<font size="+1"> It is a small difference, basically negligible. I
switched a recent project I did with aluminum spacers to insulated
in the windows only. The LV-D report showed no difference, that
could be because it reports the window U-value. The LS-C report
showed a small difference in the Window Glass + Frame, 19.500
kBTU/h for the aluminum, </font><font size="+1">out of a building
total 194.197 </font><font size="+1">kBTU/h,</font><font
size="+1"> 19.413 kBTU/h for the insulated, total 194.109 </font><font
size="+1">kBTU/h.<br>
The building had 173 SF of windows in 14,492 SF of wall and 768
SF of skylights in 7,616 SF of roof, a small percentage. Also,
most of the windows were 2'W x 5'H, 10 SF, if the edge effect is
1" around the frame that is 1.15 SF, 11%, or 19 SF of 173 SF glass
in 14,492 sf of wall. If your edge effect is R-1 in aluminum and
R-3 in insulated in a R-20 wall it becomes a very minor heat
loss. In an all glass building it would be the nearly the same
except if you spent some money on glass you might have 14,492 SF
at R-4. The edge effect would still only apply to 19 SF.<br>
The main effect as I mentioned earlier is to allow higher
humidity levels in the winter in a cold climate without damaging
surfaces below the window with condensation. It shows that
windows suck when it comes to insulating, edge effect or not.
Residentially it has a big effect, by spending an extra $12 on a
$400 window you get an insulated spacer and argon fill, taking
your glass from R-2 to R-4.2 but the wood frame will last 20 years
instead of 5 or 8 because the condensation won't rot out the
bottom of the frame. Installation is more important, if you have
a 1/16" gap around the window frame you just put in a R-4 window
and a 3.24" square hole in your R-20 wall.<br>
Bruce Easterbrook P.Eng.<br>
Abode Engineering<br>
</font><font size="+1"><br>
</font><font size="+1"><br>
</font><br>
On 05/01/2011 02:41 PM, Alex Krickx wrote:
<blockquote
cite="mid:B8B836A09111F041A16C8A3690FB3563C3340C0CA5@EXVMBX015-6.exch015.msoutlookonline.net"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=ISO-8859-1">
<meta name="Generator" content="Microsoft Word 12 (filtered
medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
<style><!--
/* Font Definitions */
@font-face
{font-family:Cambria;
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:Consolas;
panose-1:2 11 6 9 2 2 4 3 2 4;}
@font-face
{font-family:Webdings;
panose-1:5 3 1 2 1 5 9 6 7 3;}
@font-face
{font-family:"Franklin Gothic Medium Cond";}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman","serif";}
h5
{mso-style-priority:9;
mso-style-link:"Heading 5 Char";
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:10.0pt;
font-family:"Times New Roman","serif";
font-weight:bold;}
p.MsoBodyText, li.MsoBodyText, div.MsoBodyText
{mso-style-priority:99;
mso-style-link:"Body Text Char";
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p
{mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";}
pre
{mso-style-priority:99;
mso-style-link:"HTML Preformatted Char";
margin:0in;
margin-bottom:.0001pt;
font-size:10.0pt;
font-family:"Courier New";}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{mso-style-priority:99;
mso-style-link:"Balloon Text Char";
margin:0in;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma","sans-serif";}
span.Heading5Char
{mso-style-name:"Heading 5 Char";
mso-style-priority:9;
mso-style-link:"Heading 5";
font-family:"Cambria","serif";
color:#243F60;}
span.HTMLPreformattedChar
{mso-style-name:"HTML Preformatted Char";
mso-style-priority:99;
mso-style-link:"HTML Preformatted";
font-family:Consolas;}
span.BodyTextChar
{mso-style-name:"Body Text Char";
mso-style-priority:99;
mso-style-link:"Body Text";}
span.BalloonTextChar
{mso-style-name:"Balloon Text Char";
mso-style-priority:99;
mso-style-link:"Balloon Text";
font-family:"Tahoma","sans-serif";}
p.ecxmsonormal, li.ecxmsonormal, div.ecxmsonormal
{mso-style-name:ecxmsonormal;
mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";}
p.ecxmsolistnumber, li.ecxmsolistnumber, div.ecxmsolistnumber
{mso-style-name:ecxmsolistnumber;
mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";}
