<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:arial, helvetica, sans-serif;font-size:10pt"><div></div><div>One quick and easy fix is to increase the sizing factor found in the cooling tab.  Currently you have it set to 1.15.  I tried setting it to 2.0, and there were no more unmet hours.  <br> </div>__________________________________________________________<br>Eddie Corwin, Energy & Sustainability Engineer<br>ALTANOVA - www.altanova-energy.com<br>41-41 24th Street - 4th Floor - Long Island City, NY 11101<br><br><div>T: (347) 410-9049<br>E: ecorwin@altanova-energy.com<br><div><br></div><div style="font-family:arial, helvetica, sans-serif;font-size:10pt"><br><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><font size="2" face="Tahoma"><hr size="1"><b><span style="font-weight: bold;">From:</span></b> Brad L. Huff
 <BradH@BVHis.com><br><b><span style="font-weight: bold;">To:</span></b> "equest-users@lists.onebuilding.org" <equest-users@lists.onebuilding.org><br><b><span style="font-weight: bold;">Sent:</span></b> Tue, October 19, 2010 5:02:26 PM<br><b><span style="font-weight: bold;">Subject:</span></b> [Equest-users] Under sized cooling coil<br></font><br>



 
 
<style>
<!--
 
 _filtered {font-family:Wingdings;panose-1:5 0 0 0 0 0 0 0 0 0;}
 
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:"Times New Roman";}
a:link, span.MsoHyperlink
        {color:blue;text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;text-decoration:underline;}
span.EmailStyle17
        {font-family:Arial;color:windowtext;}
 _filtered {margin:1.0in 1.25in 1.0in 1.25in;}
div.Section1
        {}
 
 _filtered {}
 _filtered {margin-left:1.25in;font-family:Arial;}
 _filtered {}
 _filtered {margin-left:1.25in;font-family:Arial;}
ol
        {margin-bottom:0in;}
ul
        {margin-bottom:0in;}
-->
</style>





<div class="Section1">

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">All,</span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">  </span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">I am modeling a portion of a 100% outside air lab in a type
5A climate zone. The area is below ground/has interior walls so there is no
fenestration. The system has two chilled water air handling units and VAV boxes
with zone reheat. The two AHU’s run 24/7 at a constant CFM because the
supply air is driven by a required air change rate per room type. </span></font></p> 

<p class="MsoNormal" style="text-indent:.5in;"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">My problem is:</span></font></p> 

<p class="MsoNormal" style="margin-left:1.0in;"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">-     I have too
many unmet cooling hours when allowing e-Quest to auto-size the cooling coil
capacity of the air handling units</span></font></p> 

<p class="MsoNormal" style="margin-left:.5in;"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">Diagnosis:</span></font></p> 

<p class="MsoNormal" style="margin-left:1.25in;"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;"><span style="">-<font size="1" face="Times New Roman"><span style="font:7.0pt "Times New Roman";">         
</span></font></span></span></font><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">The delta T of the cooling coil
never gets above 7 degrees F any day of the summer.</span></font></p> 

<p class="MsoNormal" style="margin-left:1.25in;"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;"><span style="">-<font size="1" face="Times New Roman"><span style="font:7.0pt "Times New Roman";">         
</span></font></span></span></font><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">e-Quest severely undersized the
cooling coils from a design day. (I have calculated the design day cooling load
by hand)</span></font></p> 

<p class="MsoNormal" style="margin-left:1.25in;"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;"><span style="">-<font size="1" face="Times New Roman"><span style="font:7.0pt "Times New Roman";">         
</span></font></span></span></font><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">No warnings in the Sim report</span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">  </span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">I have tried troubleshooting the system for a couple of days
but am unable to find the reason e-Quest is under sizing the cooling coil
capacity. I have attached the .inp file. Any suggestion are greatly
appreciated.</span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">  </span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">Thank you,</span></font></p> 

<p class="MsoNormal"><font size="2" face="Arial"><span style="font-size:10.0pt;font-family:Arial;">Brad</span></font></p> 

<p class="MsoNormal" style=""><font size="1" color="gray" face="Arial"><span style="font-size:8.0pt;font-family:Arial;color:gray;">Brad Huff, E.I.T., Mechanical Engineer</span></font><font size="1" color="navy" face="Arial"><span style="font-size:8.0pt;font-family:Arial;color:navy;"> </span></font><strong><b><font size="1" color="navy" face="Times New Roman"><span style="font-size:8.0pt;color:navy;">I </span></font></b></strong><strong><b><font size="1" face="Times New Roman"><span style="font-size:8.0pt;">BVH Integrated
Services<font color="navy"><span style="color:navy;"> </span></font><font color="black"><span style="color:black;">I </span></font></span></font></b></strong><font size="1" color="gray" face="Arial"><span style="font-size:8.0pt;font-family:Arial;color:gray;">860.286.9171 tel </span></font><strong><b><font size="1" color="black" face="Times New Roman"><span style="font-size:8.0pt;color:black;">I</span></font></b></strong><strong><b><font size="1" color="gray" face="Times New Roman"><span style="font-size:8.0pt;color:gray;"> </span></font></b></strong><font size="1" color="gray" face="Arial"><span style="font-size:8.0pt;font-family:Arial;color:gray;">860.242.0236 fax </span></font><strong><b><font size="1" color="black" face="Times New Roman"><span style="font-size:8.0pt;color:black;">I</span></font></b></strong><strong><b><font size="1" color="gray" face="Times New Roman"><span style="font-size:8.0pt;color:gray;"> </span></font></b></strong><font
 size="1" color="gray" face="Arial"><span style="font-size:8.0pt;font-family:Arial;color:gray;">50 Griffin Road South, Bloomfield CT 06002 </span></font><b><font size="1" color="black" face="Arial"><span style="font-size:8.0pt;font-family:Arial;color:black;font-weight:bold;">I </span></font></b><font color="navy"><span style="color:navy;"><a rel="nofollow" title="blocked::www.bvhis.com"><b><font size="1" face="Arial" title="blocked::www.bvhis.com"><span title="blocked::www.bvhis.com"><span style="font-size:8.0pt;font-family:Arial;font-weight:bold;">www.bvhis.com</span></span></font></b></a></span></font><font color="#c00000"><span style="color:#C00000;"> </span></font><font color="navy"><span style="color:navy;"></span></font></p> 

<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="
font-size:12.0pt;">  </span></font></p> 

</div>




</div></div></div><div style="position:fixed"></div>


</div></body></html>