Rick,<br><br>The PFP box is just the zone delivery box for your VAV system. Use the efficiency for the corresponding size of your system, not the box.<br><br>Best,<br>Carol<br><br><div class="gmail_quote">2010/10/17 YinRic <span dir="ltr"><<a href="mailto:cesseric@hotmail.com">cesseric@hotmail.com</a>></span><br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">



<div>
Hi Users,<br>
 <br>
I am not an HVAC expert, and I have a basic question to ask, though it is not quite related to equest itself: <br>
 <br>
If the Baseline HVAC system type is "System 6-Packaged VAV w/PFP Boxes", which one from Table 6.8.1A-G shall I use to determine the minimum efficiency?  <br>
 <br>
After review of EAc1 from GBCI, it is stated that my COP/EER input is inconsistent with Table 6.8.1--"Th<span style="font-size: 8.5pt;" lang="EN-US">e applicable capacity ranges for the systems used in the Baseline and Proposed Case shall be consistent with the ranges listed in Tables 6.8.1A through 6.8.1G</span>." It seems to me that a wrong table is used as reference. <br>

 <br>
Thanks in advance!<br>
 <br>
Rick<br>                                    </div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; left: -5000px;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup{position: absolute;z-index: 9999;padding: 0px 0px;margin-left: 0px;margin-top: 0px;overflow: hidden;word-wrap: break-word;color: black;font-size: 10px;text-align: left;line-height: 130%;}</style>