p.ecxmsobodytext, li.ecxmsobodytext, div.ecxmsobodytext
{mso-style-name:ecxmsobodytext;
mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";}
p.ecxmsoacetate, li.ecxmsoacetate, div.ecxmsoacetate
{mso-style-name:ecxmsoacetate;
mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";}
p.ecxmsonormal1, li.ecxmsonormal1, div.ecxmsonormal1
{mso-style-name:ecxmsonormal1;
mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
margin-bottom:0in;
margin-left:0in;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Arial","sans-serif";}
p.ecxmsolistnumber1, li.ecxmsolistnumber1, div.ecxmsolistnumber1
{mso-style-name:ecxmsolistnumber1;
mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";}
p.ecxmsobodytext1, li.ecxmsobodytext1, div.ecxmsobodytext1
{mso-style-name:ecxmsobodytext1;
mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";}
p.ecxmsoacetate1, li.ecxmsoacetate1, div.ecxmsoacetate1
{mso-style-name:ecxmsoacetate1;
mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
margin-bottom:0in;
margin-left:0in;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Arial","sans-serif";}
p.msochpdefault, li.msochpdefault, div.msochpdefault
{mso-style-name:msochpdefault;
mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:10.0pt;
font-family:"Times New Roman","serif";}
p.codeword, li.codeword, div.codeword
{mso-style-name:codeword;
mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";}
span.heading5char0
{mso-style-name:heading5char;
font-family:"Times New Roman","serif";
color:#243F60;}
span.ecxmsohyperlink1
{mso-style-name:ecxmsohyperlink1;
color:blue;
text-decoration:underline;}
span.ecxmsohyperlinkfollowed1
{mso-style-name:ecxmsohyperlinkfollowed1;
color:purple;
text-decoration:underline;}
span.ecxemailstyle171
{mso-style-name:ecxemailstyle171;
font-family:"Arial","sans-serif";
color:windowtext;}
span.ecxheading5char1
{mso-style-name:ecxheading5char1;
font-family:"Times New Roman","serif";
font-weight:bold;}
span.ecxbodytextchar1
{mso-style-name:ecxbodytextchar1;
font-family:"Times New Roman","serif";}
span.ecxballoontextchar1
{mso-style-name:ecxballoontextchar1;
font-family:"Arial","sans-serif";}
span.htmlpreformattedchar0
{mso-style-name:htmlpreformattedchar;
font-family:Consolas;}
span.emailstyle41
{mso-style-name:emailstyle41;
font-family:"Arial","sans-serif";
color:#1F497D;}
span.EmailStyle44
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle45
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle46
{mso-style-type:personal;
font-family:"Arial","sans-serif";
color:navy;}
span.EmailStyle47
{mso-style-type:personal-reply;
font-family:"Calibri","sans-serif";
color:#1F497D;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="2050" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">Hi Bill,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">I actually don’t have any skylights, only
windows. I was asking about “Curb” because I saw it in the
report and I thought it might be the edge-of-glass
performance I was looking for (I was corrected by the
list-serv).<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">I changed the Spacer-Type for the windows in my
model and didn’t see any changes…<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">Thanks,<br>
Alex<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<div>
<div style="border-right: medium none; border-width: 1pt
medium medium; border-style: solid none none; border-color:
rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color;
padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><span style="font-size: 10pt;
font-family:
"Tahoma","sans-serif";">From:</span></b><span
style="font-size: 10pt; font-family:
"Tahoma","sans-serif";"> Bishop,
Bill [<a class="moz-txt-link-freetext" href="mailto:wbishop@pathfinder-ea.com">mailto:wbishop@pathfinder-ea.com</a>] <br>
<b>Sent:</b> Wednesday, January 05, 2011 11:39 AM<br>
<b>To:</b> Alex Krickx<br>
<b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> RE: [Equest-users] Window "Curb"<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt; font-family:
"Arial","sans-serif"; color: navy;">Alex,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 10pt; font-family:
"Arial","sans-serif"; color: navy;">One
