Hi all,<br><br>I agree with all the strategies listed in these emails. HOWEVER, please do not pass by the article I attached again today, and will attach to this also. <br><br>This article was not written by me but rather by Steve Gates, the same guy that writes and maintains the HVAC portion of eQUEST. I was working with a client on chiller curves when the original Chiller Curves (Oh Boy!), thanks Nick, chain of emails began. There was something about the EDR article that bothered me and I talked to Steve about it. Steve, being nothing if not thorough, read the article and wrote the new article with some amendments and additions. <br>
<br>This article, the contents of the DOE2 Manuals and the EDR article should provide you with everything you need to create chiller curves. I would suggest reading all of them starting with everything in the DOE2 Manuals, moving on the the EDR article and finishing with the Chiller Curves SDG, etc., as it is, more or less, the final word.<br>
<br>Best,<br><br>Carol<br><br><div class="gmail_quote">On Wed, Jan 19, 2011 at 9:00 AM, Nick Caton <span dir="ltr"><<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div link="blue" vlink="purple" lang="EN-US">
<div>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Hi Afaan,</span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">The first table below contains
the <u>sort</u> of information you will need to make a centrifugal EIR curve,
but as David says you’re lacking in the minimum # of data points. I
believe the bare minimum to extrapolate an accurate bi-quadratic curve would require
9 rows of data (minimum 3 PLR’s for a minimum 3 dT’s), though you
should probably use the maximum number of data entry points permitted when
allowing eQuest to determine the coefficients (20 per curve). </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">dT is simply the difference
between the chilled and condenser water temps.</span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">I’m not sure exactly what
we’re looking at in the second table, but it doesn’t look like data
for creating a curve... If you want to make CAP-FT and EIR-FT curves (and
if you don’t, that’s okay too – see below) you’ll need
a rep who understands and can provide you with “maximum capacity” (not
the designed capacity, or where PLR = 1.0) and power drawn under different conditions.
I’ve previously selected 5 CW temps and 4 CHW temps around and
including the design conditions being normalized to, totaling the maximum 20
data entry points we’re permitted to input. </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">The attached email contains an
overview of materials you should review to understand the process of custom chiller
curve creation (includes a reference to the same EDR guideline David brings up below).
Once you feel comfortable understanding the required data collection described towards
the end of the referenced EDR chapter, you might do well to also read through a
fairly lengthy discussion on this list that I started: </span><span style="color: rgb(31, 73, 125);">“Chiller Curves (oh boy!).” </span><span style="color: rgb(31, 73, 125);"> There, I eventually provided an illustrated
breakdown of each default curve and its function/implications, eventually realizing
and providing visuals of their combined effects analogous to what equipment reps
often provide for “chiller efficiency curves.” You should be
able to follow this discussion from start to finish, and should come away
knowing exactly what eQuest is doing “under the hood” moving
forward. Carol Gardner also provided a writeup within that discussion
that is similar to the EDR… oh I see she just posted it again =)!</span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">One final suggestion: Your
collected data suggests a possible pitfall – if you want to make the CAP-FT
and EIR-FT curves, you MUST gather data for multiple CHW temps, even if the
design should only ever call for 44 degree water to be produced. If you don’t
understand why, then honestly you need further review of what the curves are functionally
doing – see suggested reading above and attached. </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">If you and your reps are struggling
with producing the data required to make CAP-FT and EIR-FT curves, it’s advisable
to stick with the defaults, and ensure your custom EIR-fPLR&dT curve
entries are all normalized to ARI rather than a design condition.</span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Best of luck!</span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">~Nick</span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
<div>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><img src="https://mail.google.com/mail/?ui=2&ik=367e06555b&view=att&th=12d9f390e5dcd509&attid=0.0.1&disp=emb&zw" alt="cid:489575314@22072009-0ABB" height="37" width="119"></span><b><span style="color: rgb(45, 77, 94);"></span></b></p>
<p class="MsoNormal"><b><span style="color: rgb(45, 77, 94);"> </span></b></p>
<p class="MsoNormal"><b><span style="color: rgb(45, 77, 94);">NICK CATON, E.I.T.</span></b><b><span style="font-size: 12pt; color: rgb(45, 77, 94);"></span></b></p>
