemswestengineers.com</a>>, "Dana Troy" <<a href="mailto:DTroy@glumac.com">DTroy@glumac.com</a>><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Modeling Multistack Units in eQUEST<br>
Message-ID:<br>
        <<a href="mailto:83996EE70003D04B830E1C4A5E6688CE018C196F@PATHMAIL2.pathfinderengineers.com">83996EE70003D04B830E1C4A5E6688CE018C196F@PATHMAIL2.pathfinderengineers.com</a>><br>
<br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
Steven, Dana,<br>
<br>
You could also consider using the Heat Pump chiller type (instead of<br>
Loop-to-Loop), attached to a two-pipe loop. From the description, it<br>
sounds like each stage/compressor of the Multistack unit supplies either<br>
HW or CHW to a two-pipe loop. You still have to use the Lake/Well loop<br>
type to represent the vertical bore field, but you avoid creating<br>
separate HW and CHW loops and duplicating the pumps, and you deal more<br>
realistically with the limitations of a two-pipe loop.<br>
<br>
Regards,<br>
Bill<br>
<br>
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects<br>
LLP<br>
Mechanical Engineer<br>
<br>
 134 South Fitzhugh Street                 Rochester, NY 14608<br>
T: (585) 325-6004 Ext. 114                F: (585) 325-6005<br>
<a href="mailto:wbishop@pathfinder-ea.com">wbishop@pathfinder-ea.com</a>           <a href="http://www.pathfinder-ea.com" target="_blank">www.pathfinder-ea.com</a><br>
<<a href="http://www.pathfinder-ea.com/" target="_blank">http://www.pathfinder-ea.com/</a>><br>
P   Sustainability - the forest AND the trees. P<br>
________________________________<br>
<br>
From: <a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a><br>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>] On Behalf Of Dana<br>
Troy<br>
Sent: Tuesday, February 08, 2011 1:08 PM<br>
To: <a href="mailto:ssavich@systemswestengineers.com">ssavich@systemswestengineers.com</a><br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Modeling Multstack Units in eQUEST<br>
<br>
Steven,<br>
<br>
We successfully developed a methodology for simulating ground-coupled<br>
Multistack heat pumps in eQUEST. I have included below portions of our<br>
SEED Report (Oregon's stated required program for publicly funded<br>
buildings). A lot of the text is specific to the project we were working<br>
on, but the general idea is there.<br>
<br>
The project ended up pursuing a standard chilled/heating water<br>
arrangement for the final design, so the Multistack heat pump was not<br>
installed.<br>
<br>
I hope this information helps.<br>
<br>
Regards,<br>
Dana<br>
<br>
<br>
Heating and cooling will be provided by hot and chilled water,<br>
respectively, from a ground-coupled heat pump Multistack unit and will<br>
be connected to a condenser water vertical bore field. A Multistack unit<br>
is essentially a unit that contains a number of heat pump modules linked<br>
together in parallel. Depending on the load, each module can provide<br>
either heating water or chilled water. The condenser water loop is then<br>
connected to a vertical bore field onsite, where 200 ft deep bores<br>
located 20 feet on center is anticipated. The Multistack on this project<br>
utilizes seven modules.<br>
<br>
As eQUEST cannot directly model a Multistack unit, an alternate approach<br>
had to be taken in order to approximate the operation of the equipment.<br>
In summary, the Multistack was modeled in eQUEST by simulating each<br>
module of the Multistack as an individual chiller for heating and<br>
cooling. A general diagram on how the system is modeled in eQUEST can be<br>
seen in Figure 8 on the following page while more detailed explanations<br>
can be seen on the following pages.<br>
<br>
<br>
Figure: How the Multistack was simulated in eQUEST<br>
<br>
<br>
Chilled water<br>
The chillers have a total flow of approximately 640 gpm and provide<br>
45-degree chilled water with a 57-degree return water temperature.<br>
Connected to the chilled water loop are two pumps, in parallel that<br>
provide the 640 gpm flow.<br>
<br>
Each chiller module is modeled as an electric hermetic centrifugal<br>
chiller with a capacity of 70 tons. Each stage is scheduled remain off<br>
until the stage before has been loaded to 100% and has an EER of 23 (EIR<br>
of 0.1483).<br>
<br>
Default capacity curves were used for the preliminary analysis, however,<br>