idea - does the roof surface with the skylight belong to a
plenum, or unconditioned space? Building coincident peak
loads shown on LS-C do not include plenums or unconditioned
spaces.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 10pt; font-family:
"Arial","sans-serif"; color: navy;">Regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 10pt; font-family:
"Arial","sans-serif"; color: navy;">Bill<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 10pt; font-family:
"Arial","sans-serif"; color: navy;"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><b><span style="font-size: 10pt;
font-family: "Franklin Gothic Medium
Cond","sans-serif"; color: black;">William
Bishop, PE, BEMP, LEED<sup>®</sup> AP </span></b><b><span
style="font-size: 10pt; font-family: "Franklin
Gothic Medium Cond","sans-serif"; color:
rgb(0, 102, 0);">|</span></b><b><span style="font-size:
10pt; font-family: "Franklin Gothic Medium
Cond","sans-serif"; color: black;"> </span></b><b><span
style="font-size: 10pt; font-family: "Franklin
Gothic Medium Cond","sans-serif"; color:
black;">Pathfinder Engineers & Architects LLP</span></b><b><span
style="font-size: 10pt; font-family: "Franklin
Gothic Medium Cond","sans-serif"; color:
black;"><o:p></o:p></span></b></p>
<p class="MsoNormal"><span style="font-size: 9pt; font-family:
"Arial","sans-serif"; color: black;">Mechanical
Engineer<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 5pt; font-family:
"Arial","sans-serif"; color: black;"><o:p> </o:p></span></p>
<p class="MsoNormal"><!--[if gte vml 1]><v:shapetype id="_x0000_t75" coordsize="21600,21600" o:spt="75" o:preferrelative="t" path="m@4@5l@4@11@9@11@9@5xe" filled="f" stroked="f">
<v:stroke joinstyle="miter" />
<v:formulas>
<v:f eqn="if lineDrawn pixelLineWidth 0" />
<v:f eqn="sum @0 1 0" />
<v:f eqn="sum 0 0 @1" />
<v:f eqn="prod @2 1 2" />
<v:f eqn="prod @3 21600 pixelWidth" />
<v:f eqn="prod @3 21600 pixelHeight" />
<v:f eqn="sum @0 0 1" />
<v:f eqn="prod @6 1 2" />
<v:f eqn="prod @7 21600 pixelWidth" />
<v:f eqn="sum @8 21600 0" />
<v:f eqn="prod @7 21600 pixelHeight" />
<v:f eqn="sum @10 21600 0" />
</v:formulas>
<v:path o:extrusionok="f" gradientshapeok="t" o:connecttype="rect" />
<o:lock v:ext="edit" aspectratio="t" />
</v:shapetype><v:shape id="_x0000_s1026" type="#_x0000_t75" style='position:absolute;margin-left:275.35pt;margin-top:12.75pt;width:45.2pt;height:43.55pt;z-index:-1'>
<v:imagedata src="mailbox:///C|/Documents%20and%20Settings/Bruce/Application%20Data/Thunderbird/Profiles/0444ln0h.BruceEm/Mail/Local%20Folders/Inbox?number=322144395&header=quotebody&part=1.1.2&filename=image003.jpg" o:title="Top 100 Rochester 2010" />
</v:shape><![endif]--><!--[if !vml]--><span style="position: absolute;
z-index: -1; margin-left: 367px; margin-top: 17px; width:
60px; height: 58px;"><img
src="cid:part1.03020105.05030902@bellnet.ca"
v:shapes="_x0000_s1026" height="58" width="60"></span><!--[endif]--><span
style="font-size: 9pt; font-family:
"Arial","sans-serif"; color: navy;">134
South Fitzhugh Street</span><span style="font-size: 9pt;
color: navy;"> </span><span
style="font-size: 9pt; font-family:
"Arial","sans-serif"; color: navy;">Rochester,
NY 14608</span><span style="font-size: 9pt; color: navy;"><br>
</span><span style="font-size: 9pt; font-family:
"Arial","sans-serif"; color: navy;">T:
(585) 325-6004 </span><span style="font-size: 9pt;
font-family: "Arial","sans-serif";
color: black;">Ext. 114</span><span style="color: navy;">
</span><span style="font-size: 9pt; font-family:
"Arial","sans-serif"; color: navy;">F:
(585) 325-6005</span><span style="font-size: 9pt;
font-family: "Arial","sans-serif";
color: black;"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 9pt; font-family:
"Arial","sans-serif"; color: black;"><a
moz-do-not-send="true"
href="mailto:wbishop@pathfinder-ea.com">wbishop@pathfinder-ea.com</a>
</span><span style="font-size: 9pt; font-family:
"Arial","sans-serif"; color: black;"><a
moz-do-not-send="true"
href="http://www.pathfinder-ea.com/">www.pathfinder-ea.com</a><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 18pt;
font-family: Webdings; color: green;">P</span><span
style="color: green;"> </span><span style="font-size:
