    With respect to your first point, you can have either a single loop
    pump, a chiller pump or both.  (this can be set up in the wizard or
    detailed interface -- obviously you are well into the detailed
    interface on this project.)<br>
    <br>
    For each chiller in eQUEST, one of the tabs is "loop attachments"
    where you can specify a chiller chilled water pump and a chiller
    condenser water pump which will then operate with the chiller.  Once
    you have defined the pumps there, you can delete the main loop pump.<br>
    <br>
    Note that I have found it helpful to save and then reopen and eQUEST
    file once water side changes have been made -- especially when you
    are reconfiguring loops and pumps.  Sometimes saving and reopening
    clears .bdl errors that would otherwise crop up.<br>
    <br>
    <br>
    With regard to your 2nd query, I have not had time to open your
    file.  You can change the loop "sizing option" from secondary (where
    it adds up all connected coil capacities) to primary (where it looks
    at capacity of primary equipment on the loop).  Perhaps this may
    resolve the issue.  Apologies if I missed the point on this one.<br>
    <br>
    <br>
    <br>
    <br>
    <br>
    On 1/24/2011 12:27 PM, Heinrich.ib-bauklima.de wrote:
    <blockquote
      cite="mid:0Lb8B7-1Q5BNe1JxR-00lAqf@mrelayeu.kundenserver.de"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta content="MSHTML 6.00.6000.17063" name="GENERATOR">
      <div><span class="890062716-21012011">
          <p class="MsoNormal"><font face="Arial"><span
                class="890062716-21012011">Hi </span>Everyone,<o:p></o:p></font></p>
          <p class="MsoNormal"><o:p><font face="Arial"><span
                  class="890062716-21012011"></span></font></o:p> </p>
          <p class="MsoNormal"><o:p><font face="Arial"><span
                  class="890062716-21012011">I got a review comment that
                  got me in big trouble and I can't find the solution
                  yet.</span></font></o:p></p>
          <p class="MsoNormal"><o:p><font face="Arial"><span
                  class="890062716-21012011">May be there is no solution
                  for this in eQUEST....!</span></font></o:p></p>
          <p class="MsoNormal"><o:p><font face="Arial"><span
                  class="890062716-21012011">I rate this forum as the
                  very best address for difficulties with eQUEST and
                  LEED EAc1 simulation.</span></font></o:p></p>
          <p class="MsoNormal"><o:p><font face="Arial"><span
                  class="890062716-21012011">So please give me some
                  guidance and feel free to test the model attached.</span></font></o:p></p>
          <p class="MsoNormal"><o:p><font face="Arial"><span
                  class="890062716-21012011"></span></font></o:p> </p>
          <p class="MsoNormal"><o:p><font face="Arial"><span
                  class="890062716-21012011">Here are the two comments
                  of the reviewer.</span></font></o:p></p>
          <p class="MsoNormal"><o:p><span class="890062716-21012011"><span
                  lang="DE"><font face="Arial"><em>"It appears as if the
                      pumps and circulation loops were not modeled
                      correctly for the Baseline Case. It appears based
                      on the PS-C reports that there is only one primary
                      chilled water pump and one condenser water pump
                      for the Baseline Case. However, ASHRAE 90.1
                      Section G3.1.11 requires that each chiller be
                      modeled with separate condenser water and chilled
                      water pumps interlocked to operate with each
                      associated chiller. Please model two primary
                      chilled water pumps and two primary condenser
                      water pumps in accordance with Section G3.1.11.
                      Also update the chilled water valves to two-way
                      valves so that the secondary chilled water loop
                      operates as a variable flow loop with pumps riding
                      the curve. Provide updated PS-C reports confirming
                      that the changes have been made."</em></font></span></span></o:p></p>
          <p><font face="Arial"><em><span class="890062716-21012011">"</span>It
                is unclear why the pump flow for the secondary chilled
                water loop is so much larger than that of the primary
                chilled water loop when the temperature differential for
                both loops is expected to be the same. It also appears
                based on the outputs in PS-C that the secondary chilled
                water loop is operated at the same load for every hour
                that it is on even though it is a variable speed pump.
                Please update the secondary chilled water loop flow to
                be consistent with the primary chilled water loop flow,
                and confirm that the secondary chilled water loop is
                operating as a variable flow loop.<span
                  class="890062716-21012011">"</span></em></font></p>
        </span>
        <p class="MsoNormal"><o:p><font face="Arial"><span
                class="890062716-21012011"></span></font></o:p> </p>
        <p class="MsoNormal"><o:p><font face="Arial"><span
                class="890062716-21012011">I have to say:</span></font></o:p></p>
        <p class="MsoNormal"><o:p><font face="Arial"><span
                class="890062716-21012011">I didn't see any equest-model
                modeled with separate condenser water and chilled water
                pumps interlocked to operate with each associated
                chiller. </span></font></o:p></p>
        <p class="MsoNormal"><o:p><font face="Arial"><span
                class="890062716-21012011">I manually resized the
                boilers and chillers with reference to SS-D report,
                because auto sizing of eQUEST generated capacities that
                were double the size of SS-D report. </span></font></o:p><o:p><font
              face="Arial"><span class="890062716-21012011">Resizing of
                the volume flow of secondary loop of chillers according
                to primary loop of chillers generated warning messages
                but changed nothing.</span></font></o:p></p>
        <p class="MsoNormal"><span class="890062716-21012011"><span
              class="890062716-21012011"><font face="Arial"><span
                  class="890062716-21012011"></span></font></span></span> </p>
        <p class="MsoNormal"><span class="890062716-21012011"><span
              class="890062716-21012011"><font face="Arial"><span
                  class="890062716-21012011">Heinrich</span></font></span></span></p>
      </div>
      <div>
        <div> </div>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <p class="avgcert" color="#000000" align="left">No virus found in
        this message.<br>
        Checked by AVG - <a moz-do-not-send="true"
          href="http://www.avg.com">www.avg.com</a><br>
        Version: 10.0.1202 / Virus Database: 1435/3400 - Release Date:
        01/24/11</p>
    </blockquote>
    <br>
  </body>
</html>