customizes curves will be used once the information becomes available. A<br>
screenshot of the eQUEST layout in the Water-Side HVAC tab can be seen<br>
below in Figure 9.<br>
<br>
<br>
<br>
Heating water<br>
Since there is no heat pump boiler, an alternative method had to be<br>
developed to simulate the production of hot water. The heat pump chiller<br>
(LOOP-TO-LOOP-HP) in eQUEST is a heat pump that provides heating and<br>
chilled water simultaneously, with the larger load rejecting heat to the<br>
smaller load. This system could not be used for both the heating and<br>
cooling of the Multistack unit because it internal heat recovery when<br>
the dominant load rejects or adds heat to the small load. The Multistack<br>
has multiple smaller modules that operate in either cooling or heating<br>
only, and therefore do not provide integral heat recovery.<br>
<br>
Since the LOOP-TO-LOOP-HP needs to be connected to a chilled water loop<br>
to work properly in eQUEST, the chillers had to be connected to a<br>
"dummy" chilled water loop. In order to avoid a "loop has zero flow"<br>
error, the loop had a minimal process chilled water flow that reset down<br>
to zero after the first hour of the year. The chillers were then<br>
connected to the hot water loop that serves the building. Since the hot<br>
water demand will always be higher than the dummy process chilled water<br>
flow the chillers will be driven by the hot water loop.<br>
<br>
The chillers have a flow of 715 gpm and provide 110-degree hot water<br>
with a 90-degree return water temperature. Connected to the hot water<br>
loop are two pumps, in parallel, that provide the 715 gpm flow.<br>
<br>
In eQUEST, it is required that secondary hot water pumps and chilled<br>
water pumps be connected to each heat pump chiller. Since the design is<br>
a variable primary flow and the chilled water is a dummy load, the<br>
secondary hot water pump power and the dummy chilled water pump power<br>
was zeroed out.<br>
eQUEST also does not allow the heat pump chiller to be connected to any<br>
condenser water loop except the type "LAKE/WELL". In order to keep the<br>
ground coupled performance level, both the chilled water and heating<br>
water chillers connected to lake/well loops. Details of the condenser<br>
water loop can be seen in the next section. A screenshot of the eQUEST<br>
layout in the Water-Side HVAC tab can be seen below in Figure 9.<br>
<br>
Also included in the design is a hot water condensing boiler to provide<br>
additional heating capacity during extreme peaking cooling. Since eQUEST<br>
uses TMY2 weather data that generally uses hourly averages, extreme cold<br>
days are never modeled, and therefore the boiler never turns on.<br>
<br>
<br>
<br>
<br>
Condenser water<br>
Due to modeling limitations of the heat pump chiller, each condenser<br>
water loop was modeled as a LAKE/WELL loop. Each heating and cooling<br>
module was given its own loop to track and verify performance in the<br>
hourly reports. Each loop was scheduled to supply 55-degree condenser<br>
water back to the chillers, as scheduled in drawings.<br>
<br>
The design consists of two condenser water loops connected in parallel.<br>
In the model, the two pumps were divided up amongst the chillers, with<br>
each pump set to single speed. Since each pump would only turn on when<br>
the chiller it was attached to was operating, it would loosely represent<br>
a variable speed drive pump with multiple stages.<br>
<br>
<br>
Dana Troy<br>
Senior Energy Analyst<br>
LEED AP(r)<br>
<br>
  <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
________________________________<br>
<br>
320 SW Washington, Suite 200<br>
Portland, OR 97204-2640<br>
T.  503.227.5280  F. 503.274.7674<br>
<br>
Thinking. Inside the building.<br>
<a href="http://www.glumac.com" target="_blank">www.glumac.com</a> <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
<br>
<br>
From: Steven Savich [mailto:<a href="mailto:ssavich@systemswestengineers.com">ssavich@systemswestengineers.com</a>]<br>
Sent: Tuesday, February 08, 2011 9:57 AM<br>
To: Dana Troy<br>
Cc: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Modeling Multstack Units in eQUEST<br>
<br>
Dana,<br>
<br>
What solution did you end up using to model the Multistack heat pump<br>
chiller coupled to a vertical bore field in eQuest?<br>
<br>
Any pointers would be greatly appreciated.<br>