7.5pt; color: green;">Sustainability – the forest AND the
trees.</span><span style="font-size: 18pt; font-family:
Webdings; color: green;"> P </span><span style="color:
green;"><o:p></o:p></span></p>
</div>
<div>
<div class="MsoNormal" style="text-align: center;"
align="center">
<hr align="center" size="2" width="100%"></div>
<p class="MsoNormal"><b><span style="font-size: 10pt;
font-family: "Tahoma","sans-serif";">From:</span></b><span
style="font-size: 10pt; font-family:
"Tahoma","sans-serif";">
<a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On
Behalf Of </b>Alex Krickx<br>
<b>Sent:</b> Wednesday, January 05, 2011 1:40 PM<br>
<b>To:</b> John Aulbach; Jeremy Goth<br>
<b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Window "Curb"</span><o:p></o:p></p>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">Alright- I know have a follow up question:<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">I ran my model with 3 different spacer types –
steel, aluminum and insulated. While I expected the
differences to be small the result I got was 0 difference at
all- No difference in the loads in Report LS-C, and no
difference in the Average U-value reported in LV-D.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">In some research I’ve done in the past using
Therm and Window I’ve found that going from a steel spacer
to an insulated spacer can change the U-value by as much as
0.30 to 0.38. I would say that’s a significant difference
and would expect that any change of that magnitude would
impact loads in eQUEST. Unfortunately I saw 0 change.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">Any suggestions?<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">Thanks for all the responses so far – this topic
is really interesting!<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">Kind regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">Alex Krickx<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-family:
"Calibri","sans-serif"; color: rgb(38,
47, 19);">Alex Krickx, LEED AP<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 9pt; font-family:
"Calibri","sans-serif"; color: gray;">Building
Energy Specialist<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 8pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><img id="_x0000_i1026"
src="cid:part2.08040307.01050005@bellnet.ca"
alt="email_sig" border="0" height="42" width="121"></span><span
style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 9pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">1250 Elko Dr, Sunnyvale, CA 94089<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 9pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">(t) 408.541.8124<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 9pt; font-family:
"Calibri","sans-serif"; color: gray;"><o:p> </o:p></span></p>
<p class="MsoNormal"><b><i><span style="font-size: 7.5pt;
font-family: "Arial","sans-serif";
color: rgb(31, 73, 125);">Warning:</span></i></b><i><span
style="font-size: 7.5pt; font-family:
"Arial","sans-serif"; color: rgb(31,
73, 125);"> The information contained in this e-mail may
be privileged attorney-client communications or attorney
work product and/or proprietary and confidential. If the
reader of this message is not the intended recipient then
you have received it in error and any review, distribution
or copying of this message is prohibited and you are to
notify us immediately by reply e-mail and delete the
original message immediately.</span></i><span
style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<div>
<div style="border-right: medium none; border-width: 1pt
medium medium; border-style: solid none none; border-color:
rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color;
padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><span style="font-size: 10pt;
font-family:
"Tahoma","sans-serif";">From:</span></b><span
style="font-size: 10pt; font-family:
"Tahoma","sans-serif";">
<a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On
Behalf Of </b>Alex Krickx<br>
<b>Sent:</b> Wednesday, January 05, 2011 9:09 AM<br>
<b>To:</b> John Aulbach; Jeremy Goth<br>
