It is my understanding that the loads are calculated based on the "Indoor Design Temperature" and not the setpoint temperature. You can generate hourly reports using the "Space" blocks in the hourly report blocks however you would need to make a separate block for each space. <br>
<br><div class="gmail_quote">On Thu, Jan 27, 2011 at 4:47 PM, Morrison, Andrew <span dir="ltr"><<a href="mailto:amorrison@haleyaldrich.com">amorrison@haleyaldrich.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div link="blue" vlink="purple" lang="EN-US"><div><p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Brian, </span></p><p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Thanks for that input. I have a follow-up question: I looked at the LS-B report and it has a note that says “The above loads are calculated assuming a constant indoor space temperature.” Is this temperature equal to the setpoint temperature of the space?</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p><p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Also, is there a counterpart to this report that outputs hourly values?</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p><p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Thanks</span></p><p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Drew</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p><div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;"> Brian Gregory [mailto:<a href="mailto:bgregory@dynamix-ltd.com" target="_blank">bgregory@dynamix-ltd.com</a>] <br><b>Sent:</b> Thursday, January 27, 2011 4:24 PM<br>
<b>To:</b> Morrison, Andrew<br><b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> Re: [Equest-users] HVAC Loads output question</span></p>
</div><p class="MsoNormal"> </p><p class="MsoNormal" style="margin-bottom: 12pt;">Drew,<br><br>I typically use the "LS-B Peak Load Components" report from the sim-output file for loads. </p><div><p class="MsoNormal">
On Thu, Jan 27, 2011 at 1:34 PM, Morrison, Andrew <<a href="mailto:amorrison@haleyaldrich.com" target="_blank">amorrison@haleyaldrich.com</a>> wrote:</p><div><div><p class="MsoNormal">Hi,</p><p class="MsoNormal"> </p>
<p class="MsoNormal">I’m modeling a 1940s-era apartment building for a geothermal retrofit. The current heating system consists of hot-water radiators supplied by gas-fired boilers. Cooling is supplied by window air conditioning units in each apartment. The ultimate objective is to generate building space heating and cooling loads to size a heat pump and ground heat exchanger – by space heating and cooling loads, I mean the total heat which has to be added or removed by the HVAC system to maintain all conditioned spaces at their set points.</p>
<p class="MsoNormal"> </p><p class="MsoNormal">Currently I’m generating hourly loads from the Building HVAC hourly report block using variables 1 & 2, entitled “Building cool load (coils + losses&gains)” and “Building heat load (coils + losses&gains)”. Are these the right variables to use, or do I need to look somewhere else?</p>
<p class="MsoNormal"> </p><p class="MsoNormal">Thanks,</p><p class="MsoNormal"> </p><p class="MsoNormal"> </p><p class="MsoNormal">Drew Morrison</p><p class="MsoNormal">Engineer</p><p class="MsoNormal"><b>Haley & Aldrich, Inc.</b></p>
<p class="MsoNormal">8899 Gander Creek Drive</p><p class="MsoNormal">Miamisburg, OH 45342-5432</p><p class="MsoNormal">Office: 937.530.1431</p><p class="MsoNormal">Cell: 937.307.2223</p><p class="MsoNormal"><a href="http://amorrison@haleyaldrich.com" target="_blank">amorrison@haleyaldrich.com</a></p>
<p class="MsoNormal"> </p></div></div><p class="MsoNormal" style="margin-bottom: 12pt;"><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p></div><p class="MsoNormal"><br><br clear="all">
<br>-- </p><p><b><span style="font-size: 22pt; color: rgb(192, 0, 0);">Dynamix</span></b></p><p><b><span style="color: black;">Engineering Ltd</span></b></p><p><b><span style="font-size: 13pt; color: black;">Brian Gregory</span></b></p>
<p><b><span style="color: black;">Mechanical Engineer                                                                            </span></b></p><p><span style="font-size: 10pt; color: black;">855 Grandview Ave., 3rd Floor    Columbus, OH 43215      </span></p>
<p class="MsoNormal"><b><span style="font-size: 10pt; color: rgb(33, 88, 104);">614-443-1178 ext. 278             </span></b><b><span style="font-size: 10pt; color: rgb(118, 146, 60);"><a href="http://www.dynamix-ltd.com/" target="_blank"><span style="color: rgb(118, 146, 60);">www.dynamix-ltd.com</span></a></span></b></p>
</div></div></blockquote></div><br><br clear="all"><br>-- <br><p><b><span style="font-size: 22pt; color: rgb(192, 0, 0);">Dynamix</span></b><b><span style="font-size: 22pt; color: rgb(31, 73, 125);"></span></b></p>
  <p><b><span style="color: black;">Engineering Ltd</span></b><span style="color: black;"></span></p>
  
  
  <p><b><span style="font-size: 13pt; color: black;">Brian Gregory</span></b><b><span style="font-size: 13pt; color: black;"></span></b></p>
  <p><b><span style="color: black;">Mechanical
  Engineer                                                                           
  </span></b><b><span style="color: black;"></span></b></p>
  <p><span style="font-size: 10pt; color: black;">855 Grandview Ave., 3rd Floor    Columbus, OH
  43215      </span><span style="font-size: 10pt; color: black;"></span></p>
  <b><span style="font-size: 10pt; color: rgb(33, 88, 104);">614-443-1178 ext.
  278             </span></b><b><span style="font-size: 10pt; color: rgb(118, 146, 60);"><a href="http://www.dynamix-ltd.com/" target="_blank"><span style="color: rgb(118, 146, 60);">www.dynamix-ltd.com</span></a></span></b><br>