<p class="MsoNormal"><span style="font-size: 7.5pt; color: rgb(204, 153, 0);">PROJECT ENGINEER</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">Smith &
Boucher Engineers</span><span style="font-size: 7.5pt; font-family: "Times New Roman","serif"; color: rgb(204, 153, 0);"></span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">25501 west
valley parkway</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">olathe ks 66061</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">direct 913
344.0036</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">fax 913
345.0617</span></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size: 10pt;">www.smithboucher.com</span></a></span><u><span style="font-size: 10pt; color: blue;"> </span></u><span style="color: rgb(31, 73, 125);"></span></p>
</div>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>
<div>
<div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>David
Eldridge<br>
<b>Sent:</b> Wednesday, January 19, 2011 7:38 AM<div class="im"><br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
</div><b>Subject:</b> Re: [Equest-users] Constructing chiller part load curves</span></p>
</div>
</div><div><div></div><div class="h5">
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="color: black;">You may want to run through this
document before you get too much further. Skip ahead to “Part
2” of the document.</span></p>
<p class="MsoNormal"><span style="color: black;"> </span></p>
<p class="MsoNormal"><a href="http://www.energydesignresources.com/media/2654/EDR_DesignGuidelines_%20HVAC_Simulation.pdf" target="_blank">http://www.energydesignresources.com/media/2654/EDR_DesignGuidelines_%20HVAC_Simulation.pdf</a></p>
<p class="MsoNormal"><span style="color: black;"> </span></p>
<p class="MsoNormal"><span style="color: black;">In a nutshell – you should
acquire a few more data points to develop a more comprehensive matrix.
Right now your matrix would be equivalent to a line through the middle of
possible conditions, you need to extend your data set over a wider range of
water temperatures and load conditions.</span></p>
<p class="MsoNormal"><span style="color: black;"> </span></p>
<p class="MsoNormal"><span style="color: black;">David</span></p>
<p class="MsoNormal"><span style="color: black;"> </span></p>
<div>
<p class="MsoNormal"><u><span style="color: black;">
</span></u></p>
<p class="MsoNormal"><span style="font-size: 8pt; color: black;"> </span></p>
<p class="MsoNormal"><b><span style="color: rgb(31, 73, 125);">David S. Eldridge, Jr.</span><span style="color: rgb(36, 64, 97);">, P</span><span style="color: rgb(31, 73, 125);">.</span><span style="color: rgb(36, 64, 97);">E</span><span style="color: rgb(31, 73, 125);">.</span><span style="color: rgb(36, 64, 97);">, LEED AP BD+C, BEMP, HBDP</span></b></p>
<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Project Manager</span></p>
<p class="MsoNormal"><span style="font-size: 4pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="color: rgb(54, 95, 145);">Direct: (847) 316-92</span><span style="color: rgb(31, 73, 125);">24</span><span style="color: rgb(54, 95, 145);"> | Fax: (</span><span style="color: rgb(31, 73, 125);">847</span><span style="color: rgb(54, 95, 145);">) </span><span style="color: rgb(31, 73, 125);">328</span><span style="color: rgb(54, 95, 145);">-</span><span style="color: rgb(31, 73, 125);">4550</span></p>
<p class="MsoNormal"><span style="color: black;"><a href="http://www.grummanbutkus.com" target="_blank">http://www.grummanbutkus.com</a></span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><b><span style="color: rgb(36, 64, 97);">Grumman/Butkus Associates</span></b><span style="color: gray;"> </span><span style="color: rgb(54, 95, 145);">| 820 Davis Street,
Suite 300 | Evanston, IL 60201</span></p>
<p class="MsoNormal"><span style="font-size: 9pt; color: gray;">Energy Efficiency
Consultants and Sustainable Design Engineers</span></p>
<p class="MsoNormal"><u><span style="color: black;">
</span></u></p>
</div>
<p class="MsoNormal"><span style="color: black;"> </span></p>
<div style="border-width: medium medium medium 1.5pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color blue; padding: 0in 0in 0in 4pt;">
<div>
<div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Afaan Naqvi<br>
<b>Sent:</b> Tuesday, January 18, 2011 8:33 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Constructing chiller part load curves</span></p>
</div>
</div>
<p class="MsoNormal"> </p>
<p class="MsoNormal">After browsing the forums, it seems there are many users
that have constructed custom chiller curves based on selection data. I believe
I have all the data I need to do this, but am coming up with polynomial
coefficients and hourly results that do not make sense at all. Can someone
please walk me through how to go about building the 3 curves for a centrifugal,
water cooled chiller with a VSD based on the following data:</p>
<p class="MsoNormal"> </p>
<table style="width: 485pt; border-collapse: collapse;" border="0" cellpadding="0" cellspacing="0" width="647">
<tbody><tr style="min-height: 13.2pt;">
<td style="width: 48pt; border: 1pt solid windowtext; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">% Load</span></p>