<b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Window "Curb"<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">Wow….<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">John – your question led me to the right answer
(almost). Under Window Properties/Basic Specs I can edit the
Spacer-Type. This edits the Edge-of-Glass conductance. Does
anyone know what the corresponding values are for the
different Spacer-Types? And is there any way to have a
user-entered value?<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<h5>SPACER-TYPE<o:p></o:p></h5>
<p class="MsoBodyText">Takes a code-word that specifies the type
of pane-to-pane spacer air in multi-pane windows. The type of
SPACER affects the edge-of-glass conductance.<o:p></o:p></p>
<p class="codeword">ALUMINUM Aluminum spacer<o:p></o:p></p>
<p class="codeword">BUTYL/METAL Butyl/Metal spacer<o:p></o:p></p>
<p class="codeword">INSULATED Insulated spacer<o:p></o:p></p>
<p class="codeword">STEEL Steel spacer<o:p></o:p></p>
<p class="codeword">UE-EQ-UC Fictitious
spacer that gives an edge-of-glass conductance equal to the
center-of-glass conductance (i.e., conductance of glass is
uniform over its area).<o:p></o:p></p>
<p class="codeword"><o:p> </o:p></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">John – I think that in the wizard mode you can
choose different frame materials. I’m not sure but I’m
guessing that the frame selection will vary what the frame
spacer type is. Thanks for the question!<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">Kind regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">Alex Krickx<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-family:
"Calibri","sans-serif"; color: rgb(38,
47, 19);">Alex Krickx, LEED AP<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 9pt; font-family:
"Calibri","sans-serif"; color: gray;">Building
Energy Specialist<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 8pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><img id="Picture_x005f_x0020_1"
src="cid:part2.08040307.01050005@bellnet.ca"
alt="email_sig" border="0" height="42" width="121"></span><span
style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 9pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">1250 Elko Dr, Sunnyvale, CA 94089<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 9pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);">(t) 408.541.8124<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 9pt; font-family:
"Calibri","sans-serif"; color: gray;"><o:p> </o:p></span></p>
<p class="MsoNormal"><b><i><span style="font-size: 7.5pt;
font-family: "Arial","sans-serif";
color: rgb(31, 73, 125);">Warning:</span></i></b><i><span
style="font-size: 7.5pt; font-family:
"Arial","sans-serif"; color: rgb(31,
73, 125);"> The information contained in this e-mail may
be privileged attorney-client communications or attorney
work product and/or proprietary and confidential. If the
reader of this message is not the intended recipient then
you have received it in error and any review, distribution
or copying of this message is prohibited and you are to
notify us immediately by reply e-mail and delete the
original message immediately.</span></i><span
style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size: 11pt; font-family:
"Calibri","sans-serif"; color: rgb(31,
73, 125);"><o:p> </o:p></span></p>
<div>
<div style="border-right: medium none; border-width: 1pt
medium medium; border-style: solid none none; border-color:
rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color;
padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><span style="font-size: 10pt;
font-family:
"Tahoma","sans-serif";">From:</span></b><span
style="font-size: 10pt; font-family:
"Tahoma","sans-serif";"> John
Aulbach [<a class="moz-txt-link-freetext" href="mailto:jra_sac@yahoo.com">mailto:jra_sac@yahoo.com</a>] <br>
<b>Sent:</b> Wednesday, January 05, 2011 8:59 AM<br>
<b>To:</b> Alex Krickx; Jeremy Goth<br>
<b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Window "Curb"<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<div>
<p class="MsoNormal">Hi Alex:<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">Dumb Question.<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">Doesn't the eQuest Windows library
