There is an option when assigning your roof construction in the wizard to make the space be below a conditioned space, and therefore ambient.  I have used this option before and it works beautifully.  if you need more information or a screenshot of what i am talking about let me know.<div>
<br></div><div>Rob<br><br><div class="gmail_quote">2011/2/1 Ömer Moltay <span dir="ltr"><<a href="mailto:omoltay@mimtarch.com">omoltay@mimtarch.com</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
Dear All,<br>
<br>
We are encountering this problem all too often and would like to know if anybody has a satisfactory solution. For example, in a two storey building, the interior space configurations in each floor are considerably different, forcing us to create two separate shells that sit on top of each other in eQuest schematic wizard. However, when this is the case, eQuest treats each shell as a separate building and place exterior surfaces (ie. Roofs) between floors (instead of ceilings). The times it takes to manually convert these into interior surfaces with the right intra-space relationships is way out of reasonable limits.<br>

<br>
Is there a way to create a shell with floors that each have different interior layouts (even different exterior footprints for that matter)?<br>
<br>
Thanks,<br>
<br>
Omer Moltay, LEED AP<br>
Mimta Ltd.<br>
<br>
<br>
-----<br>
Bu iletide virüs bulunmadı.<br>
AVG tarafından kontrol edildi - <a href="http://www.avg.com" target="_blank">www.avg.com</a><br>
Sürüm: 10.0.1204 / Virüs Veritabanı: 1435/3416 - Sürüm Tarihi: 01.02.2011<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote></div><br><br clear="all"><br>-- <br>Rob Hudson<br>
</div>