<div>Praveen,   System Type 7 is actually VAV w/reheat, chillled water coils....etc.</div>
<div> </div>
<div>The "packaged" that is printed in front of it is a "typo" in the Standard.    You should use the non-packaged option for your baseline model.</div>
<div> </div>
<div>Pasha<br><br></div>
<div class="gmail_quote">On Wed, Nov 24, 2010 at 9:19 AM, Rob Hudson <span dir="ltr"><<a href="mailto:rdh4176@gmail.com">rdh4176@gmail.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">use VAV type system.  Typically packaged is for DX units.  i am doing the same thing in a model right now as well.<br>
<br>
<div class="gmail_quote">
<div>
<div></div>
<div class="h5">On Wed, Nov 24, 2010 at 10:36 AM, Praveen Jain <span dir="ltr"><<a href="mailto:praveenjain83@gmail.com" target="_blank">praveenjain83@gmail.com</a>></span> wrote:<br></div></div>
<blockquote style="BORDER-LEFT: rgb(204,204,204) 1px solid; MARGIN: 0pt 0pt 0pt 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div>
<div></div>
<div class="h5"><br clear="all">Dear all 
<div><br></div>
<div>As per ASHRAE 90.1 HVAC System 7 is Packged rooftop VAV with Reheat and cooling type is Chilled water.</div>
<div>How can we model above  HVAC System  in eQUEST.</div>
<div>If I choose Cooling source as Chilled water coils than it donot show any Packaged system in System Type drop-down.<br>-- <br>With Thanks and Regards,<br>Praveen K. Jain<br>Roorkee<br></div><br></div></div>_______________________________________________<br>
Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br><font color="#888888">Rob Hudson<br></font><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>