allow you to chose glazing with a certain type of fram
(wodd, aluminum, thermal bridge, no thermal bridge)?<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:
"Calibri","sans-serif"; color:
rgb(31, 73, 125);">John R. Aulbach, PE, CEM<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-family:
"Calibri","sans-serif"; color:
rgb(31, 73, 125);">Senior Energy Engineer<o:p></o:p></span></p>
<div>
<div>
<div>
<div>
<div class="MsoNormal"><span style="font-family:
"Calibri","sans-serif";
color: rgb(23, 54, 93);">
<hr style="color: rgb(23, 54, 93);" align="left"
noshade="noshade" size="2" width="30%"></span></div>
</div>
</div>
</div>
</div>
<p class="MsoNormal"><b><span style="font-family:
"Calibri","sans-serif";
font-variant: small-caps; color: navy;">Partner</span></b><b><span
style="font-family:
"Calibri","sans-serif";
font-variant: small-caps; color: green;"> </span></b><b><span
style="font-family:
"Calibri","sans-serif";
font-variant: small-caps; color: rgb(0, 102, 0);">Energy</span></b><b><span
style="font-family:
"Calibri","sans-serif";
font-variant: small-caps; color: navy;"><o:p></o:p></span></b></p>
<p class="MsoNormal"><span style="font-family:
"Calibri","sans-serif"; color:
rgb(31, 73, 125);">1990 E. Grand Avenue, El Segundo, CA
90245</span><br>
<span style="font-family:
"Calibri","sans-serif"; color:
rgb(31, 73, 125);">W: 888-826-1216, X254| D:
310-765-7295 | F: 310-817-2745<o:p></o:p></span></p>
<p class="MsoNormal"><a moz-do-not-send="true"
href="http://www.ptrenergy.com/"><span
style="font-family:
"Calibri","sans-serif";">www.ptrenergy.com</span></a><span
style="font-family:
"Calibri","sans-serif"; color:
rgb(31, 73, 125);"> </span><a moz-do-not-send="true"
href="mailto:%7C%20jaulbach@ptrenergy.com"><span
style="font-family:
"Calibri","sans-serif";">|
jaulbach@ptrenergy.com</span></a><span style="color:
rgb(31, 73, 125);"><o:p></o:p></span></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<div>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<div class="MsoNormal" style="text-align: center;"
align="center"><span style="font-size: 10pt;
font-family:
"Tahoma","sans-serif";">
<hr align="center" size="1" width="100%"></span></div>
<p class="MsoNormal" style="margin-bottom: 12pt;"><b><span
style="font-size: 10pt; font-family:
"Tahoma","sans-serif";">From:</span></b><span
style="font-size: 10pt; font-family:
"Tahoma","sans-serif";"> Alex
Krickx <a class="moz-txt-link-rfc2396E" href="mailto:akrickx@seriousmaterials.com"><akrickx@seriousmaterials.com></a><br>
<b>To:</b> Jeremy Goth <a class="moz-txt-link-rfc2396E" href="mailto:jngoth@hotmail.com"><jngoth@hotmail.com></a><br>
<b>Cc:</b> <a class="moz-txt-link-rfc2396E" href="mailto:equest-users@lists.onebuilding.org">"equest-users@lists.onebuilding.org"</a>
<a class="moz-txt-link-rfc2396E" href="mailto:equest-users@lists.onebuilding.org"><equest-users@lists.onebuilding.org></a><br>
<b>Sent:</b> Wed, January 5, 2011 8:43:44 AM<br>
<b>Subject:</b> Re: [Equest-users] Window "Curb"</span><o:p></o:p></p>
<div>
<p class="MsoNormal"><span style="font-size: 11pt;
font-family:
"Arial","sans-serif"; color:
rgb(31, 73, 125);">Thanks Bruce and Jeremy,</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 11pt;
font-family:
"Arial","sans-serif"; color:
rgb(31, 73, 125);"> </span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 11pt;
font-family:
"Arial","sans-serif"; color:
rgb(31, 73, 125);">Well, you’ve answered my question
but I still have the same problem: how to account
for edge-of-glass effects in eQUEST (the edge of
glass U-value will be between the frame and COG
values). Back to the drawing board I guess. Thanks
for the responses.</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 11pt;
font-family:
"Arial","sans-serif"; color:
rgb(31, 73, 125);"> </span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 11pt;
font-family:
"Arial","sans-serif"; color:
rgb(31, 73, 125);">Kind regards,</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 11pt;
font-family:
"Arial","sans-serif"; color:
rgb(31, 73, 125);">Alex Krickx</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 11pt;
font-family:
"Arial","sans-serif"; color:
rgb(31, 73, 125);"> </span><o:p></o:p></p>