</td>
<td style="width: 68pt; border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="91">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">Capacity</span></p>
</td>
<td style="width: 48pt; border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">kW in</span></p>
</td>
<td style="width: 48pt; border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">Perf</span></p>
</td>
<td style="width: 65pt; border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="87">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">Evap T in</span></p>
</td>
<td style="width: 1in; border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="96">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">Evap T out</span></p>
</td>
<td style="width: 69.75pt; border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="93">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">Conden T in</span></p>
</td>
<td style="width: 66.25pt; border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="88">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">Coned T out</span></p>
</td>
</tr>
<tr style="min-height: 13.2pt;">
<td style="width: 48pt; border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">100</span></p>
</td>
<td style="width: 68pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="91">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">85</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">53.6</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">0.63</span></p>
</td>
<td style="width: 65pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="87">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">54</span></p>
</td>
<td style="width: 1in; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="96">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">44</span></p>
</td>
<td style="width: 69.75pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="93">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">85</span></p>
</td>
<td style="width: 66.25pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="88">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">94.8</span></p>
</td>
</tr>
<tr style="min-height: 13.2pt;">
<td style="width: 48pt; border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">75</span></p>
</td>
<td style="width: 68pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="91">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">63.8</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">29.8</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">0.47</span></p>
</td>
<td style="width: 65pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="87">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">51.5</span></p>
</td>
<td style="width: 1in; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="96">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">44</span></p>
</td>
<td style="width: 69.75pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="93">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">75</span></p>
</td>
<td style="width: 66.25pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="88">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">82</span></p>
</td>
</tr>
<tr style="min-height: 13.2pt;">
<td style="width: 48pt; border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">50</span></p>
</td>
<td style="width: 68pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="91">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">42.5</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">13.3</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">0.31</span></p>
</td>
<td style="width: 65pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="87">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">49</span></p>
</td>
<td style="width: 1in; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="96">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">44</span></p>
</td>
<td style="width: 69.75pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="93">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">65</span></p>
</td>
<td style="width: 66.25pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="88">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">69.5</span></p>
</td>
</tr>
<tr style="min-height: 13.2pt;">
<td style="width: 48pt; border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">25</span></p>
</td>
<td style="width: 68pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="91">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">21.3</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">6.9</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">0.32</span></p>
</td>
<td style="width: 65pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="87">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">46.5</span></p>
</td>
<td style="width: 1in; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="96">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">44</span></p>
</td>
<td style="width: 69.75pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="93">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">65</span></p>
</td>
<td style="width: 66.25pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" nowrap width="88">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">67.2</span></p>
