Hi Omer,<br><br>You need to consult with the design engineer that is specifying the heat recovery system for your building. If you tell him/her the information you need to input into eQUEST to model heat recovery, he/she should be able to provide you with the proper values.<br>
<br>Cheers,<br><br>Carol<br><br><div class="gmail_quote">2010/12/17  <span dir="ltr"><<a href="mailto:omoltay@mimtarch.com">omoltay@mimtarch.com</a>></span><br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
Dear All,<br>
<br>
I need to model heat recovery in one of my fan systems for the baseline<br>
case according to G3.1.2.10. As far as I understand there are only 2<br>
requirements dictated by ASHRAE:<br>
<br>
- At least 50% recovery effectiveness,<br>
- Permitting air economizer operation by bypassing heat recovery.<br>
<br>
Since there are so many options in Equest Heat Recovery tabs, I am at a<br>
loss to where to start. Has anybody had experience with modelling ERV to<br>
satisfy ASHRAE 90.1?<br>
<br>
Best regards,<br>
<br>
Ömer Moltay<br>
Mimta Ltd.<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; left: -5000px;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup{position: absolute;z-index: 9999;padding: 0px 0px;margin-left: 0px;margin-top: 0px;overflow: hidden;word-wrap: break-word;color: black;font-size: 10px;text-align: left;line-height: 130%;}</style>