<div>
<div style="border-right: medium none; border-width:
1pt medium medium; border-style: solid none none;
border-color: rgb(181, 196, 223) -moz-use-text-color
-moz-use-text-color; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><span style="font-size:
10pt; font-family:
"Arial","sans-serif";">From:</span></b><span
style="font-size: 10pt; font-family:
"Arial","sans-serif";">
Jeremy Goth [<a class="moz-txt-link-freetext" href="mailto:jngoth@hotmail.com">mailto:jngoth@hotmail.com</a>] <br>
<b>Sent:</b> Wednesday, January 05, 2011 8:26 AM<br>
<b>To:</b> Alex Krickx<br>
<b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> RE: [Equest-users] Window "Curb"</span><o:p></o:p></p>
</div>
</div>
<p class="MsoNormal"> <o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";">Go to
your building shell and navigate to the
space/roof/skylight in the component tree. Select
the skylight then go to the spreadsheet tab on the
right and find 'Skylight Surface - Curb -
Performance'.<br>
<br>
Jeremy<br>
</span><o:p></o:p></p>
<div class="MsoNormal" style="text-align: center;"
align="center"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";">
<hr align="center" size="2" width="100%"></span></div>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";">Date:
Tue, 4 Jan 2011 20:00:19 -0500<br>
From: <a class="moz-txt-link-abbreviated" href="mailto:bruce5@bellnet.ca">bruce5@bellnet.ca</a><br>
To: <a class="moz-txt-link-abbreviated" href="mailto:akrickx@seriousmaterials.com">akrickx@seriousmaterials.com</a><br>
CC: <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Subject: Re: [Equest-users] Window "Curb"<br>
<br>
</span><span style="font-size: 13.5pt; font-family:
"Arial","sans-serif";"> A
curb is used to lift the window up off the roof and
allow the window to be flashed and made water
tight. It can be as simple as a 2x6 or 2x8 wood
box. A complicated one would be a fully insulated
wall tunnel through a roof truss system. It should
be modelled as an exterior wall. There should be no
edge of glass effect as all the glass should be
inside the opening. There will be an edge/corner
effect where the window frame sits on the curb.<br>
Bruce Easterbrook P.Eng.<br>
Abode Engineering<br>
<br>
</span><span style="font-size: 10pt; font-family:
"Arial","sans-serif";"><br>
On 04/01/2011 04:12 PM, Alex Krickx wrote: </span><o:p></o:p></p>
<div>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";">Hi
everyone,</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";"> </span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";">Happy
New Year! Well, to start off the new year, I have
a question on what the “curb” is in the LV-H
report. The placement of the information, and the
fact that it has an area and U-value (much the way
the window frame does) leads me to believe it may
be to account for Edge-of-Glass effects (if you
look at Window5 outputs it has COG U-values, frame
U-values and edge-of-glass U-values).</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";"> </span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";">I can’t
see anywhere in the detailed edit mode to input
curb information - I looked in both the “Glass
Type Properties” and “Window Properties” Screens.</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";"> </span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";">I found
the following info in the DOE2 help file, but it
looks like it only applies to skylights? It also
wasn’t clear if it was in fact for edge of glass,
and how to add this information (I’m guessing in
the INP file?). Thanks for any help.</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";"> </span><o:p></o:p></p>
<p class="MsoNormal"><b><span style="font-size: 10pt;">CURB
-CONDUCT</span></b><a moz-do-not-send="true"
name="_Toc140138080"></a><o:p></o:p></p>
<p class="MsoNormal">Conductance of the skylight curb,
excluding the outside air film but including the
inside air film. <o:p></o:p></p>
<p class="MsoNormal">Notes:<o:p></o:p></p>
<p class="MsoNormal" style="margin-left: 0.25in;">1.
You can define curbs only for exterior windows and
skylights, not for interior windows.<o:p></o:p></p>
<p class="MsoNormal" style="margin-left: 0.25in;">2.