</td>
</tr>
</tbody></table>
<p class="MsoNormal"> </p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">I believe the additional data I need is calculated below,
except for the dT term which I am unclear on:</p>
<p class="MsoNormal"> </p>
<table style="width: 212pt; border-collapse: collapse;" border="0" cellpadding="0" cellspacing="0" width="283">
<tbody><tr style="min-height: 13.2pt;">
<td style="width: 48pt; border: 1pt solid windowtext; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">Load</span></p>
</td>
<td style="width: 68pt; border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="91">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">PLR</span></p>
</td>
<td style="width: 48pt; border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">kW</span></p>
</td>
<td style="width: 48pt; border-width: 1pt 1pt 1pt medium; border-style: solid solid solid none; border-color: windowtext windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">f PLR</span></p>
</td>
</tr>
<tr style="min-height: 13.2pt;">
<td style="width: 48pt; border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">85</span></p>
</td>
<td style="width: 68pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="91">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">1</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">53.6</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">1</span></p>
</td>
</tr>
<tr style="min-height: 13.2pt;">
<td style="width: 48pt; border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">63.8</span></p>
</td>
<td style="width: 68pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="91">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">0.751</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">29.8</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">0.556</span></p>
</td>
</tr>
<tr style="min-height: 13.2pt;">
<td style="width: 48pt; border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">42.5</span></p>
</td>
<td style="width: 68pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="91">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">0.500</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">13.3</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">0.248</span></p>
</td>
</tr>
<tr style="min-height: 13.2pt;">
<td style="width: 48pt; border-width: medium 1pt 1pt; border-style: none solid solid; border-color: -moz-use-text-color windowtext windowtext; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">21.3</span></p>
</td>
<td style="width: 68pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="91">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">0.251</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">6.9</span></p>
</td>
<td style="width: 48pt; border-width: medium 1pt 1pt medium; border-style: none solid solid none; border-color: -moz-use-text-color windowtext windowtext -moz-use-text-color; padding: 0in 5.4pt; min-height: 13.2pt;" width="64">
<p class="MsoNormal" style="text-align: center;" align="center"><span style="font-size: 10pt;">0.129</span></p>
</td>
</tr>
</tbody></table>
<p class="MsoNormal"> </p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Not sure if the dT term required by the curves is the
difference in condenser supply and return, or condenser and evaporator supply,
condenser supply and evaporator return, etc. Can someone please clarify?</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Thanks</p>
<p class="MsoNormal"><span style="font-family: "Times New Roman","serif";"> </span></p>
<p class="MsoNormal"><span style="font-family: "Times New Roman","serif";"> </span></p>
<p class="MsoNormal"><b><span style="font-family: "Times New Roman","serif"; color: rgb(40, 170, 225);">Afaan Naqvi </span></b><b><span style="font-family: "Times New Roman","serif"; color: gray;"> </span></b><span style="font-size: 10pt; font-family: "Times New Roman","serif"; color: gray;">PE LEED AP</span></p>
<p class="MsoNormal"><span style="font-size: 12pt; font-family: "Courier New";">____________________________________________________________<br>
Electronic mail messages entering and leaving Arup business<br>
systems are scanned for acceptability of content and viruses</span></p>
</div>
</div></div></div>
</div>
<br><br>---------- Forwarded message ----------<br>From: "Nick Caton" <<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>><br>To: "Grammy" <<a href="mailto:grammy.hkust@gmail.com">grammy.hkust@gmail.com</a>>, "Ana N." <<a href="mailto:ananeddav@hotmail.com">ananeddav@hotmail.com</a>><br>
Date: Fri, 5 Nov 2010 09:12:24 -0600<br>Subject: Re: [Equest-users] Electricity consumption by CHILLER<br>
<div link="blue" vlink="purple" lang="EN-US">
<div>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Ana/Grammy:</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Chiller modeling is a topic that took me many attempts (projects)
to fully get my arms around, so don’t get discouraged if it boggles the
mind.</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">To start, remember that the reported “space cooling”
end use consumption values may include energy from components other than your
