Drew,<br><br>I typically use the "LS-B Peak Load Components" report from the sim-output file for loads. <br><br><div class="gmail_quote">On Thu, Jan 27, 2011 at 1:34 PM, Morrison, Andrew <span dir="ltr"><<a href="mailto:amorrison@haleyaldrich.com">amorrison@haleyaldrich.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;"><div link="blue" vlink="purple" lang="EN-US"><div><p class="MsoNormal">Hi,</p><p class="MsoNormal">
 </p><p class="MsoNormal">I’m modeling a 1940s-era apartment building for a geothermal retrofit. The current heating system consists of hot-water radiators supplied by gas-fired boilers. Cooling is supplied by window air conditioning units in each apartment. The ultimate objective is to generate building space heating and cooling loads to size a heat pump and ground heat exchanger – by space heating and cooling loads, I mean the total heat which has to be added or removed by the HVAC system to maintain all conditioned spaces at their set points.</p>
<p class="MsoNormal"> </p><p class="MsoNormal">Currently I’m generating hourly loads from the Building HVAC hourly report block using variables 1 & 2, entitled “Building cool load (coils + losses&gains)” and “Building heat load (coils + losses&gains)”. Are these the right variables to use, or do I need to look somewhere else?</p>
<p class="MsoNormal"> </p><p class="MsoNormal">Thanks,</p><p class="MsoNormal"> </p><p class="MsoNormal"> </p><p class="MsoNormal">Drew Morrison</p><p class="MsoNormal">Engineer</p><p class="MsoNormal"><b>Haley & Aldrich, Inc.</b></p>
<p class="MsoNormal">8899 Gander Creek Drive</p><p class="MsoNormal">Miamisburg, OH 45342-5432</p><p class="MsoNormal">Office: 937.530.1431</p><p class="MsoNormal">Cell: 937.307.2223</p><p class="MsoNormal"><a href="http://amorrison@haleyaldrich.com" target="_blank">amorrison@haleyaldrich.com</a></p>
<p class="MsoNormal"> </p></div></div><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br><p><b><span style="font-size: 22pt; color: rgb(192, 0, 0);">Dynamix</span></b><b><span style="font-size: 22pt; color: rgb(31, 73, 125);"></span></b></p>
  <p><b><span style="color: black;">Engineering Ltd</span></b><span style="color: black;"></span></p>
  
  
  <p><b><span style="font-size: 13pt; color: black;">Brian Gregory</span></b><b><span style="font-size: 13pt; color: black;"></span></b></p>
  <p><b><span style="color: black;">Mechanical
  Engineer                                                                           
  </span></b><b><span style="color: black;"></span></b></p>
  <p><span style="font-size: 10pt; color: black;">855 Grandview Ave., 3rd Floor    Columbus, OH
  43215      </span><span style="font-size: 10pt; color: black;"></span></p>
  <b><span style="font-size: 10pt; color: rgb(33, 88, 104);">614-443-1178 ext.
  278             </span></b><b><span style="font-size: 10pt; color: rgb(118, 146, 60);"><a href="http://www.dynamix-ltd.com/" target="_blank"><span style="color: rgb(118, 146, 60);">www.dynamix-ltd.com</span></a></span></b><br>