Based on what you have said, I think I just need a new heating and cooling schedule.  I found them in my component tree, but I am not sure how to do what I want because the annual schedule only specifies an ending month and day.  How do I know when that schedule starts?<br>

<br><div class="gmail_quote">On Thu, Feb 3, 2011 at 9:24 PM, Nick Caton <span dir="ltr"><<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">











<div lang="EN-US" link="blue" vlink="purple">

<div>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Whoah buddy =)!</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">First, let me give the preface that I’ll be passing the 70hr
mark for this workweek tonight, so I’m kind of in zombie-mode right now
XD!</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Okay, I reckon you’re hunting rabbits with a  bazooka
by resorting to an absorption chiller/boiler setup to approximate your gas
furnace!  I’d go ahead and save your work in a separate file for
reference, then I’d step back to the wizards to try a packaged
single-zone furnace with DX cooling for your 2-story zone, and a single-zone
heatpump (DX/DX) for your garage.  Make the systems “on” 24hrs
with intermittent fan operation, and be sure you’re not specifying “system
per zone.”  Use the shell wizard to be sure the zones are assigned
to the right system.  </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">If you wish, you can restrict heating and cooling availability
for each system, the way a residential thermostat has “heating” and
“cooling” modes, with a COOLING-SCHEDULE and HEATING-SCHEDULE.  By
default, heating and cooling are generally available whenever they’re
called for, but you can edit that without going to a chiller/boiler system ;).</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">If you are finding your building is flip-flopping between
heating and cooling hour-to-hour in the dead of summer, it might be a sign other
items are off… check your envelope constructions/layers, and note that
oversimplifying geometries/spaces (i.e. – one per floor) may result in a
lot of thermal mass from partitions being excluded that would otherwise be a
stabilizing presence.</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">I’m copying the eQuest list, because I will be of little
use to you others in the next 24 hours…  Our strength is in numbers,
so do keep everyone in the loop as you work through this and you’ll get
the best chance of quality assistance - best of luck =)!</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Back to the grindstone…<br>
<br>
~Nick</span></p><div class="im">

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><img width="119" height="37" src="cid:image001.jpg@01CBC3E5.9443CEB0" alt="cid:489575314@22072009-0ABB"></span><b><span style="font-size:11.0pt;color:#2D4D5E"></span></b></p>



<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E"> </span></b></p>

<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E">NICK CATON, E.I.T.</span></b><b><span style="color:#2D4D5E"></span></b></p>

<p class="MsoNormal"><span style="font-size:7.5pt;color:#CC9900">PROJECT ENGINEER</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">Smith & Boucher Engineers</span><span style="font-size:7.5pt;color:#CC9900"></span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">25501 west valley parkway</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">olathe ks 66061</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">direct 913 344.0036</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">fax 913 345.0617</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size:10.0pt">www.smithboucher.com</span></a></span><u><span style="font-size:10.0pt;color:blue"> </span></u><span style="font-size:11.0pt;color:#1F497D"></span></p>



<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

</div><div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">

<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> Cory Duggin
[mailto:<a href="mailto:crduggin@gmail.com" target="_blank">crduggin@gmail.com</a>] <br>
<b>Sent:</b> Thursday, February 03, 2011 1:23 PM<br>
<b>To:</b> Nick Caton<br>
<b>Subject:</b> Re: [Equest-users] HVAC System Lockout</span></p>

</div><div><div></div><div class="h5">

<p class="MsoNormal"> </p>

<p class="MsoNormal" style="margin-bottom:12.0pt">I am modeling a two story house
with a one story garage that has been converted into a conditioned space.
 It is setup so there are 3 zones.  One in each floor of the two
story part and then the garage.  The real system in the house is one unit
for the two story part that has gas heat, and the garage has its own small heat
pump unit.  Since most people don't flip their thermostat back and forth
between heat and cool, I don't want my systems suddenly switching to heat for
an hour in the middle of summer because one of the zones got below set
point.  I have now changed the system to a chilled water loop and a hot
water loop.  Where the hot water is provided by a natural draft boiler and
the chilled water is provided by a single effect absorption chiller.  I am
trying to create a loads file that will have the load on the chiller rather
than the load on each coil for each zone and also the heating load for all the
zones, but I don't want it to be able to change from cooling to heating in the
cooling season or vice versa.  Does that makes sense?  Thanks</p>

<div>

<p class="MsoNormal">On Thu, Feb 3, 2011 at 11:19 AM, Nick Caton <<a href="mailto:ncaton@smithboucher.com" target="_blank">ncaton@smithboucher.com</a>> wrote:</p>

<div>

<div>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Cory, your query needs more description
to include what you’re trying to model and what you’ve input, but
if you’ve got simultaneous calls for heating and cooling being handled,
it sounds like you have either a multi-zone system or multiple systems
specified where you want only (1) single-zone system.  </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">If I were trying to model the behavior
of the HVAC in my apartment accurately (a simple CV electric furnace with DX
cooling controlled by a single remote thermostat), I’d group all
conditioned spaces and their zones under a single system, taking care to assign
the thermostat zone where the thermostat actually resides – it’s
the zone highlighted red in the graphic under the airside HVAC tab.</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">I’d suggest revisiting the
quantity and type of system you’ve specified first, and modify/reassign
your systems/zones as necessary to see if that’s where the problem
resides.  If you’re still having troubles, you’ll need to
provide a better description of what sort of system you’re trying to
model (layman’s terms are fine in this forum) and what you’ve tried
to specify on the model side.  Attaching your project’s .inp/.pd2
files may encourage others to help troubleshoot also ;).</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Best of luck!</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">~Nick</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><img border="0" width="119" height="37" src="cid:image001.jpg@01CBC3E5.9443CEB0" alt="cid:489575314@22072009-0ABB"></span></p>

<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E"> </span></b></p>

<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E">NICK CATON, E.I.T.</span></b></p>

<p class="MsoNormal"><span style="font-size:7.5pt;color:#CC9900">PROJECT ENGINEER</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">Smith & Boucher Engineers</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">25501 west valley parkway</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">olathe ks 66061</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">direct 913 344.0036</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">fax 913 345.0617</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size:10.0pt">www.smithboucher.com</span></a></span><u><span style="font-size:10.0pt;color:blue"> </span></u></p>



<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">

<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of
</b>Cory Duggin<br>
<b>Sent:</b> Wednesday, February 02, 2011 4:07 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] HVAC System Lockout</span></p>

</div>

<div>

<div>

<p class="MsoNormal"> </p>

<p class="MsoNormal">Is
there a way I can create a schedule to lockout either the heating or cooling
system based on the time of year?  I am modeling a residential system, so
I don't want it to try and satisfy heating a cooling loads simultaneously in
different zones.  Thanks<br clear="all">
<br>
-- <br>
Cory Duggin, EI<br>
Tennessee Tech University<br>
Graduate Research Assistant<br>
Mechanical Engineering</p>

</div>

</div>

</div>

</div>

</div>

<p class="MsoNormal"><br>
<br clear="all">
<br>
-- <br>
Cory Duggin, EI<br>
Tennessee Tech University<br>
Graduate Research Assistant<br>
Mechanical Engineering</p>

</div></div></div>

</div>


</blockquote></div><br><br clear="all"><br>-- <br>Cory Duggin, EI<br>Tennessee Tech University<br>Graduate Research Assistant<br>Mechanical Engineering<br>