Hi Gregory,<br><br>It's hard to comment without seeing your .inp and .pd2 input files and without knowing exactly what reports you are looking at, e.g. SS-A, SV-A, BEPS, etc. My first thought, however, was to wonder if you are looking at a system report that doesn't include the ventilation load. Some eQUEST reports do and some do not. It would require investigation to determine whether that is the case and since, again, I don't know what exactly you're looking at, I'm not up for it. You might check the documentation about what's in reports, look on the DOE2 website or Google it, to see for yourself.<br>
<br>That's a start anyway.<br><br>Carol<br><br><div class="gmail_quote">On Fri, Jan 21, 2011 at 3:34 PM, Gregory Raffio <span dir="ltr"><<a href="mailto:graffio@gosustainableenergy.com">graffio@gosustainableenergy.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">Paul and the rest of the user group,<div><br></div><div>The attached presentation was a great tool to both confirm and improve our approach for modeling VRF.  I do have a follow-up question/problem that arose during the excel work (Slides 33 and 34 of the presentation). </div>


<div><br></div><div><u>Question:</u> Has anyone ever followed this approach and found out that the results from the hourly report are significantly different than the "monthly and annual energy consumption by enduse" reports that eQuest generates?</div>


<div><br></div><div><u>Step-by-step explanation of my process:</u></div><div>I created an hourly report exactly as in the presentation with the electric input to both heat and cool for every system in the facility along with an hourly report for the building as a whole. When I add up the heating energy and cooling energy of the individual systems, it equals the heating and cooling energy for the whole facility, so far so good.</div>


<div><br></div><div>Next, we looked at this heating and cooling energy and compared it to the "monthly and annual energy consumption by enduse" report that eQuest spits out. These numbers were not in agreement. For example, according to the hourly reports, the electricity used for space heating is 18,615 kWh while the space heating electricity in the "monthly energy consumption by enduse" report is 10,930 kWh. Big difference. </div>


<div><br></div><div>In some modeling programs (cough, Trace), I've seen heat pumps output the combination of their energy in either space heating or space cooling and not differentiate (which appears to be happening in eQuest as our space cooling energy is going up in the winter with the VRF system... and the building is definitely in a heating-dominated climate and has little internal space). The combination of the hourly report heating and cooling energy was 74,224 kWh and according to the "monthly energy consumption by enduse" report, the combination is 64,330 kWh. </div>


<div><br></div><div>I tried adding in the "HP Supp" energy  and some other uses from the "monthly energy consumption by enduse" report to no avail. I've had another eQuest user check my excel calculations and my hourly reports and they seem to be in good working order. </div>


<div><br></div><div>Any guesses, suggestions, strong reactions?</div><div><br></div><div><br></div><div><br></div><div><br><br><div class="gmail_quote"><div><div></div><div class="h5">On Tue, Oct 5, 2010 at 9:39 AM, Paul Diglio <span dir="ltr"><<a href="mailto:paul.diglio@sbcglobal.net" target="_blank">paul.diglio@sbcglobal.net</a>></span> wrote:<br>


</div></div><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;"><div><div></div><div class="h5"><div><div style="font-family: times new roman,new york,times,serif; font-size: 10pt;">
<div>Gary:<br><br>Please find attached file.<br>

<br>Paul Diglio<br></div><div style="font-family: times new roman,new york,times,serif; font-size: 10pt;"><br><div style="font-family: times new roman,new york,times,serif; font-size: 12pt;"><font size="2" face="Tahoma"><hr size="1">


<b><span style="font-weight: bold;">From:</span></b> "<a href="mailto:Gary.Schrader@buildings.schneider-electric.com" target="_blank">Gary.Schrader@buildings.schneider-electric.com</a>" <<a href="mailto:Gary.Schrader@buildings.schneider-electric.com" target="_blank">Gary.Schrader@buildings.schneider-electric.com</a>><div>


<br><b><span style="font-weight: bold;">To:</span></b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br></div><b><span style="font-weight: bold;">Sent:</span></b> Tue, October 5, 2010 9:06:28 AM<div>


<br><b><span style="font-weight: bold;">Subject:</span></b> [Equest-users] VRF/VRV PowerPoint on Modeling<br></div></font><div><div></div><div><br>



 
 

 

 

 

 

 

 

 

 





<div>

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">All,</span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">  </span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">At one time I recall seeing a PowerPoint presentation posted
to the ListServ about how to model VRV/VRF in eQuest. It took you through each
of the individual steps necessary to create a system.</span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">  </span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">In searching the archives, I believe that this file was
scrubbed. Does anybody have a copy of it to repost? My understanding is that it
was developed by a firm out on the west coast, perhaps
 Oregon .</span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">  </span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">Thanks,</span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">Gary</span></font></p> 

<p class="MsoNormal" style="margin-bottom: 12pt;"><font size="1" face="Arial"><span style="font-size: 8.5pt; font-family: Arial;"><br>
<font color="green"><span style="color: green;">_______________________________________________________________________________________________________________________</span></font></span></font></p> 

<p><b><font size="1" face="Arial"><span style="font-size: 8.5pt; font-family: Arial; font-weight: bold;">Gary Schrader</span></font></b><font size="1" face="Arial"><span style="font-size: 8.5pt; font-family: Arial;"> | <b><font color="green"><span style="color: green; font-weight: bold;">Schneider Electric </span></font></b>|
<b><span style="font-weight: bold;">Buildings Business</span></b> | <b><span style="font-weight: bold;">Energy Solutions </span></b>| <b><span style="font-weight: bold;">Engineer I</span></b><br>
<b><span style="font-weight: bold;">Phone:</span></b> +1 913 217 8068 | <b><span style="font-weight: bold;">Fax: </span></b>+1 913 469 0206<br>
<b><span style="font-weight: bold;">Email: </span></b><a rel="nofollow" href="Mailto:gary.schrader@buildings.schneider-electric.com" target="_blank">gary.schrader@buildings.schneider-electric.com</a>
| <b><span style="font-weight: bold;">Site: </span></b><a rel="nofollow" href="http://www.schneider-electric.com/buildings" target="_blank">www.schneider-electric.com/buildings</a>
| <b><span style="font-weight: bold;">Address: </span></b>
 16011 College Boulevard, Suite 212 , Lenexa ,
 KS 66219 ,
 USA<br>
<br>
<font color="green"><span style="color: green;">*** Please consider the environment
before printing this email.</span></font></span></font><font size="1" color="green" face="Arial"><span style="font-size: 8.5pt; font-family: Arial; color: green;"></span></font></p> 

<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="font-size: 12pt;">  </span></font></p> 

</div>

<br>
______________________________________________________________________<br>
This email has been scanned by the MessageLabs Email Security System.<br><span>
For more information please visit <a href="http://www.messagelabs.com/email" target="_blank">http://www.messagelabs.com/email</a> </span><br>
______________________________________________________________________<br>
</div></div></div></div>
</div></div><br></div></div>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Gregory Raffio, LEED AP BD+C<br>Go Sustainable Energy, LLC<br><a href="mailto:graffio@gosustainableenergy.com" target="_blank">graffio@gosustainableenergy.com</a><br>
Cell: 773-484-9610<br>

Skype: Gregory.Raffio<br><a href="http://www.gosustainableenergy.com/" target="_blank">http://www.gosustainableenergy.com/</a><br>
</div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; left: -5000px;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup{position: absolute;z-index: 9999;padding: 0px 0px;margin-left: 0px;margin-top: 0px;overflow: hidden;word-wrap: break-word;color: black;font-size: 10px;text-align: left;line-height: 130%;}</style>