chiller (heat pumps, DX cooling…), so make sure that’s not clouding
your perspective.</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">With that out of the way, you’re right to first check and
ensure the loads on the loop are appropriate to what you’re trying to
model. I think you should review what CAP</span><span style="font-size: 10pt; color: rgb(31, 73, 125);">hour</span><span style="font-size: 11pt; color: rgb(31, 73, 125);"> and PLR
really represent… Multiplying them should result in your hourly
load, in Btuh, but if you’re multiplying your “</span><span style="font-size: 10pt;">operating chiller
capacity at current condition</span><span style="font-size: 11pt; color: rgb(31, 73, 125);">” (Hourly Load) by your PLR then I
suspect the result would be equal to “PLR^2/CAP</span><span style="font-size: 10pt; color: rgb(31, 73, 125);">hour.</span><span style="font-size: 11pt; color: rgb(31, 73, 125);">”
I’m doubtful that’s the value you were looking for… Let
me suggest two paths to account for what you’re trying to do:</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><u><span style="font-size: 11pt; color: rgb(31, 73, 125);">If you are working with the library performance curves</span></u><span style="font-size: 11pt; color: rgb(31, 73, 125);">,
recognize you have a limited number of critical inputs to review/edit regarding
the behavior of the chiller itself: Capacity (a part of CAP</span><span style="font-size: 10pt; color: rgb(31, 73, 125);">hour</span><span style="font-size: 11pt; color: rgb(31, 73, 125);">) and
EIR at the design/rated conditions, the design conditions themselves, and the
associated loop temperatures. If any input on the chiller screens is
something you’re unsure of, right-click it and read/re-read the
associated help entry.</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><u><span style="font-size: 11pt; color: rgb(31, 73, 125);">If you want to delve into custom performance curves</span></u><span style="font-size: 11pt; color: rgb(31, 73, 125);">, welcome
to the rabbit hole! This required significant personal learning and time
for me to get my arms around, I would suggest expecting the same. I’d
suggest first getting comfortable specifying chillers using the library curves,
per above before pursuing this skillset. </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Still here? Okay, the following 3-step program is what I
wish I could go back in time and tell myself months ago:</span></p>
<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"><span>1.<span style="font: 7pt "Times New Roman";">
</span></span></span><span style="font-size: 11pt; color: rgb(31, 73, 125);">Open the DOE2 help files to Volume 2: Dictionary > HVAC
Components > Chiller. Read everything in the tree in order up to the “Attachment
to Chilled Water Loop” entry, and stop. Pay special attention to
the “Chiller Energy Consumption” article and the sub-entries
describing each performance curve in that equation. When you’re
familiar enough to recount all the variables involved in that equation you
brought up below by memory, proceed to…</span></p>
<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"><span>2.<span style="font: 7pt "Times New Roman";">
</span></span></span><span style="font-size: 11pt; color: rgb(31, 73, 125);">Download the <a href="http://www.energydesignresources.com/Portals/0/documents/DesignGuidelines/EDR_DesignGuidelines_%20HVAC_Simulation.pdf" target="_blank">EDR
design guidelines to HVAC simulation</a>, and read the chapter on chillers,
pages 23-44 (of 65). </span></p>
<p style="margin-left: 1in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);"><span>a.<span style="font: 7pt "Times New Roman";"> </span></span></span><span style="font-size: 11pt; color: rgb(31, 73, 125);">Re-read
until you feel comfortable understanding what information you need from your
manufacturer rep/vendor. A good rep is always trying to be helpful, and may
unintentionally provide the wrong information and convince you both you’re
on solid footing. You must know exactly what data you do and don’t
need before beginning the discussion of asking for that information.
Whether your vendor/rep can deliver exactly what you want is something of a
toss-up, but it’s a pretty slim chance if you don’t know what that
is yourself.</span></p>
<p style="margin-left: 1in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);"><span>b.<span style="font: 7pt "Times New Roman";"> </span></span></span><span style="font-size: 11pt; color: rgb(31, 73, 125);">The equations
presented showing the math behind the coefficients may seem insurmountable, but
for context recognize the author(s) of this document advocating to not figure
out the coefficients directly… rather to let eQuest/DOE2 do that legwork
for you (the “data method”). To an extent this is something
of a reference regarding what’s going on “under the hood.”</span></p>
<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"><span>3.<span style="font: 7pt "Times New Roman";">
</span></span></span><span style="font-size: 11pt; color: rgb(31, 73, 125);">Read the lengthy discussion I started this week (with
illustrations) under the heading “Chiller Curves (oh boy!).”
