Andrew,<br><br>Create a Dummy space, very small 1ft x 1ft x 1ft with no load and then a Dummy Zone for it and use this for your zone. I would not use Multi Zone but rather PSZ if you are supply the fresh air at a constant volume or PVAVS if it is supplied at a variable volume.<br>
<br>Best,<br><br>Carol<br><br><div class="gmail_quote">On Wed, Nov 3, 2010 at 2:48 AM, Andy Harrison <span dir="ltr"><<a href="mailto:Andy.Harrison@arup.com">Andy.Harrison@arup.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
Hi All,<br>
<br>
I am trying to model a building which has a minimum fresh air AHU serving all zones, each of which also has a local cooling unit.  I was trying to model this using a single zone AHU for each zone, with outside air to all units coming from the multizone unit, which I created later, however I am getting an error saying that the multizone AHU needs to be assigned at least one zone.  How can I do this, when all of the zones are assigned to a local unit?  If I assign a small zone to get rid of the error, will the multizone AHU only be sized for the cooling load associated with this zone?  How can I confirm that the multizone AHU is sized for the appropriate fresh air load?<br>

<br>
Regards,<br>
<br>
Andrew<br>
____________________________________________________________<br>
Electronic mail messages entering and leaving Arup  business<br>
systems are scanned for acceptability of content and viruses<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; left: -5000px;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup{position: absolute;z-index: 9999;padding: 0px 0px;margin-left: 0px;margin-top: 0px;overflow: hidden;word-wrap: break-word;color: black;font-size: 10px;text-align: left;line-height: 130%;}</style>