As I see it, the best option is to create secondary heating loops
off the primary heating loop (type=secondary) with their own pumps
and head & flow characteristics.<br>
<br>
Brian<br>
<br>
<br>
On 9/30/2010 2:39 PM, Scott Meader wrote:
<blockquote
cite="mid:AANLkTikB3M1VF3DK44=euN=BmTq73D4KXfSWng4Sn6uO@mail.gmail.com"
type="cite">I have a Campus/District Heating situation for the
Heating Hot Water. The system is utilizing a Secondary pump and
two Tertiary pumps. The characteristics of the Secondary pump and
Tertiary pumps are different, I cannot find a way to pump multiple
different pumps on the same system.<br>
<br>
Any help would be great.<br>
<br>
Scott<br>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
No virus found in this incoming message.
Checked by AVG - <a class="moz-txt-link-abbreviated" href="http://www.avg.com">www.avg.com</a>
Version: 9.0.856 / Virus Database: 271.1.1/3168 - Release Date: 09/30/10 02:34:00
</pre>
</blockquote>
<br>
<br>
<pre class="moz-signature" cols="72">--
Brian Fountain, Principal
GreenSim
voice - 519-489-0112
email - <a class="moz-txt-link-abbreviated" href="mailto:bfountain@greensim.com">bfountain@greensim.com</a></pre>
</body>
</html>