This hopefully also bring you full circle to understanding what the default curves
really look like, what they each individually represent, and ultimately how
they work together. Note my discussion revolved around a centrifugal VSD
chiller, for context. Other equipment may use curves of a simpler format.</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">*If a “bi-quadratic equation” sounds like something that
makes the warp drives work on the Star Ship Enterprise, stop for a second and
review the math – it’s not that crazy. You might want to skip
ahead to see to those visualizations I provided, or even build your own in
excel. </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Best of luck!</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">~Nick</span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"><img src="https://mail.google.com/mail/?ui=2&ik=367e06555b&view=att&th=12d9f390e5dcd509&attid=0.1.0.0.1&disp=emb&zw" alt="cid:489575314@22072009-0ABB" border="0" height="37" width="119"></span><b><span style="font-size: 11pt; color: rgb(45, 77, 94);"></span></b></p>
<p class="MsoNormal"><b><span style="font-size: 11pt; color: rgb(45, 77, 94);"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size: 11pt; color: rgb(45, 77, 94);">NICK CATON, E.I.T.</span></b><b><span style="color: rgb(45, 77, 94);"></span></b></p>
<p class="MsoNormal"><span style="font-size: 7.5pt; color: rgb(204, 153, 0);">PROJECT ENGINEER</span><span style="font-size: 7.5pt; color: rgb(204, 153, 0);"></span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">25501 west valley parkway</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">olathe ks 66061</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">direct 913 344.0036</span></p>
<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">fax 913 345.0617</span></p>
<p class="MsoNormal"><i><span style="font-size: 10pt; color: rgb(45, 77, 94);">Check out our new web-site @ </span></i><span style="font-size: 11pt; color: rgb(31, 73, 125);"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size: 10pt;">www.smithboucher.com</span></a></span><u><span style="font-size: 10pt; color: blue;"> </span></u><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>
<div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Grammy<br>
<b>Sent:</b> Friday, November 05, 2010 6:17 AM<br>
<b>To:</b> Ana N.<br>
<b>Cc:</b> equest-users<br>
<b>Subject:</b> Re: [Equest-users] Electricity consumption by CHILLER</span></p>
</div>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="font-family: "Comic Sans MS";">I am also
confusing this problem, and I strongly recommend you to read the
DOE-2 engineering manual, verison 2.1A, and DOE-2.2 volume 4, which can be
downloaded from eQuest web site.</span></p>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal"><span>On page V.35
- V.38, engineering manual, it introduces the electric calculation of chiller,
and on page 265, volume4, it introduces the chiller variable list number, you
can export the hourly data in eQuest and calculated by hand. I am lost at this
step. As i know at this place, there is something you need to notice, the unit
of assign loading (1) shall be BTU, and electric demand (12) may be kW, then I
still can't get the right number, if you get it, please let me know how.</span></p>
<div>
<p class="MsoNormal" style="margin-bottom: 12pt;"> </p>
<div>
<p class="MsoNormal">On Fri, Nov 5, 2010 at 8:04 AM, Ana N. <<a href="mailto:ananeddav@hotmail.com" target="_blank">ananeddav@hotmail.com</a>>
wrote:</p>
<div>
<p class="MsoNormal"> <br>
<span style="font-size: 10pt;">I am trying to
calculate/estimate the electricity consumption by a chiller based
on hourly outputs. </span><br>
<span style="font-size: 10pt;"> </span><br>
<span style="font-size: 10pt;">First,
I plugged the cooling coil load on loop and corrected EIR in the the
equitation </span><br>
<span style="font-size: 10pt;"> Elec=
CAP hour* EIR*EIR(t1,t2)*EIR(PLR,dT)/3413 Btu/kW</span><br>
<span style="font-size: 10pt;"> </span><br>
<span style="font-size: 10pt;">but the
calculated annual electricity consumption was not even close to the
numbers reported under Space Cooling Enduse.</span><br>
<span style="font-size: 10pt;"> </span><br>
<span style="font-size: 10pt;">Then, I used
PLR and operating chiller capacity at current condition to calculate CAP
hour (instead of using the cooling coil load on loop), but calculated
numbers did not make any sense.</span><br>
<span style="font-size: 10pt;"> </span><br>
<span style="font-size: 10pt;">Has anyone
done similar calculations? I am sure I am missing something very simple
here, but what?</span><br>
<span style="font-size: 10pt;"> </span><br>
<span style="font-size: 10pt;">Any
suggestions are very appreciated</span><br>
<span style="font-size: 10pt;"> </span><br>
<span style="font-size: 10pt;"> </span><br>
<span style="font-size: 10pt;">Ana</span><br>
<span style="font-size: 10pt;"> </span></p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"> </p>
</div>
<p class="MsoNormal" style="margin-bottom: 12pt;"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>
</div>
<p class="MsoNormal"> </p>
</div>
</div>
</div>
</div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; left: -5000px;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup{position: absolute;z-index: 9999;padding: 0px 0px;margin-left: 0px;margin-top: 0px;overflow: hidden;word-wrap: break-word;color: black;font-size: 10px;text-align: left;line-height: 130%;}</style>