<br>
Thanks,<br>
Steven<br>
<br>
Steven Savich, LEED AP<br>
Systems West Engineers<br>
411 High Street<br>
Eugene, OR  97401-2427<br>
(541) 342-7210<br>
(541) 342-7220 (fax)<br>
<br>
<br>
Has anyone had any luck modeling a Multistack<br>
(<a href="http://www.multistack.com/" target="_blank">http://www.multistack.com/</a>) unit in eQUEST?<br>
<br>
<br>
<br>
We have a project that uses a Multistack unit to provide hot and chilled<br>
water to a project and is coupled to a vertical bore field. eQUEST does<br>
not have the capability to model system directly, so I have been trying<br>
to look into other methods, all which are falling short. So far I have<br>
tried:<br>
<br>
<br>
<br>
*         Using the "Loop-to-Loop Heat Pump" chiller; however, this<br>
system does not work like the Multistack, as the Multistack does not<br>
have internal heat exchange, has multiple compressor stages which are<br>
all piped in parallel with the condenser water, and can only be<br>
connected to a Lake/Well loop.<br>
<br>
*         Using a separate chilled water loop and hot water loop, each<br>
of which are connected to a WLHP loop with a vertical bore HX. This<br>
would be perfect, as I can put as many chillers and boilers on the loops<br>
as there are stages in the Multistack; however, eQUEST does not have a<br>
heat-pump boiler, so the boiler cannot be connected to the vertical bore<br>
field.<br>
<br>
*         Using a dummy space/zone/system connected to a dummy heat<br>
recovery chiller. The chiller would then reject heat to the hot water<br>
loop that supplies the rest of the building. This would work, however<br>
the chiller demand is driven by the cooling load of the dummy system and<br>
it is impossible to create a dummy cooling load that would exactly match<br>
the heating load required by the hot water loop.<br>
<br>
*         And finally, using a domestic hot water loop because the<br>
boiler type can be set to "heat pump", however, the heat cannot be<br>
rejected to a condenser water loop.<br>
<br>
<br>
<br>
So I guess the question I am asking is has anyone either successfully<br>
modeled the Multistack unit OR modeled a heat pump boiler?<br>
<br>
<br>
<br>
Thanks in advance.<br>
<br>
<br>
<br>
-Dana<br>
<br>
<br>
Dana Troy<br>
Energy Analyst<br>
LEED(r) Accredited Professional<br>
<br>
  <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
<br>
________________________________<br>
<br>
320 SW Washington, Suite 200<br>
Portland, OR 97204-2640<br>
T.  503.227.5280  F. 503.274.7674<br>
<br>
Thinking. Inside the building.<br>
<a href="http://www.glumac.com" target="_blank">www.glumac.com</a> <<a href="http://www.glumac.com/" target="_blank">http://www.glumac.com/</a>><br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0001.htm</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/gif<br>
Size: 1425 bytes<br>
Desc: image006.gif<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0001.gif" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0001.gif</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 3422 bytes<br>
Desc: image005.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0005.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0005.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 43024 bytes<br>
Desc: image004.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0006.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0006.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 27732 bytes<br>
Desc: image003.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0007.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0007.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 50724 bytes<br>
Desc: image002.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0008.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0008.jpeg</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/jpeg<br>
Size: 2412 bytes<br>
Desc: image001.jpg<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0009.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/9e94a1ea/attachment-0009.jpeg</a>><br>

<br>
------------------------------<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="mailto:Equest-users@lists.onebuilding.org">Equest-users@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
<br>
<br>
End of Equest-users Digest, Vol 35, Issue 8<br>
*******************************************<br>