If the CURB-HEIGHT is zero no curb calculations will
be performed.<o:p></o:p></p>
<p class="MsoNormal" style="margin-left: 0.25in;">3.
The curb area is <b>not</b> subtracted from the
associated exterior wall area.<o:p></o:p></p>
<p class="MsoNormal" style="margin-left: 0.25in;">4.
Each hour, the program adds the effect of a wind
speed-dependent outside air film to the user
specified CURB-CONDUCT.<o:p></o:p></p>
<p class="MsoNormal" style="margin-left: 0.25in;">5.
The various elements of a curb (top, bottom, side,
dividers, etc.) may have different conductances. In
this case, CURB-CONDUCT should be an area-weighted
average of the different elements.<o:p></o:p></p>
<p class="MsoNormal" style="margin-left: 0.25in;">6.
The program finds the overall window conduction by
adding curb, frame, edge-of-glass, and
center-of-glass contributions. Thus, all three of
these contributions are included in each of the
following report quantities:<br>
"Window Conduction" in summary reports
LS-B, LS-C, LS-E, and LS-F;<br>
"Window U-Value" and "Window Area" in
verification report LV-D and LV-H;<br>
WINDOW hourly report variable #1, "Window
U-Value".<o:p></o:p></p>
<p class="MsoNormal" style="margin-left: 0.25in;">7.
A WINDOW multiplier also multiplies the curb area.<o:p></o:p></p>
<p class="MsoNormal" style="margin-left: 0.25in;">8.
Window fins and overhangs shade the curb as well as
the glazing.<o:p></o:p></p>
<p class="MsoNormal" style="margin-left: 0.25in;">9.
Shading devices, like blinds and drapes, that you
specify using the WINDOW keywords SHADING-SCHEDULE
and CONDUCT-SCHEDULE, affect only the glazed part of
the window. They do not affect the heat conduction
through the curb.<o:p></o:p></p>
<p class="MsoNormal" style="margin-left: 0.25in;">10.
If the window has a setback, the curb is also set
back by the same amount.<o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";"> </span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";">Kind
regards,</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";">Alex
Krickx</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";"> </span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-family:
"Arial","sans-serif"; color:
rgb(38, 47, 19);">Alex Krickx, LEED AP</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 9pt;
font-family:
"Arial","sans-serif"; color:
gray;">Building Energy Specialist</span><o:p></o:p></p>
<p class="MsoNormal"><b><span style="font-size: 8pt;
font-family:
"Arial","sans-serif"; color:
rgb(31, 73, 125);">Error! Filename not
specified.</span></b><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 9pt;
font-family:
"Arial","sans-serif";">1250
Elko Dr, Sunnyvale, CA 94089</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 9pt;
font-family:
"Arial","sans-serif";">(t)
408.541.8124</span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 9pt;
font-family:
"Arial","sans-serif"; color:
gray;"> </span><o:p></o:p></p>
<p class="MsoNormal"><b><i><span style="font-size:
7.5pt; font-family:
"Arial","sans-serif";">Warning:</span></i></b><i><span
style="font-size: 7.5pt; font-family:
"Arial","sans-serif";"> The
information contained in this e-mail may be
privileged attorney-client communications or
attorney work product and/or proprietary and
confidential. If the reader of this message is
not the intended recipient then you have
received it in error and any review,
distribution or copying of this message is
prohibited and you are to notify us immediately
by reply e-mail and delete the original message
immediately.</span></i><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";"> </span><o:p></o:p></p>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";"> </span><o:p></o:p></p>
</div>
<pre> <o:p></o:p></pre>
<pre>_______________________________________________<o:p></o:p></pre>
<pre>Equest-users mailing list<o:p></o:p></pre>
<pre><a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><o:p></o:p></pre>
<pre>To unsubscribe from this mailing list send a blank message to <a moz-do-not-send="true" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></pre>
<p class="MsoNormal"><span style="font-size: 10pt;
font-family:
"Arial","sans-serif";"><br>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank
message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</span><o:p></o:p></p>
</div>
</div>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>