Sorry, hit the wrong button. I'm not sure which volume the equations are in but I'll see if I can find and send to you.<div><br></div><div>Carol<br><br><div class="gmail_quote">On Sat, Feb 5, 2011 at 12:54 PM, Carol Gardner <span dir="ltr"><<a href="mailto:cmg750@gmail.com">cmg750@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">Hi John,<div><br></div><div>The entering wet bulb temperature for the outside air. You will normalize the curve around whatever that is to meet the ARI design conditions, 67F maybe, I can't remember off the top of my head. There is a full set of equations for equipment under Curve-fit for HVAC Equipment, but I'<br>

<br><div class="gmail_quote"><div><div></div><div class="h5">On Wed, Feb 2, 2011 at 10:17 AM, Grando, John <span dir="ltr"><<a href="mailto:JGrando@cosentini.com" target="_blank">JGrando@cosentini.com</a>></span> wrote:<br>
</div></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div><div></div><div class="h5">







<div>
<font face="Arial, sans-serif" size="2">
<div>I'm basically trying to figure out how eQUEST comes up with the total Electric consumption for a DX coil.  I thought it was the below</div>
<div> </div>
<div>Total Capacity * Capacity Curve [T] * Total EIR * EIR Curve [T] * EIR Curve [PLR] but it's not coming out exactly the same.  Does anyone have any input for what I'm missing.  The attached .xls is an example for one day.  The total capacity is 79.983 kBTU/Hr
and the EIR is  0.2722.</div>
<div> </div>
<div> </div>
<div> </div>
<div><font size="3"> </font></div>
<div style="margin-top:5pt;margin-bottom:5pt"><font color="#0000FF"><div><b>John Grando</b><font color="#000000"><b> </b></font><b>LEED AP</b><font color="#000000"><b>| </b></font><font color="#808080"><b>Mechanical Engineer<br>



</b></font></div><font color="#808080">Phone: 212-615-3705 | Fax: 212-615-3700<br>

</font><a href="mailto:jgrando@cosentini.com" target="_blank">jgrando@cosentini.com</a><br>

<br>

<font color="#808080"><b>Cosentini Associates - A Tetra Tech Company<br>

</b></font><font color="#808080">Two Pennsylvania Plaza - Third Floor - New York, NY 10121<br>

</font><a href="http://www.cosentini.com/" target="_blank"><u>www.cosentini.com</u></a><br>

</font></div>
<div><font size="3"> </font></div>
<div><font size="3"> </font></div>
<div> </div>
</font><div>
<br clear="all"> NOTICE OF CONFIDENTIALITY

This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof.  In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law.  If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission.  Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege.  If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.
</div></div>


<br></div></div><div class="im">_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></div></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
</div>
</blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
</div>